UPS Overload

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS Overload
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

0 Likes
1
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

UPS Overload

A week or so ago, my APC UPS took a lightening strike and did not function as it should and the power went out and all attached devices lost power. After about a week, the UPS went into "overload" status and removing load and rescharing batteries without load did not fix the problem. Unbfortunately, I spent $72.00 on new batteries and the problem still persists. So what other options do I have? Can it be repaired? Do I have to buy a new UPS? Can I buy one without batteries?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

Alvin,

I apologize for the inconvenience this has caused you. Before we proceed I would like to know if the equipment attached on the UPS were damaged when you got hit by lightning. From what I can see, the UPS has took the surge and sacrificed which then led to its failure.

Regarding your questions, the UPS that we are selling comes with batteries on them. The other options that you can choose are:
# Purchasing a new UPS through our Trade-UPS program. The APC Trade-UPS program* is a cost-effective way to upgrade your \\ existing units and protect your latest investment. Trade in any UPS, \\ regardless of its manufacturer or its working condition, for the latest \\ APC UPS technology and receive up to a 25% discount on your new purchase. To know more about APC Trade-UPS please click here and here. Once you are decided to go with the Trade-UPS please do not hesitate to call our toll-free hotline at 1-800-800-4272.
# If you would like to have your UPS repaired you can try to reach our authorize APC UPS Repair Center which is Coastal Business Machines. Unfortunately I do not have any details on how much it would cost. Please visit their website to know more about them, they can be reached at [www.cbmi.com|http://www.cbmi.com/].
JonPro

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

0 Likes
0
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:11 AM . Last Modified: ‎2024-03-22 02:46 AM

Alvin,

I apologize for the inconvenience this has caused you. Before we proceed I would like to know if the equipment attached on the UPS were damaged when you got hit by lightning. From what I can see, the UPS has took the surge and sacrificed which then led to its failure.

Regarding your questions, the UPS that we are selling comes with batteries on them. The other options that you can choose are:
# Purchasing a new UPS through our Trade-UPS program. The APC Trade-UPS program* is a cost-effective way to upgrade your \\ existing units and protect your latest investment. Trade in any UPS, \\ regardless of its manufacturer or its working condition, for the latest \\ APC UPS technology and receive up to a 25% discount on your new purchase. To know more about APC Trade-UPS please click here and here. Once you are decided to go with the Trade-UPS please do not hesitate to call our toll-free hotline at 1-800-800-4272.
# If you would like to have your UPS repaired you can try to reach our authorize APC UPS Repair Center which is Coastal Business Machines. Unfortunately I do not have any details on how much it would cost. Please visit their website to know more about them, they can be reached at [www.cbmi.com|http://www.cbmi.com/].
JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore