UTS10BI when a circuit is set to "either" how does it decide UPS or Gen?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI when a circuit is set to "either" how does it decide UPS or Gen?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

0 Likes
1
768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

UTS10BI when a circuit is set to "either" how does it decide UPS or Gen?

I ran a good test this week-end with the UTS10BI and the Honda EU2000i. I ran the house for about 30 minutes on the generator. I noticed something unexpected for what I thought would happen. When I switched off the main breaker to simulate a power outage, the UTS automatically switched over to the UPS for circuits defined as "either" just great. Then I fire up the EU2000i and plugged it in and a few seconds later, the UTS switched to Generator. All is great and I'm a very happy camper.

What caught my eye as I was looking through the circuit's status display on the UTS was that the circuits defined as "either" were still running through the UPS, while the circuits defined as "Gen Only" were running on the Generator. All this is good & ok, but I would have expected the UTS to switch the circuits defined as "either" over to the generator.

I performed another test. With both the UPS on-line and the Generator running & plugged in (on-line), I again turned the main breaker off. There was again a few seconds delay & everything powered on just Great, Yea! However, this time when I reviewed the circuit's status display, all the circuits where running on the generator. The "either" circuits this time were not running on the UPS, but were running on the generator.

My question is, How does the firmware determine when a circuit defined as "either" gets to run on UPS or Generator?

The manual doesn't seem to go into any kind of explanation on this depth of a level.

I prefer to have all the circuits running through the generator once it's plugged in to save the UPS, but it seems that this may not always be the case.

A follow on question is, Will the UTS switch a circuit that is set to "either" from Generator to UPS if the UTS senses that it's going to run into a generator overload situation?

Thx so much!

-Todd

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • eu2000
  • eu2000i
  • generator
  • help
  • question
  • test
  • testing
  • ups
  • uts
  • uts10bi
  • uts6
  • uts6bi
  • uts6h
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

0 Likes
0
768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

i looked at this and came to the conclusion based on discussions here that the generator is always the primary and if it becomes close to overloading, the circuit will switch to the secondary source, i.e. the UPS in your case. based on your testing results, i am not 100% sure what happened there but the UTS somehow decides whats best. beyond that, i am just not sure but on your follow up question, the answer is yes as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

0 Likes
0
769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:50 PM . Last Modified: ‎2024-03-20 01:01 AM

i looked at this and came to the conclusion based on discussions here that the generator is always the primary and if it becomes close to overloading, the circuit will switch to the secondary source, i.e. the UPS in your case. based on your testing results, i am not 100% sure what happened there but the UTS somehow decides whats best. beyond that, i am just not sure but on your follow up question, the answer is yes as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now