Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Three UPS's Gone Bad in a Week?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Three UPS's Gone Bad in a Week?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
148
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

0 Likes
6
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

Three UPS's Gone Bad in a Week?

Last year the lights in our apartment were flickering. This had happened for a long time which we had reported it, but the management did nothing. I thought there is no way that it would be harmful to the electronics, since we had the UPS's as the middle man between the wall and the electronics. Almost a year later, the lights started flickering again (two weeks ago) and all of a sudden, this week three UP's go bad within a week.

Can someone please point me in the right direction with this one? All of these UPS's, all different models and bought and different times go bad this week. One is a white tower APC-Chute, I believe it is a 1200 or 1500 W. Now flashes red and will not turn on. The other is a black midsized tower with LCD front screen, I believe this is 1200, and the other is a 500w that has cords which come out the top of it.

I need to get a firm grasp on what I can check for, and what to do, because if I do find its dirty electricity this may go to court due to our managements negligence.


Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

Hi

when there is Problem with power all ups transfer to battery condition. when ups transfer to battery condition that meat check for battery state and give you alarm if there is any error

thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

To begin, let's get a specific model and serial number (or just the first six characters of it) from each UPS. This is on a white sticker on the back or bottom of the UPS.

When we have this, please outline the model with the symptoms next to it because that will better help us understand what unit we're working with and we'll know what it looks like and what the symptoms mean per unit.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:53 AM

I do not have the serials handy, however let me know if this is enough information below.


Model / Symptoms

Back-UPS RS APC BACK-UPS 1200VA 120V - Upon turning on tower, red light will flash, beeping will continually occur until we turn it off.

Back-UPS APC Back-UPS 550 - Short beeps, all electronics will continue to function normally.

Back-UPS APC Back-UPS 1200VA LCD 230V - Short beeps, battery on screen will continually flash; however all electronics will continue to function normally.

Message was edited by: Seth I am not sure if these are the exact models. I am basing these off the picture, but I am hoping someone will be able to let me know if these battery's can be reset, or if the power coming from my outlets may have fried the battery's.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

Well, ideally I need the exact models off the sticker where the serial number is to give you accurate answers. I only say that because we have multiple units that could be called Back UPS 1200VA and while they might be similar, some things could be different. I'll tell you what I know based on the information you were able to provide.

I don't think anything is necessarily "fried" and this could all just be a result of needing new batteries on older systems as they are lead acid and die over time, similar to a car battery.

  1. I need to know what LED this is - overload or replace battery? It sounds like it could be replace battery solid which when it is also "chirping" means the battery is disconnected. This can happen over time where the unit cannot see the battery because its voltage is below a certain limit so knowing the serial number will be good to see the age of the UPS and battery. Once I know the LEDs for sure and what they are labeled, I can give further testing instructions.
  2. No LEDs with this one? Need age here too which serial # can tell me.
  3. This sounds very similar to #1 except you have an LCD unit. This could just be the UPS not seeing the battery because the voltage is too low. Need to know the age though to see if this makes sense or its something else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

Angela, thank you for the prompt reply. Each of these units are older than 2010; however, what I am having the most difficult time understanding is them all deciding to go bad within three days of each other.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

Yes I can understand that but keep in mind, if these are battery problems and they are all at the same location and all are similar age, then it makes sense they all might need a replacement battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 PM . Last Modified: ‎2024-03-21 12:52 AM

Hi

when there is Problem with power all ups transfer to battery condition. when ups transfer to battery condition that meat check for battery state and give you alarm if there is any error

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore