UPS choice for router & generator in desert location

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS choice for router & generator in desert location
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
118
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
10
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

UPS choice for router & generator in desert location

I need to set up a network for a school in a remote desert area. The only electricity is a 240v generator which runs about 3 hours per day. It was suggested that I could hook up a UPS to the generator, then power the router directly from the UPS (standard Linksys 802.11n probably). So three questions:

1 - Which model UPS, if any, would be effective for a solution in this situation?
2 - How long will it take to charge the UPS?
3 - How long can I expect the UPS to power the router between charges?

Thanks,

-sd

Message was edited by: hofendisapc

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • desert
  • generator
  • router
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

For so little current i recomend you try installing a solar/eolic solution with a propper filtered inverter and a battery bank sized according wind-solar energy in the zone.

You should use an online UPS genset compatible, for 240V you should use: SURT1000XLI. Small size gensets are poor in quality and stability and if chosen badly you will degrade the UPS prematurely.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

The answers to 2 and 3 depend on the answer to 1, but there isn't enough information to answer that question. Is the router the only thing on the UPS? What does the router require for power (240, 208, 120)? And what plug type?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

Most of the routers that I've looked at are 12V 1.5A. But the power supplies are (or will be) 110-240V adapters. I would think that if we're trying to run this off of a UPS, we'd dedicate the UPS to only this router.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

If I may interject, the UPS batteries are designed to be kept charged. Discharging those batteries every day may lead to premature battery failure. So, if you go that route, I'd make sure the batteries never completely discharge (they like that even less) and be prepared for the cost of replacing them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

The smallest model that's designed to take 240v input is the [SURTD3000XLT|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURTD3000XLT]. By itself, it will output either 208 or 240v. Pretty expensive solution for just one router though...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

Thanks, but that's not accurate. There are a wide number of smaller APC models that take 240v, for instance the ES-325-GR. (Sorry, should have mentioned that the desert location is not in the US. APC makes lots of models for non-Northern America locations.)

So we've narrowed the question down a bit. What size UPS to run something offline that uses 12v 1.5A? And how long does the UPS take to get a full charge?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

(double post)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

That model is 230v in/out, which is international voltage, not 240v, which is US. So you want 230v then? Where is it located? What plug type does it need to connect to the wall? Are you going to custom-wire an outlet for this UPS that is powered by the generator so the plug type is irrelevant?

While the 325 model you mentioned would support the router in terms of capacity, that family doesn't play very well with generators. Depending on the size of the generator (typically you want them oversized a bit), you might be able to use a model in the Back-UPS RS family, though Smart-UPS models seem to handle generator power best. Others keep switching between on battery & online.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

A better question is how many hours a day are you expecting the UPS to provide power to this router? Most UPS are designed to provide power for a short period of time 10-30 mins. If you need to get hours of runtime from a UPS you would probably have to buy a much larger UPS than you need and additional battery components.

However if you fully discharge the batteries each day I don't think 3 hours would be enough to recharge them each day. Also you are going to go through alot of batteries if you charge/discharge them each day. Plus I would guess there is no A/C in this room so you are going to have your batteries deplete even faster becasue of the high temp.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

present 2010model is better for UPS.what i am saying is usp gives back up to the computer, when i am playing the online gaming, ups plays key role in preventing power problems.
Golddigger l [Online casinos|http://onlinecasinorsk.blogspot.com/]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

0 Likes
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:15 AM . Last Modified: ‎2024-03-22 01:35 AM

For so little current i recomend you try installing a solar/eolic solution with a propper filtered inverter and a battery bank sized according wind-solar energy in the zone.

You should use an online UPS genset compatible, for 240V you should use: SURT1000XLI. Small size gensets are poor in quality and stability and if chosen badly you will degrade the UPS prematurely.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore