UTS10BI connecting 10 120v circuits

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI connecting 10 120v circuits
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:23 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
9
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:23 PM . Last Modified: ‎2024-03-20 03:01 AM

UTS10BI connecting 10 120v circuits

I recently bought a Honda EU6500I generator and a UTS10BI Transfer switch with a UPS 1500 battery back up. to be prepared for the next power outage here in Washington State. My house is Gas and Electric (Gas Furnace only 120v no A/C Gas Water Heater). I called APC and asked about connecting 10 120v loads however they said you can only connect 8 120v loads and if you do not have a 240v load, you just have to cap wires 9 and 10. I know that I need a 240v input as required on circuits 9 and 10, however why can I not connect 2 120v loads to circuits 9 and 10 and run those simultaneously since they are switched together as a single switch.

Pleased help to explain.

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • christian
  • louboutin
  • switch
  • transfer
  • uts
  • uts10
  • uts10bi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

updated release date now is June 17th.:-( hope this is the last time

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:23 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:23 PM . Last Modified: ‎2024-03-20 03:01 AM

I recently bought a Honda EU6500I generator and a UTS10BI Transfer switch with a UPS 1500 battery back up. to be prepared for the next power outage here in Washington State. My house is Gas and Electric (Gas Furnace only 120v no A/C Gas Water Heater). I called APC and asked about connecting 10 120v loads however they said you can only connect 8 120v loads and if you do not have a 240v load, you just have to cap wires 9 and 10. I know that I need a 240v input as required on circuits 9 and 10, however why can I not connect 2 120v loads to circuits 9 and 10 and run those simultaneously since they are switched together as a single switch.

Pleased help to explain.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

hello,

circuits 9 and 10 need to be 180º out of phase (which gives you 240v) in order to power up the UTS itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

I understand the 180 degrees phase difference on the input side.

What I would like to do, is use the output on two different loads. I know that loads will have to be managed as a single load by the switch.

Is this going to cause a load imballance or something like that on the output side of switches 9 and 10?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

yes, load imbalance is a problem with this so that is why it cannot be done.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

I placed and order (and paid for) for this UTS unit back in early September 2011 and everytime I call to find out status of when it will be coming my dealer keeps telling me that the manufacturer has pushed back the anticipated delivery date agian. Would mind letting me know where you were able to find this unit in stock. Every where I look online it is out of stock. A company name and phone # or website address would greatly appreciated. I can't understand why after 6 months this unit is still out of stock.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

I searched every local equipment company within 3 cities and found a retail outlet that had one from 2010 that had never been open or sold. They had just performed a 5 year inventory and found it. I know that APC has this unit on back order because all available stock was depleted during this winter.
Keep trying and do not get discouraged.
Good Luck in your searching.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

I am having the same problem. I ordered one at the end of September and I'm still waiting for it. Every couple of weeks I get a new expected date that is a few more weeks away. I am on the verge of cancelling my order and going with a traditional transfer switch. At least I know I can get one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

Hold out for APC to replenish their stock. Winter is almost over in most of the country and you will not be disappointed. If your wife or you want more than one backup source with the ability to automatically manage your loads, wait for this one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

0 Likes
0
1998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:01 AM

updated release date now is June 17th.:-( hope this is the last time

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore