UTS10BI and circuits 9 & 10

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI and circuits 9 & 10
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
8
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

UTS10BI and circuits 9 & 10

On the UTS circuits 9&10 work together to power a 240v load... great. But what if you dont have a 240v load to be powered, do you lose the use of these circuits? Can they be used to power a small sub-panel feeding a couple of 120v loads? In other words, does the UTS10BI care about the load balance between the legs of this 240v circuit? ...or can 9 & 10 be used independently each powering separate 120v loads?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • uts
  • uts10bi
  • uts6
  • uts6h
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

i checked on this and was told the 20A 240v subpanel should be okay.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

I was planning on running a 240 subpanel because I have no 20 amp 240 loads in the breaker. I don't see why the uts would care what it powers as long as the main is sending power to a 240 2 pole breaker and the uts is connected using the 9 and 10 in/out wire. That is my take from the manual.
I hope that logic holds true and I can use the subpanel to power a 240 outlet in the garage and 120 connection to a battery charger.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

9 and 10 must be two 120v circuits and they are required to power the UTS itself since it runs off of 240v. the user's guide states: Together, circuits 9 and 10 form a dedicated 240 V circuit. DO NOT use these circuits as individual 120 V circuits.

http://www.apcmedia.com/salestools/ASTE-6Z7VBL_R0_EN.pdf

PDF pg 6.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

Together, circuits 9 and 10 form a dedicated 240 V circuit. DO NOT use these circuits as individual 120 V circuits.
...and that's the source of the original question. So to rephrase: is a 20a 240v sub-panel a dedicated 240v circuit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

i checked on this and was told the 20A 240v subpanel should be okay.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

i picKed a winna wrote:i checked on this and was told the 20A 240v subpanel should be okay.
Thank you. That's good to know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

This sounds like dumb question but I am not an electrician and don’t know much about this kind of stuff but I have questions.

I purchased APC Transfer Switch about a month ago and installed by local electrician.
When he install the unit, we used all 10 circuits include circuit 9 and 10. Where circuit 9 is 120V/15A Bed Rm 2 and 10 is 120V/15A garage. According to him, he reverse the phase between 9 and 10 to have 204V for circuit 9 and 10.

The 10 circuits that we have connected are;
1. Sump pump – 20A
2. Kitchen – 20A
3. Family Rm – 20A
4. Dinning Rm – 15A
5. Rec Rm – 15A
6. Master Bed Rm – 15A
7. Study Rm – 15A
8. Bed Rm 1 – 15A
9. Bed Rm 2 – 15A
10. Garage – 15A

This is OK?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

this is not good. it should be a dedicated 240 circuit required in order to power the UTS. you may run into issues with this, you may not since its designed or tested like this. i would advise that it be set up properly with a dedicated 240v circuit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:17 PM . Last Modified: ‎2024-03-20 03:06 AM

I'm a consumer and not an expert, but my view point from my testing, as long as your bedroom 2 & garage circuits are on opposite legs of the main panel (which you say they are as 240v) and are set to trip together, you should be ok.

The problem comes (in my personal testing is) when the CB's tied to UTS 9 & 10 don't trip together. These two appear to tell the UTS if the main power is out. If only one is tripped, the UTS throws a error.

Make sure your bedroom 2 & garage circuit breakers are next to each other (like CB 1 & 3 for example) and that they are using a 240v breaker or are at least tied together with a tie bar so if one trips, they both trip.

My 2 cents.

-Todd

My advise is from my testing and observations only

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of