Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82583members
350212posts

UTS10BI - Doubling up circuts

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
javf_apc
Cadet
0 Likes
3
138

UTS10BI - Doubling up circuts

This was originally posted on APC forums on 8/28/2015


I am in the process of installing a UTS10BI and have seen some postings regarding "doubling up" low-usage circuits. I have a few low usage circuits (mainly lights) that I would like to combine on one of the UTS circuits. Is this doable and if so how would the wiring look?

Thank oyu for your time.

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
138

Re: UTS10BI - Doubling up circuts

This reply was originally posted by Bill on APC forums on 2/1/2016


Hi,

The below information in bold is from the installation guide

Safety Precautions:

• Adhere to all national and local electrical codes when installing, configuring and operating the UTS.

• Installation of the UTS must be performed by a licensed electrician.

Any configuration that does not meet national and local code will void any warranty. 

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
138

Re: UTS10BI - Doubling up circuts

This reply was originally posted by Craig on APC forums on 1/31/2016


I would very interested in an official response from Schneider on this question.

Tags (1)
wayne_i_apc
Lieutenant
Lieutenant
0 Likes
0
138

Re: UTS10BI - Doubling up circuts

This was originally posted on APC forums on 2/1/2016


I need to ask what is meant by "doubling up" circuits? The UTS can ONLY have a one-to-one connection of each input connection to a circuit breaker (in other words, for a UTS10BI, circuits 1 - 8 each to a 120V single pole breaker and circuits 9 and 10 to each pole of one 240V double pole breaker, exactly as shown on the UTS wiring diagram), and the output connections only connected to a load circuit, where the load circuit's current and wire size are appropriate for the UTS's circuit capacity and the circuit breaker in the panel feeding the respective UTS input (think local and National Electrical Codes here).

If you rewire your circuits by disconnecting the wire from multiple "low-usage" circuit breakers in your breaker panel and connecting them to a single UTS output, this is obviously a permanent change to your (home's) wiring. Again, consider the resulting circuit's current and wire size(s), and adhere to electrical codes.

NEVER DO IT!!! (don't even THINK about doing it!)-- if "doubling up" means connecting more than one circuit breaker to a single UTS input, or connecting an output of the UTS to ANY other source of power or other powered circuit. I can't think of any other configuration that could be considered "doubling up".

There is NO way to wire the UTS to provide a back-up feature to any circuits that are NOT supplied by circuit breakers connected to the UTS inputs as shown on the UTS wiring diagram.

If you are not familiar with electrical codes or how transfer switches work you should consult with a qualified electrician about making changes to your UTS installation. Very, very bad things can happen if you do something wrong!

DISCLAIMER: I am an owner of a UTS, not associated with APC, and NOT recommending anyone make the wiring changes described above.

BillP
Administrator Administrator
Administrator
0 Likes
0
139

Re: UTS10BI - Doubling up circuts

This reply was originally posted by Bill on APC forums on 2/1/2016


Hi,

The below information in bold is from the installation guide

Safety Precautions:

• Adhere to all national and local electrical codes when installing, configuring and operating the UTS.

• Installation of the UTS must be performed by a licensed electrician.

Any configuration that does not meet national and local code will void any warranty.