Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

UTS10BI and circuits 9 & 10

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: UTS10BI and circuits 9 & 10
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
dBeau_apc
Crewman dBeau_apc
Crewman

Posted: ‎2021-06-29 10:17 PM

0 Likes
8
502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

UTS10BI and circuits 9 & 10

This was originally posted on APC forums on 11/15/2011


On the UTS circuits 9&10 work together to power a 240v load... great. But what if you dont have a 240v load to be powered, do you lose the use of these circuits? Can they be used to power a small sub-panel feeding a couple of 120v loads? In other words, does the UTS10BI care about the load balance between the legs of this 240v circuit? ...or can 9 & 10 be used independently each powering separate 120v loads?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • uts
  • uts10bi
  • uts6
  • uts6h
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This reply was originally posted by Angela on APC forums on 11/17/2011


i checked on this and was told the 20A 240v subpanel should be okay.

See Answer In Context

Reply
Replies 8
codename47_apc
Ensign codename47_apc
Ensign

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This was originally posted on APC forums on 11/17/2011


I was planning on running a 240 subpanel because I have no 20 amp 240 loads in the breaker. I don't see why the uts would care what it powers as long as the main is sending power to a 240 2 pole breaker and the uts is connected using the 9 and 10 in/out wire. That is my take from the manual.
I hope that logic holds true and I can use the subpanel to power a 240 outlet in the garage and 120 connection to a battery charger.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This reply was originally posted by Angela on APC forums on 11/16/2011


9 and 10 must be two 120v circuits and they are required to power the UTS itself since it runs off of 240v. the user's guide states: Together, circuits 9 and 10 form a dedicated 240 V circuit. DO NOT use these circuits as individual 120 V circuits.

http://www.apcmedia.com/salestools/ASTE-6Z7VBL_R0_EN.pdf

PDF pg 6.

Reply
dBeau_apc
Crewman dBeau_apc
Crewman

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This was originally posted on APC forums on 11/17/2011


Together, circuits 9 and 10 form a dedicated 240 V circuit. DO NOT use these circuits as individual 120 V circuits.
...and that's the source of the original question. So to rephrase: is a 20a 240v sub-panel a dedicated 240v circuit?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This reply was originally posted by Angela on APC forums on 11/17/2011


i checked on this and was told the 20A 240v subpanel should be okay.

Reply
dBeau_apc
Crewman dBeau_apc
Crewman

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This was originally posted on APC forums on 11/17/2011


i picKed a winna wrote:i checked on this and was told the 20A 240v subpanel should be okay.
Thank you. That's good to know.

Reply
KyeLee_apc
KyeLee_apc
Cadet

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This was originally posted on APC forums on 10/23/2012


This sounds like dumb question but I am not an electrician and don’t know much about this kind of stuff but I have questions.

I purchased APC Transfer Switch about a month ago and installed by local electrician.
When he install the unit, we used all 10 circuits include circuit 9 and 10. Where circuit 9 is 120V/15A Bed Rm 2 and 10 is 120V/15A garage. According to him, he reverse the phase between 9 and 10 to have 204V for circuit 9 and 10.

The 10 circuits that we have connected are;
1. Sump pump – 20A
2. Kitchen – 20A
3. Family Rm – 20A
4. Dinning Rm – 15A
5. Rec Rm – 15A
6. Master Bed Rm – 15A
7. Study Rm – 15A
8. Bed Rm 1 – 15A
9. Bed Rm 2 – 15A
10. Garage – 15A

This is OK?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This reply was originally posted by Angela on APC forums on 10/23/2012


this is not good. it should be a dedicated 240 circuit required in order to power the UTS. you may run into issues with this, you may not since its designed or tested like this. i would advise that it be set up properly with a dedicated 240v circuit.

Reply
Boatingrtb_apc
Lieutenant JG Boatingrtb_apc
Lieutenant JG

Posted: ‎2021-06-29 10:17 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:17 PM

This was originally posted on APC forums on 10/27/2012


I'm a consumer and not an expert, but my view point from my testing, as long as your bedroom 2 & garage circuits are on opposite legs of the main panel (which you say they are as 240v) and are set to trip together, you should be ok.

The problem comes (in my personal testing is) when the CB's tied to UTS 9 & 10 don't trip together. These two appear to tell the UTS if the main power is out. If only one is tripped, the UTS throws a error.

Make sure your bedroom 2 & garage circuit breakers are next to each other (like CB 1 & 3 for example) and that they are using a 240v breaker or are at least tied together with a tie bar so if one trips, they both trip.

My 2 cents.

-Todd

My advise is from my testing and observations only

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.