Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS on power backup with a cut-off limit - ACP BR1500G

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS on power backup with a cut-off limit - ACP BR1500G
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

0 Likes
5
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

UPS on power backup with a cut-off limit - ACP BR1500G

Hi,

I am planning to buy a Dell Workstation that draws 750 watts of power. The place where I stay has a power problem and there are regular power outages that can sometime last up to 4-5 hours. Fortunately, my apartment building has a diesel generator that provides power backup for as long as there is a power outage. The only problem is that there is limit to which you can draw electricity when the backup generator in running. The cut-off limit is 400 watts. If the consumption in a household crosses 400 watts then the power supply trips and it can only be resumed by going all the way downstairs and flipping up a MCB switch.

Now, I need to keep running my workstation even during power outages. But since the workstation draws 750 watts, it will trip the backup power supply when the backup generator is running. So I am thinking of getting myself the ACP BR1500G-IN 1.5 KVA UPS to solve this problem.

My question is: How much power will this UPS draw? I need to know this, because, if it draws more than 400 watts then it will trip the power supply and my problem will remain unresolved. If this model will not help me, then is there any other model that draws less than 400 watts but gives an output of 750watts?

Look forward to all your replies.

Thank you in advance
Nik

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

Thank you for clearing this up.

This would mean that I cannot run the workstation on an UPS. Though the actually power consumption may be less than 750w, it certainly cannot go below 400w.

Thanks again for your help

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

Thank you *'I picked a winna'* and *'voidstar'*.

Now I know that the UPS would need only about 30w to keep charging. So it means that it can keep charging on the generator power and at the same time also run the workstation.

Also, perhaps I wasn't clear in my explanation, but I 'do not' want the UPS to run on the battery at all. I want it to run on the main supply and during outages I want it to run on the generator power.

So, to restate my question: Will the ACP BR1500G-IN 1.5 KVA UPS keep drawing 30 watts of power from the generator and continue charging, while it is being loaded by a workstation drawing 750 watts of power?

Thanks again for all your support.

Note: The backup generator is actually an industrial scale generator generating enough power to provide 400 watts of power to 240 apartments (400x250=100kW). Plus it can also run about 6 escalators. The only problem is that one apartment cannot draw more than 400w, during outages.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 03:00 AM

no, it definitely does not. the most that it should be using would be an extra 30W while it is charging the battery. beyond that, we'd just need to account for the efficiency of this UPS which seems to be almost 100% (85%) meaning there is not much power coming into the UPS that does not leave to support the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

>
...is there any other model that draws less than 400 watts but gives an output of 750watts?
>

I think there are a lot of people who would love a UPS that exceeds 100% efficiency ๐Ÿ™‚

Maybe another way to think about it is you want a UPS that runs on battery when the generator is operational. Our line-interactive UPSes may do this if you set the UPS to high sensitivity and your generator produces dirty power (typically the case). But we can't guarantee it; we prefer that our UPSes accept generator power rather than going to battery.

I think getting a generator that can produce more power is a safer option.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

Hi Nik,

>
Will the ACP BR1500G-IN 1.5 KVA UPS keep drawing 30 watts of power from the generator and continue charging, while it is being loaded by a workstation drawing 750 watts of power?
>

When the UPS runs on generator, the total draw from the generator will be, at most, 30W (UPS) + 750W (Computer) = 780 W. That's more than the 400W provided for your apartment, but it's also a worse case. You'd have to measure the computer's actual power consumption to see if you can get under the 400W limit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:15 PM . Last Modified: โ€Ž2024-03-21 02:59 AM

Thank you for clearing this up.

This would mean that I cannot run the workstation on an UPS. Though the actually power consumption may be less than 750w, it certainly cannot go below 400w.

Thanks again for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore