"Refrigerator" Circuit on UTS6H powered by Honda EU2000i will not light

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • "Refrigerator" Circuit on UTS6H powered by Honda EU2000i will not light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
3
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

"Refrigerator" Circuit on UTS6H powered by Honda EU2000i will not light

Hi again,

Had our first power outtage in Seattle after a nice long summer, and I found a small problem. My UTS6H powered by my Honda EU2000i will not power up my #3 Circuit, which is dedicated to my kitchen fridge, at all. Older image here. All 6 circuits are on standard settings; max power set to 1600 watts per instructions. As soon as I plugged in the generator, #3 lights, then goes dark. I waited over 30 minutes (Max time off), and still nothing. The overall load of the 6 circuits is very low usually, maybe 200 watts, but still nothing. The only workaround was to turn off load shedding (but that is the primary reason for having an APC UTS). But, the fear in that is that if the kitchen fridge, garage fridge (plugged in directly to the front of the ATS), and furnace blower kick on at once, something will trip. I even turned off the thermostat just to avoid the furnace blower causing any trouble.

Maybe I need to use some custom setting? But, it's just a fridge, it should work out of the box.

 

Thanks,

Rudy

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • circuit
  • eu2000i
  • honda
  • refrigerator
  • uts6h
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

Any luck with getting it to work?

Thanks

Will

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

Hi,

Have you tried to turn off the delay for that circuit?

This is from the user's guide

  Problem: While operating on backup power the UTS repeatedly drops some connected loads
  Cause: The circuit may be incorrectly configured as delayable.
Use the Circuit Setup button to navigate to CKT DELAYABLE screen for the circuit affected. Disable the circuit delayable option, (select NO). This disables ALM for that circuit. Repeat this process for all circuits affected.

Another possibility is the genorator power rating is set to low.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 PM . Last Modified: ‎2024-03-21 03:58 AM

Thanks Bill. Though, I feel I shouldn't have to set a fridge to not delayable. A fridge only needs power once in a while; say for 5 minutes every 30 minutes. Those are the stock settings. I could set the delayable feature to "off" for the fridge, but I would rather not if it can be avoided. The power rating of the generator is only 2000 watts, recommended settings for the UTS are to set it at 1600 (recommended load for this generator vs. peak 2000 watts). But again, that's the whole point of the UTS, to load balance the power from the fridge to other circuits.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

Any luck with getting it to work?

Thanks

Will

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.