Posted: 2024-05-05 05:25 AM
I have a BR1000MS & BR1000G and I am trying to calculate power draw when recharging battery. I see the BR1000MS has a battery charge power of 8 watts but it also has a maxim input current of 12Amps. I am trying to understand if it is OK to have both of these UPS on a 20AMp circuit. Now under normal use with charged batteries they both draw under 150 & 225 watts each. Is it as simple as, if the battery charge power is 8 watts the unit will use a additional 8 watts from the wall to charge the battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-06 05:33 AM
For a 120 VAC circuit the 80% power capacity is 1920 watts.
16 Amps X 120 Volts = 1920 Watts
Based on your stated power draw there are no worries about exceeding the ampacity of the circuit breaker.
If APC states the charger consumes only 8 watts to recharge the battery. Then yes just add in the 8 watts to the connected load total. 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-06 05:33 AM
For a 120 VAC circuit the 80% power capacity is 1920 watts.
16 Amps X 120 Volts = 1920 Watts
Based on your stated power draw there are no worries about exceeding the ampacity of the circuit breaker.
If APC states the charger consumes only 8 watts to recharge the battery. Then yes just add in the 8 watts to the connected load total. 👍