UPS For a basement sump pump, which one?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS For a basement sump pump, which one?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
5
34316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

UPS For a basement sump pump, which one?

Hi, I have a question, this seems really odd but I know I cannot be the only one but I do not seem to find any information for this anywhere.

Anyway, I am a computer programmer, I recently bought a nice house in the country with a basement. All has been good with the new house until recently. We seriously got over 5 ft of snow here in december and then the weather warmed up dramatically which melted all the snow, the heat wave also came in with a sudden rainstorm that soaked the ground and added more water to the melting snow. This left a lot of water seeping into the basement, which the sump pump was more than happy to handle. That was until that night some time in the middle of the night the power got knocked out and was out for 8 hours. Well for heat there was no big deal I have a fireplace, However after i got power back I decided to go down to the basement and when i stepped down, the carpet was wet. Then it dawned on me, no power, and the sump pump can't pump out the water. So after i cleaned up the mess i instantly thought battery backup for the sump pump. Eventually I will get a generator but that is a year or two down the road. Plus I would have to be home to switch over to generator so I would need a battery backup on the sump pump.

Anyway, all APC battery back ups are for computers. I do not see why I couldn't use one for a sump pump but which one? I can't unfortunately give you a lot of info on the electrical workings of the sump pump. What I can tell you is it plugs into a regular outlet on the wall so it is 120 volt. I know it is able to pump out about 15 gallons in just a few seconds. Basically all it does is during a severe storm it might fire up once or twice every hour for about 3-4 seconds and thats it. So basically i just need a Battery back up that can last through a storm, I am not sure how long i would be without power but the longer this could last the better.

Anyway any ideas on what I should use?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

Been there, done that! You're best choice, as others suggested, is a backup 12v pump & battery and good maintenance charger (one that lowers the trickle charge voltage as the battery reaches capacity....otherwise you'll find that the battery deteriorates). I ran this same setup for a period of years, and IF a long power outage depletes the pump battery, simply run a wire to your car and use it to top up the pump battery. Also, your total cost will be much less than what a "Super-Size-UPS" might cost!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

Been there, done that! You're best choice, as others suggested, is a backup 12v pump & battery and good maintenance charger (one that lowers the trickle charge voltage as the battery reaches capacity....otherwise you'll find that the battery deteriorates). I ran this same setup for a period of years, and IF a long power outage depletes the pump battery, simply run a wire to your car and use it to top up the pump battery. Also, your total cost will be much less than what a "Super-Size-UPS" might cost!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

been there, done that as well... We have a Craftsman model that came with a charger, DieHard Gold Marine Battery, battery box, pump and float.

works great for us.

worth noting however, the one we have will set off an alarm every time the pump is activated, Highly annoying, although it was being set off, not because of a power failure, but because the main pump float had become waterlogged, and tit not have enough buoyancy to trigger the switch on the pump. don't think the alarm ever went as a result of a power failure, but not sure.

FYI, you want a Marine battery and not an automotive one because the power draw is very different.

Cars need a very short burst of very high amperage. they are made with thinner lead plates to get more of those "Cold Cranking Amps" marine batteries have thicker lead plates, and are designed to handle a longer draw at a lower amperage. (an RV would use marine batteries to power 12v lighting, and 120v AC inverters and such like that....

I have also heard that there are backup systems that rely on the water pressure of the municipal water supply. IIRC, they will remove like 2-3 gallons of water for every gallon they allow to flow into the sump. although with a larger-scale blackout, you could still be SOL if the muni water pressure drops, as in the 2003(?) northeast/midwest blackout.

I think I saw something that said you could hook a couple of marine batteries in parallel to get either more amps, or more run-time. If you expect extended outages to be a serious problem, you may want to look into it. connect the batteries, positive pole to positive pole, Negative to negative, and they also said it's best to connect the positive and negative leads from the charger to opposite ends of the bank.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

Seriously, a big UPS to do that task.

Hello from no problems with damp inland Eastern Australia here at 35°C.

The problem could be the surge demand placed by the pump motor as it starts, now you system is 110/120, here it's 240/480 and the surge currents to start an electric motor are much higher for you for the same power // Watt.

I have a 5.9kVA Honda powered backup generator which is divert wired into our office, workshop and home, it just starts a 2HP single phase air compressor and really struggles with a new 1.5HP submersible well pump 100m down the paddock. All the other appliances are easy, refrigeration, lights home theatre, server and full network, we don't use any Air Conditioning at all - ever.

Someone from APC should be by to let you know which one you'd need, but at a guess I reckon the petrol genset is going to be streets cheaper!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

yeah, APC doesnt really recommend a UPS for a sump pump due to the type of load it is.

but, IF you plan on doing it anyway, you will need something a bit beefy to account for the inrush current of the device. from experience, with your average sump pump, i'd start looking at something like an [SUA2200 Smart UPS|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA2200].

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

0 Likes
0
34305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-22 04:23 AM

I dont think that APC backup units are made for this usage

You should check for a backup pump with a marine battery.

I Have one and it's the perfect solution.


http://www.flotecwater.com/pdf/Pg_8_2006.pdf


Carpediem

Message was edited by: carpediem99

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.