Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

UPS ES 350 shutdown

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS ES 350 shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
5
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

UPS ES 350 shutdown

I guess I made the mistake of getting this battery as the salesman said it was the most popular for what I needed. However, now I find out it doesn't have automatic shutdown software.

So what happens if I'm gone and the electricity goes out? Does it just do a hard shutdown or what? And if it does, then every day when I go to work I'll have to shut the computer down, I guess?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

0 Likes
0
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

I guess I made the mistake of getting this battery as the salesman said it was the most popular for what I needed. However, now I find out it doesn't have automatic shutdown software.

So what happens if I'm gone and the electricity goes out? Does it just do a hard shutdown or what? And if it does, then every day when I go to work I'll have to shut the computer down, I guess?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

Yes Jon, thanks very much. The model number is BE 350G.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

0 Likes
0
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

Thanks. I did checked the BE350G and unfortunately this particular unit does not offer/ have data port that would make the UPS communicate with a PC. The data port is important since this is where you are going to connect the RJ45-USB cable going to the UPS. Have you asked the salesperson if you can have the unit exchanged with a different model?

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

0 Likes
0
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

Jon, unfortunately I've already got it connected so I doubt that they would take it back. I'll try and call them. I purchased it from Batteries Plus. My last battery was a cyberpower and it had the USB capability, so dummy me never thought to ask them about this. I just assumed the APC would have it also. Ummmmm, I was wrong. I'm still learning in my old age...heh heh.

So my thinking was that I could somehow create some kind of script (I know NOTHING about script) and find someone who could maybe figure out that when it's on battery power for, say, 5 minutes, the PC would automatically shut down.

I DID learn something last night though. I was playing around trying to configure the battery and in the power options and made a major boo-boo by giving myself 2 minutes to shutdown, thinking that it had something to do with the battery power......Nooooooo.... What it did was cause a constant loop from the time the PC came on to the time it shutdown, was not enough time to go back into the control panel to change it back. That was REALLY fun.....sigh. But I finally fixed it. Won't play with THOSE controls again, lol.

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

0 Likes
0
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

I hope everything is in order with your PC settings. Unfortunately, our UPS communicates with the PC using the data port and the cable without these it would not be able to send signal and provide it's current state. I haven't tested creating a script using the Native options without the cable. Let us wait and see if some other posters have done this in the past.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:39 AM . Last Modified: ‎2024-03-22 01:18 AM

I guess I made the mistake of getting this battery as the salesman said it was the most popular for what I needed. However, now I find out it doesn't have automatic shutdown software.

So what happens if I'm gone and the electricity goes out? Does it just do a hard shutdown or what? And if it does, then every day when I go to work I'll have to shut the computer down, I guess?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of