Back UPS and PFC Power Supplies

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS and PFC Power Supplies
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
5
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

Back UPS and PFC Power Supplies

I am quoting Erasmus from a post made almost a year ago, on 4/27/2009:

"Starting in mid 2008 all of our Back-UPS products being manufactured were revised to better handle load requirements for PFC devices, both through small firmware and hardware revisions. This allows the majority of Back-UPS being manufactured now to handle most (not all) PFC loads within their wattage range much better than older units. Their output is still stepped-approximated, however, and we still find the occasional PFC device that they have trouble with, especially those with high inrush currents or those that are just plainly "oversized" in relation to the UPS."

For the full discussion, see: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/2271/couple-questions-just-go...

Does this mean that APC will honor its warranty when a properly-sized Back-UPS is used with a PC that has a PFC power supply?

"This allows the majority of Back-UPS being manufactured now to handle most (not all) PFC loads within their wattage range..."

Which specific models of Back-UPS are not included in "... the majority of Back-UPS being manufactured now..."?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • pfc
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

Don't you feel that APC has a responsibility to inform consumers that a Back-UPS unit may not power their computer or cause it to reboot if the computer has a power supply that requires a pure sine wave UPS?
Yes, definitely. Anyone who calls into APC for sizing will field questions about the equipment going on the UPS, one of which is about the pure vs modified sine wave. Hopefully customers are willing to take the time to do the research with APC, either knowing this beforehand, following through with PSU manufacturers to find out, or working with APC on the phone to find out the specs needed.
Otherwise, do you feel APC is misleading consumers by recommending Back-UPS units?
If someone at APC recommends a Back-UPS product for a computer knowing that it needs a pure sine wave, that would obviously be misleading. I don't think anyone would do this intentionally, though not asking the right questions could pose an issue.
If a customer buys a correctly sized Back-UPS from APC, tests the UPS on their PFC-equipped computer, and discovers that the Back-UPS either does not provide power or causes their computer to reboot, will APC issue a full refund upon return of the unit in re-saleable condition?
As long as it's still within the 30 day return period, of course. There's usually a 15% restocking fee on returns, but it's possible for that fee to be waived. It's not the customer's fault if someone at APC recommended the wrong unit (though a case number - provided for every sizing call - would help back up your story). I'm assuming by "correctly sized," you meant it was recommended by APC. However, if the customer bought it without contacting APC to ask about compatibility, the fee wouldn't likely be waived.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

There isn't a comprehensive list of power supplies that are considered "compatible" with the Back-UPS products. Your best bet would be examining the power supply's requirements in terms of step-approximated vs pure sine waves - that seems to be the latest obstacle. Some computers will work fine with a Back-UPS product until it's had time to "break in," at which point the step-approximated sine wave offered by the Back-UPS won't suffice.

Using a PFC PSU with a Back-UPS won't void your warranty or anything, but it isn't considered a product defect if it doesn't keep your computer on (assuming it DOES power other things for testing, like lamps, radios, etc). The units are better designed to attempt to handle newer technology and PFC requirements, but at the same time, PSU manufacturers are doing the same by making units that have higher demands for proper functionality.

Personally, I've heard Enermax PSUs don't like anything less than a pure sine wave... Along with some HP systems (I've had issues with the HP DC5800 in particular) and some Dell XPS systems. And, of course, servers. My OCZ 600w PSU works fine - it's on a BR800BLK. I know someone with an Antec that buzzes obnoxiously but otherwise works fine (also on a BR800). The PSU manufacturers would be the best source, though.

I wouldn't suggest a BE model. They've got the longest transfer times and the smallest capacities. I'd recommend something in the BR line for a PFC unit, though still, some PSUs don't like the step-approx sine wave, so it may not work for sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

"Why rule out the Back-UPS as an option for everyone when it works for many users..."

For many users...but not for all. Don't you feel that APC has a responsibility to inform consumers that a Back-UPS unit may not power their computer or cause it to reboot if the computer has a power supply that requires a pure sine wave UPS? Otherwise, do you feel APC is misleading consumers by recommending Back-UPS units?

If a customer buys a correctly sized Back-UPS from APC, tests the UPS on their PFC-equipped computer, and discovers that the Back-UPS either does not provide power or causes their computer to reboot, will APC issue a full refund upon return of the unit in re-saleable condition?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

Increasingly, home and small office computers are shipping with power supplies that are not compatible with the UPSes that APC markets to home and small office users. This trend is not going away.

Where does this leave the consumer?

I have yet to read a statement from APC saying: "Attention - If your computer has a PFC power supply, do not purchase a UPS from the Back-UPS product line. Only a Smart-UPS product will protect your computer."

Instead, I have read a lot of hemming and hawing and hedging...yes, the Back-UPS were improved in mid-2008 to work better with PFC power supplies, but we're still seeing problems, sometimes...yes, your warranty is still good, even though Back-UPS was not designed for your power supply/no, your warranty may not be good...

When is APC going to step up to the plate and tell consumers the straight story?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

Like I said, it depends on the PSU manufacturer - it's not just whether or not the PSU has PFC. The PFC factor alone mostly just requires a bit of oversizing to allow for inrush current. The issue is the sine wave. If a manufacturer says "this PSU is not designed to work on a step-approximated (or otherwise modified) sine wave," then it won't work with a Back-UPS. My PSU IS PFC and it works fine with a Back-UPS. Why rule out the Back-UPS as an option for everyone when it works for many users and is not a flaw with the UPS itself?

I kind of doubt people would be happy stepping up to a $300 Smart-UPS for their home computer simply because APC assumes no PFC PSU can operate with a step-approx sine wave, especially since that isn't the case. And the Smart-UPS (and higher) models are the ones that produce a pure sine wave.

I think it leaves the consumer in the position most find themselves when trying to make the "right" purchase - having to do a bit of research to make sure it's what they want/need. I can't speak for everyone, but I hope people don't just grab a random camcorder off the shelf and wait to ask questions until they're on vacation trying to use it. APC's number is 800-890-4272 for anyone who wants a recommendation, or help getting started in the right direction to know what questions to ask.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

0 Likes
0
1667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:14 AM . Last Modified: ‎2024-03-22 01:36 AM

Don't you feel that APC has a responsibility to inform consumers that a Back-UPS unit may not power their computer or cause it to reboot if the computer has a power supply that requires a pure sine wave UPS?
Yes, definitely. Anyone who calls into APC for sizing will field questions about the equipment going on the UPS, one of which is about the pure vs modified sine wave. Hopefully customers are willing to take the time to do the research with APC, either knowing this beforehand, following through with PSU manufacturers to find out, or working with APC on the phone to find out the specs needed.
Otherwise, do you feel APC is misleading consumers by recommending Back-UPS units?
If someone at APC recommends a Back-UPS product for a computer knowing that it needs a pure sine wave, that would obviously be misleading. I don't think anyone would do this intentionally, though not asking the right questions could pose an issue.
If a customer buys a correctly sized Back-UPS from APC, tests the UPS on their PFC-equipped computer, and discovers that the Back-UPS either does not provide power or causes their computer to reboot, will APC issue a full refund upon return of the unit in re-saleable condition?
As long as it's still within the 30 day return period, of course. There's usually a 15% restocking fee on returns, but it's possible for that fee to be waived. It's not the customer's fault if someone at APC recommended the wrong unit (though a case number - provided for every sizing call - would help back up your story). I'm assuming by "correctly sized," you meant it was recommended by APC. However, if the customer bought it without contacting APC to ask about compatibility, the fee wouldn't likely be waived.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore