Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

UTS10BI connecting 10 120v circuits

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI connecting 10 120v circuits
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2127
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
diy123_apc
Crewman diy123_apc
Crewman

Posted: ‎2021-06-29 10:23 PM

0 Likes
9
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:23 PM

UTS10BI connecting 10 120v circuits

This was originally posted on APC forums on 2/8/2012


I recently bought a Honda EU6500I generator and a UTS10BI Transfer switch with a UPS 1500 battery back up. to be prepared for the next power outage here in Washington State. My house is Gas and Electric (Gas Furnace only 120v no A/C Gas Water Heater). I called APC and asked about connecting 10 120v loads however they said you can only connect 8 120v loads and if you do not have a 240v load, you just have to cap wires 9 and 10. I know that I need a 240v input as required on circuits 9 and 10, however why can I not connect 2 120v loads to circuits 9 and 10 and run those simultaneously since they are switched together as a single switch.

Pleased help to explain.

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • christian
  • louboutin
  • switch
  • transfer
  • uts
  • uts10
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
beaners_apc
Ensign beaners_apc
Ensign

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 4/28/2012


updated release date now is June 17th.:-( hope this is the last time

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
diy123_apc
Crewman diy123_apc
Crewman

Posted: ‎2021-06-29 10:23 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:23 PM

This was originally posted on APC forums on 2/8/2012


I recently bought a Honda EU6500I generator and a UTS10BI Transfer switch with a UPS 1500 battery back up. to be prepared for the next power outage here in Washington State. My house is Gas and Electric (Gas Furnace only 120v no A/C Gas Water Heater). I called APC and asked about connecting 10 120v loads however they said you can only connect 8 120v loads and if you do not have a 240v load, you just have to cap wires 9 and 10. I know that I need a 240v input as required on circuits 9 and 10, however why can I not connect 2 120v loads to circuits 9 and 10 and run those simultaneously since they are switched together as a single switch.

Pleased help to explain.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This reply was originally posted by Angela on APC forums on 2/8/2012


hello,

circuits 9 and 10 need to be 180º out of phase (which gives you 240v) in order to power up the UTS itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

diy123_apc
Crewman diy123_apc
Crewman

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 2/8/2012


I understand the 180 degrees phase difference on the input side.

What I would like to do, is use the output on two different loads. I know that loads will have to be managed as a single load by the switch.

Is this going to cause a load imballance or something like that on the output side of switches 9 and 10?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This reply was originally posted by Angela on APC forums on 2/8/2012


yes, load imbalance is a problem with this so that is why it cannot be done.

Reply

Link copied. Please paste this link to share this article on your social media post.

uofd90_apc
uofd90_apc
Cadet

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 3/9/2012


I placed and order (and paid for) for this UTS unit back in early September 2011 and everytime I call to find out status of when it will be coming my dealer keeps telling me that the manufacturer has pushed back the anticipated delivery date agian. Would mind letting me know where you were able to find this unit in stock. Every where I look online it is out of stock. A company name and phone # or website address would greatly appreciated. I can't understand why after 6 months this unit is still out of stock.

Reply

Link copied. Please paste this link to share this article on your social media post.

diy123_apc
Crewman diy123_apc
Crewman

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 3/10/2012


I searched every local equipment company within 3 cities and found a retail outlet that had one from 2010 that had never been open or sold. They had just performed a 5 year inventory and found it. I know that APC has this unit on back order because all available stock was depleted during this winter.
Keep trying and do not get discouraged.
Good Luck in your searching.

Reply

Link copied. Please paste this link to share this article on your social media post.

Dklu_apc
Crewman Dklu_apc
Crewman

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 3/12/2012


I am having the same problem. I ordered one at the end of September and I'm still waiting for it. Every couple of weeks I get a new expected date that is a few more weeks away. I am on the verge of cancelling my order and going with a traditional transfer switch. At least I know I can get one.

Reply

Link copied. Please paste this link to share this article on your social media post.

diy123_apc
Crewman diy123_apc
Crewman

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 3/14/2012


Hold out for APC to replenish their stock. Winter is almost over in most of the country and you will not be disappointed. If your wife or you want more than one backup source with the ability to automatically manage your loads, wait for this one.

Reply

Link copied. Please paste this link to share this article on your social media post.

beaners_apc
Ensign beaners_apc
Ensign

Posted: ‎2021-06-29 10:24 PM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM

This was originally posted on APC forums on 4/28/2012


updated release date now is June 17th.:-( hope this is the last time

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc