How do I reset circuit breaker on 10BI?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How do I reset circuit breaker on 10BI?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
6
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

How do I reset circuit breaker on 10BI?

Using UTS 10BI with utility power I accidentally overloaded a circuit. I reset breaker in existing old circuit board but can't seem to reset the 10BI. Message on the screen says circuit failure "press a key to reset". I assume this means either of the arrows but circuit red light keeps flashing. How do I reset the UTS breaker? nothing connected to the problem circuit.

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

The UTS showed a flashing light on the overloaded circuit and you're right it was a fuse in the UTS. Both the breaker on the main board and the fuse in the UTS blew. It's a problem waiting to happen as a small kitchen has a toaster oven and a large microwave on the same circuit just waiting for either my wife or I to forget and try to use them both at the same time  I'm finally having a second circuit installed to avoid a recurrence.

consider this question answered. Thank you all  

See Answer In Context

  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

Further to my post above, an electrician found a blown fuse in the 10BI and replaced it so I'm back in business but I still don't know what "press any key to reset" means? What "key"?

On 1/2/2016 9:52 PM, Robert said:

Using UTS 10BI with utility power I accidentally overloaded a circuit. I reset breaker in existing old circuit board but can't seem to reset the 10BI. Message on the screen says circuit failure "press a key to reset". I assume this means either of the arrows but circuit red light keeps flashing. How do I reset the UTS breaker? nothing connected to the problem circuit.

  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

Robert,

The message is not as intuitive as it should be. If the Light was out for the circuit that would indicate the circuit was open and in most cases means the fuse has blown. The "press a key to reset" should be done after replacing the blown fuse to reactivate the circuit and the key to press is either the up or down arrow.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

I appreciate your observation that the message "is not as intuitive as it should be". "Press a key" sounds like it comes from desktop software that has a keyboard. I'll remember your up or down arrow suggestion for next time.

The light on the overloaded circuit was not out but flashing. The back story is that the particular circuit is in a small kitchen that due to size constraints ended up with both a toaster oven and a microwave oven plugged into the same outlet. When either my wife or I unthinkingly turned one on while the other was on it tripped a breaker which was easy to reset. This experience has shown that the tripped breaker doesn't protect the UTS 10BI fuse from blowing making for a more cumbersome punishment for our forgetfullness. We're either going to have our electrician add a 2nd circuit or maybe there's a switched adaptor that would take the plugs of both appliances but would only allow one to run without switching off the other.

Thank you very much for your help.

  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

Further to my thanks above I wanted to thank Michael Smith as well but somehow his comment vanished  from the correspondence.

  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

If the Light was out for the circuit that would indicate the circuit was open and in most cases means the fuse has blown.

The "press a key to reset" should be done after replacing the blown fuse to reactivate the circuit and the key to press is either the up or down arrow.

http://www.7pcb.co.uk

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

0 Likes
0
2036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:57 AM

The UTS showed a flashing light on the overloaded circuit and you're right it was a fuse in the UTS. Both the breaker on the main board and the fuse in the UTS blew. It's a problem waiting to happen as a small kitchen has a toaster oven and a large microwave on the same circuit just waiting for either my wife or I to forget and try to use them both at the same time  I'm finally having a second circuit installed to avoid a recurrence.

consider this question answered. Thank you all  

  • Tags:
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of