Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UTS6H ALM and load shed

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H ALM and load shed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
5
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

UTS6H ALM and load shed

Hi,
I just installed a APC UTS6H (with Hardwire kit) along with a APC BX1000g UPS and a Honda EU2000i. The install was smooth and everything works beautifully. I'm really impressed with this transfer switch and am surprised it isn't advertised more. The average 6 circuit transfer switch runs about $200-300 and the APC blows them all out of the water with it's built in intelligence. I spent the last two days testing everything out for the next power outage and have a question on the ALM time management feature along with load shed. Circuit 4 is my refrigerator(setting of "refrigerator" and "GEN" power) and I have it on the default setting of "delayable" with 30 min off/ 30 min on. I also have load shed and ALM with time management enabled. While testing with the Honda powering the circuits, when the watts approached the 1600 the load shed feature shed the fridge and it said it was in standby. I waited the 30 mins and it did not re enable the circuit. I waited a full hour and it still didn't come back on. I'm trying to figure out the logic.....

The only way the circuit came on was when I changed the circuit label to "Home Theatre" and the circuit clicked on. I reset the panel and re entered all my parameters and the circuit was still off. I then turned utility power back on and reset and the circuit stayed on when I chose fridge. I wonder if I was resetting the 30 minute "off" every time I went to circuit setting? Or maybe I just didn't wait long enough for it to turn back on? I'm sure the logic is fine and I was doing something on my end, but thought I would ask here before I test it again tomorrow. By the way, the panel came with 15 amp fuses and all 6 circuits are off of 20 amp breakers. Do I need to go into the settings and change it to 20 amp for each circuit even though they are 15 amp fuses, or can I leave it be since the 15 amp is more restrictive? My loads had no problems with the 15 amp setting. Awesome UTS and UPS APC, I really like the technology. My neighbors are impressed that I'm powering my house with a Honda EU2000i and it's hands free after starting the generator.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

UTS6 can support up to 20 AMP on each circuit doesn't mean that you should install 20am fuses.  The ampere should match with what you have on the main circuit breakers because when UTS switches to Generator mode, let's say, your generator is capable of providing more than 20 amps, you will be in trouble.  The supposed to be 15-amp circuit is now with 20-amp fuse can draw more than the electrical wire it can handle causing overheat. 

 It should not depend on the rating of the power generator because you might have larger generator in the future.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

Update:

I cured the ALM problem with circuit 4. I purchased a different heavier duty 12/3 cord from generator to outlet and it cured the problem. The 14/3 cable probably couldn't handle the load and caused the algorithm for ALM to shed circuit 4. So everything is working great right now and again really love this transfer switch! Last question is about the 15 amp setting and 15 amp fuses inside the UTS. My 6 circuits are all 20 amp, should I leave the 15 amp setting in the UTS setup or change it to 20 amp even though I only have 15 amp fuses in the UTS? My loads seem to be working fine on the 15 amp setting, but I know the manual says to match your home circuits. Do I have to buy all new fuses? they are pretty expensive. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

i am not 100% sure but i believe you should get 20 amp or else it would technically violate an electrical code to have the fuses the wrong size 😕

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

Thanks for the reply winna:)

I checked my code and the APC UTS wires and switches are rating for 20 amp circuits. So in generator mode my house circuits are rated at 15 amps which is in line with the generator and fuses and is more restrictive than the 20 amp. My generator is also limited to 1600 rated watts, so it shouldn't trip the fuse.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

yep that makes sense!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

0 Likes
0
1993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:24 PM . Last Modified: ‎2024-03-20 03:00 AM

UTS6 can support up to 20 AMP on each circuit doesn't mean that you should install 20am fuses.  The ampere should match with what you have on the main circuit breakers because when UTS switches to Generator mode, let's say, your generator is capable of providing more than 20 amps, you will be in trouble.  The supposed to be 15-amp circuit is now with 20-amp fuse can draw more than the electrical wire it can handle causing overheat. 

 It should not depend on the rating of the power generator because you might have larger generator in the future.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore