UPB70 powers off at ~30 seconds...

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPB70 powers off at ~30 seconds...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

0 Likes
12
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

UPB70 powers off at ~30 seconds...

Mu UPB70 will stay on for maybe 30 seconds and shut off, and will not pass voltage if hooked to charger. All 4 LEDS are on.

Message was edited by: mikeypizano

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Must be a four year thing! My UPB70 is also four years out of the box and has the same symptom. Like many folks on this thread, I really like the unit and would love a fix...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

Hi, do you have a serial number on your unit? Also what kind of laptop/device are you hooking it up to and what did you select for an output voltage setting? Have you always used the correct tip for the device you have powered using the UPB?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

Serial is: 6a0639b 09884

Using it with various laptops with correct tips and voltage settings. It used to work fine but I had stopped using it for a bit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

It is possible the internal battery is bad, since the unit is about 4 years old. It's hard to say for sure though and there isn't a lot more troubleshooting to be done considering how little control there is over these units. Unless the UPB is getting hot or there is a short or feedback of some kind coming from the charger FOR the UPB or to/from the laptop...there isn't much more that would just cause it to shut down in 30 seconds. Sleep mode takes 15 minutes to engage. I would call into tech support and check on the warranty status of this unit to see if it is replaceable. Since it is 4 years old I highly doubt it, unless you have a proof of purchase that shows it was bought within the last year.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:05 AM

It is 4 years old. I did some tests, and off the laptop charger, with a multimeter will show output for 30 seconds then drop to 0. The battery gauge shows it as being full. It is not getting hot or making strange noises so I am stumped.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

Yea...sounds like you should check your warranty (if you bought it within a year it will be covered if you have a proof of purchase) or purchase a replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

Maybe I will take it apart and try putting new cells in it. Are they LiPo or Li-ion?

Heres a video of the actual problem:

http://www.youtube.com/watch?v=TUbL6L_RwmI

Message was edited by: mikeypizano

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:49 PM . Last Modified: ‎2024-03-20 06:04 AM

Not that I have any personal reservations of my own to helping you with this, but APC cannot divulge information about internal parts and we cannot assist customers with any procedures along the lines of what you want to do, unfortunately. I will say, however, that googling the product will give you the battery type and some other specifics you may be curious about.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Yeah I assumed that much already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Were you successful in finding a battery? I have the same issue and have really enjoyed this unit up until this happened.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Hi Mike,
Did you ever resolve your problem? I am experiencing the same issue! Like you I bought my UPB70 about 4 years ago. I used it only occasionally but stopped for a while unitl recently only to find out now it doesn't work anymore. My unit would turn off after about 6 seconds. I watched your video. Though you mentioned 30 sec in your posting, your video shows only 6 seconds just like mine.
Thank you
Alex

Message was edited by: luckypal777

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Hallo,
I have also this problem. Please do not destroy your unit there is a hope to restore it.
Thanks the startup check the UPB70 control the quality of batteries.
If one or more are demaged the test fails and the UPB70 switch off automatically.
I've opened my unit and find one battery (six inside) demaged (smell of acid and it was inflated.
I'm trying to buy new battery from China producer. If I will success I will replay to confirm the possibility to repair the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Must be a four year thing! My UPB70 is also four years out of the box and has the same symptom. Like many folks on this thread, I really like the unit and would love a fix...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore