BE750G-ES problem : constant tone on power failure, no backup power supplied but battery shows 12V..

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE750G-ES problem : constant tone on power failure, no backup power supplied but battery shows 12V..
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
3
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

BE750G-ES problem : constant tone on power failure, no backup power supplied but battery shows 12V..

I purchased a BE750G a while back, recently the unit died on me and the device is out of warranty as I cant find the exact date of purchase vs manufacture and it's over 3 years old by APC's logs. I have a basic education in electronics repair and feel confident in troubleshooting this device with the manual provided by APC. However I cannot find anything in the manual that seems to match the behaviors that I'm experiencing with my particular unit.

In a nutshell my power went out in a storm and the unit failed to supply backup power to my devices. The laptop power supply was plugged into the master and the master enable LED was lit up along with the power LED, after the power went out the power LED went off, the master enable LED remained on and the unit made a constant tone. I had to press and hold the power button for several seconds to stop the tone and until the power came back at the house if I tried to power on the unit 'cold' it would just emit a droning tone until turned back off, the master enable light would turn off and on if pressed. At no point does the device provide backup power to any socket regardless of master enable being on or off.

In the past when the power goes out the unit would make a tone every so often to let me know it was on battery power and would support my devices for a short period of time. Now it just works as a power strip and when the power goes out the unit just dies, makes a noise until I cut it off and no power except that provided to the master enable LED.

At first I was curious to see if the battery was the problem but the battery is showing 12V when removed from the unit and tested with a multimeter. The battery also seems to hold that voltage if removed and let sit so I don't think the battery is defective. I pressed the breaker reset, removed the battery and held the power button to discharge the unit and reattached the battery, etc - nothing changes the cold start behavior. I'm wondering if the unit's logic board is just shot or if there's something I can do to fix the problem. As the manufacture date is over 3 years old and I have no chance in finding the receipt to try and get a repair I'm looking for any help. If it's a bad fuse or available component I can solder / replace it so that's not an issue if it comes down to it. However I'm not familiar with single points of failure on these devices so any help would be great.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 750
  • 750es
  • 750g
  • be750g
  • be750g-cn
  • failure
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

It is not the battery, I ran some tests and had these results :

1. I obtained a known working APC battery to an identical model UPS unit.

2. I fulled charged the battery with a working unit. Said working unit will beep 4 times every 30 seconds when power is disconnected and supplies backup power as it should.

3. I disconnected the old battery and installed the replacement into the unit that was making the constant tone on power failure hereafter referred to as the malfunctioning unit.

4. I turned the malfunctioning unit on and it proceeded to give me the same beep then constant tone until I turned it off. No change at all.

5. I disconnected said battery, the new and fully charged battery, and installed it in a known working APC UPS.

6. I tested the new, fully charged, replacement battery in a known working unit and it functioned perfectly. 4 beeps every 30 seconds, power supplied to devices.

7. I took the battery from the malfunctioning unit and put it into the known working unit and charged it for 16 hours.

8. I removed the battery, installed it back into the malfunctioning unit and again - beep then constant tone until turned off.

So no matter what battery is in the UPS, it just cuts on and makes this constant tone unless it's being supplied AC power from a wall socket.

I would like to correct my OP, the master enable light will not turn off or on while the unit is on. The unit just shows a light and makes a constant tone.

I do have some college education in electronics fundamentals so I discharged the unit and opened it up with some heavily insulated gloves on and noticed no loose connections, visible damage, burning, swollen / plagued caps, or anything that looks out of the ordinary. The board looks about perfect, not even dust.

Unless someone knows of something I'm just missing, I'm stumped.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

Hi Foodude,

I am by no means an expert on this particular APC UPS or the function of its lights and buttons, but I would be concerned if your battery is only showing 12V when removed from the unit and unloaded.  Float charge level on a 12V battery should be around 13.5 volts or better when it is fully charged.  And with three years already on the battery, it may be time for a replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:04 AM

I was thinking the same. It also sounds like the battery cannot support any load and with this type of behavior after 3 years, it could be needing a battery replacement. What happens if you turn it on and pull the plug with no load on the battery outlets? Does the UPS turn off?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

It is not the battery, I ran some tests and had these results :

1. I obtained a known working APC battery to an identical model UPS unit.

2. I fulled charged the battery with a working unit. Said working unit will beep 4 times every 30 seconds when power is disconnected and supplies backup power as it should.

3. I disconnected the old battery and installed the replacement into the unit that was making the constant tone on power failure hereafter referred to as the malfunctioning unit.

4. I turned the malfunctioning unit on and it proceeded to give me the same beep then constant tone until I turned it off. No change at all.

5. I disconnected said battery, the new and fully charged battery, and installed it in a known working APC UPS.

6. I tested the new, fully charged, replacement battery in a known working unit and it functioned perfectly. 4 beeps every 30 seconds, power supplied to devices.

7. I took the battery from the malfunctioning unit and put it into the known working unit and charged it for 16 hours.

8. I removed the battery, installed it back into the malfunctioning unit and again - beep then constant tone until turned off.

So no matter what battery is in the UPS, it just cuts on and makes this constant tone unless it's being supplied AC power from a wall socket.

I would like to correct my OP, the master enable light will not turn off or on while the unit is on. The unit just shows a light and makes a constant tone.

I do have some college education in electronics fundamentals so I discharged the unit and opened it up with some heavily insulated gloves on and noticed no loose connections, visible damage, burning, swollen / plagued caps, or anything that looks out of the ordinary. The board looks about perfect, not even dust.

Unless someone knows of something I'm just missing, I'm stumped.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of