Test and read home APC UPSes without computers?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Test and read home APC UPSes without computers?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
4
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

Test and read home APC UPSes without computers?

Hello.

Is there a way to test and read home APC UPSes (e.g., Back-UPS ES-750 (BE750G)) in detailed without computers' softwares (PowerChute in Windows and apcupsd)?

Thank you in advance. πŸ™‚

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-28 05:36 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:36 AM . Last Modified: β€Ž2024-03-27 12:52 AM

On 2/19/2017 4:55 AM, voidstar said:
On 2/18/2017 9:37 PM, Ant said:

Both software and UPS hardware told me to replace its battery. 😞 I guess the old battery died from the recent power outages?

I wonder why it didn't tell me this earlier. Or did it just started from the recent outages?

It's hard to tell that a battery has failed except by using it. The UPS does a weekly self-test where it briefly runs on battery -- this is most reliable when there's significant load on the UPS.

Batteries typically last 3-5 years.

Ah OK.  I guess it finally failed as of a couple nights ago from the 30 seconds real power outage. And then, I went to investigate why when I did a manual selftest in PowerChute PE for Windows. UPS is about five years old.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

It depends upon what kind of test you want to do.

These units perform a self test at every startup. With any significant load attached, this should give you a quick "go/no-go" indication. Should the unit fail a battery test, you'll know. It will beep constantly afterwards.

If all you want to test is runtime, plugging a stable, resistive load running to at least 30% of the unit's capacity into the unit and disconnecting it from AC power would do very well. Let it run from battery until it stops, and time how long it ran before the battery was exhausted. This will put considerable wear and tear on the battery, and it may push a weak battery past the point of no return.

A third approach would be to utilize some kind of microcontroller with a custom program to interrogate the unit as to its current status, and display this information on some kind of display.

As far as I'm aware, most if not all of the current Back-UPS product line no longer support simple (or "dumb") signaling over an RS-232 serial connection. Even if they did, this doesn't tell you anything beyond "power out" and "battery low, shut down now!". This means you'd have to implement enough of the USB protocol and figure out what information is being exchanged over that connection before you could tap into status information from the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

On 2/17/2017 11:25 PM, William said:

It depends upon what kind of test you want to do.

These units perform a self test at every startup. With any significant load attached, this should give you a quick "go/no-go" indication. Should the unit fail a battery test, you'll know. It will beep constantly afterwards.

If all you want to test is runtime, plugging a stable, resistive load running to at least 30% of the unit's capacity into the unit and disconnecting it from AC power would do very well. Let it run from battery until it stops, and time how long it ran before the battery was exhausted. This will put considerable wear and tear on the battery, and it may push a weak battery past the point of no return.

A third approach would be to utilize some kind of microcontroller with a custom program to interrogate the unit as to its current status, and display this information on some kind of display.

As far as I'm aware, most if not all of the current Back-UPS product line no longer support simple (or "dumb") signaling over an RS-232 serial connection. Even if they did, this doesn't tell you anything beyond "power out" and "battery low, shut down now!". This means you'd have to implement enough of the USB protocol and figure out what information is being exchanged over that connection before you could tap into status information from the UPS.

Yesterday, there was a 30 seconds power outage and my UPS lost power too. Its power light showed green status too. I remember there was a few hours power outage almost a month ago, and its battery was fine too (no shut down until it ran out of battery life).

I finally hooked up its USB data cable to a 64-bit W7 HPE SP1 machine to check with PowerChute PE. Everything looked fine. So, I ran its self test (nothing changed on the UPS physically) and it failed with its beeps and UPS's light showed a red color icon. Both software and UPS hardware told me to replace its battery. 😞 I guess the old battery died from the recent power outages?

I wonder why it didn't tell me this earlier. Or did it just started from the recent outages?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:35 AM . Last Modified: β€Ž2024-03-27 12:52 AM

On 2/18/2017 9:37 PM, Ant said:

Both software and UPS hardware told me to replace its battery. 😞 I guess the old battery died from the recent power outages?

I wonder why it didn't tell me this earlier. Or did it just started from the recent outages?

It's hard to tell that a battery has failed except by using it. The UPS does a weekly self-test where it briefly runs on battery -- this is most reliable when there's significant load on the UPS.

Batteries typically last 3-5 years.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-28 05:36 AM . Last Modified: β€Ž2024-03-27 12:52 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 05:36 AM . Last Modified: β€Ž2024-03-27 12:52 AM

On 2/19/2017 4:55 AM, voidstar said:
On 2/18/2017 9:37 PM, Ant said:

Both software and UPS hardware told me to replace its battery. 😞 I guess the old battery died from the recent power outages?

I wonder why it didn't tell me this earlier. Or did it just started from the recent outages?

It's hard to tell that a battery has failed except by using it. The UPS does a weekly self-test where it briefly runs on battery -- this is most reliable when there's significant load on the UPS.

Batteries typically last 3-5 years.

Ah OK.  I guess it finally failed as of a couple nights ago from the 30 seconds real power outage. And then, I went to investigate why when I did a manual selftest in PowerChute PE for Windows. UPS is about five years old.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore