Square wave/sine wave output

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Square wave/sine wave output
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:31 AM

0 Likes
23
7417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:31 AM

Square wave/sine wave output

My UPS: Back-UPS XS 1500 (865w)
My Computer: Fairly high end gaming system

Question#1: Is the output of this ups to my computer during normal operation a square wave or true sine wave?

Question#2: What is the effect of all the separate "power corrections" in my system components:
1. The ups itself
2. The PC&Power Cooling 850w Pwr supply in the computer
3. The 6 phase power correction circutry on the EVGA 680i mother board

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Hello,

The UPS will output whatever it is receiving from the input AC while it is in the online state. When the UPS is on battery, it will output a step-approximated sine wave. More sensitive power supplies cannot run off of the step-approximated sine wave and could potentially drop the load on a power outage. With Power Factor Corrected power supplies, we recommend using a Smart-UPS.

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 23
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

My UPS: Back-UPS XS 1500 (865w)
My Computer: Fairly high end gaming system

Question#1: Is the output of this ups to my computer during normal operation a square wave or true sine wave?

Question#2: What is the effect of all the separate "power corrections" in my system components:
1. The ups itself
2. The PC&Power Cooling 850w Pwr supply in the computer
3. The 6 phase power correction circutry on the EVGA 680i mother board

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Hello,

The UPS will output whatever it is receiving from the input AC while it is in the online state. When the UPS is on battery, it will output a step-approximated sine wave. More sensitive power supplies cannot run off of the step-approximated sine wave and could potentially drop the load on a power outage. With Power Factor Corrected power supplies, we recommend using a Smart-UPS.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Ok, so far so good.
I should have stated that my psu is a PC Power&Cooling 850w unit. I believe the power factor is .98 or .99;
Am I using the wrong ups ? You said I should be using a Smart-UPS.I already paid a lot for the unit I have now!
What to do?

Javalin

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:24 PM . Last Modified: β€Ž2024-03-26 02:30 AM

The BX1500 runs with a power factor of about .6. Also, you're power supply is 850 Watts, where the UPS can handle about 900 Watts total. You are risking overloading the UPS with your Power Factor Corrected power supply. Have you tried the load on this UPS yet? Power Supplies rarely run at full capacity, and there could be a chance that the UPS will support the load. You may want to put the load on the UPS and just pull the AC power cord to simulate a power outage. If the UPS cannot handle the load, it is because of the step wave and the power factor correction.

You could trade the BX1500 in and receive a discount on a Smart-UPS model through our Trade-UPS program. The link for the program can be found through the following link:

http://www.apc.com/buy/index.cfm

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Most UPS, including your UPS, simply passes on whatever comes into the power line. There are "on line" double-conversion UPSs that constantly passes power through the inverter without any switchover delay and provides a clean output within 3% or so such as the Liebert brand. These are rare and unnecessary under normal conditions.

Sometimes active PFC equipped power supplies interect poorly with quasi-square wave input and cause the UPS to trip out or crash/reboot or shut off your computer. As Sgt Slaughter suggested, you can test this out by pulling the plug. Your power supply can pull around 1,000w input at FULL LOAD, but I'd be surprised if it's pulling much more than 400-500W from the plug even under heavy use and quickly drop to 150-300W once you stop CPU/graphics intensive activity.

If they don't get along, you can change the PSU to a non PFC type or get a SmartUPS, but I wouldn't use APC's TradeUPS program, because in the end it's horribly expensive. A used 1000VA/670W with new batteries is around $120 + S&H and it's just as good as new. You can get a used one from UPSforless.com, or find a dead SmartUPS 1000 to 1500 locally and get a new battery pack from gruberpower.com (or whoever you chose, but BatteriesPlus is a big rip off when it comes to batteries).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Thanks for the reply...
Ok, I pulled the plug on the APC ups and went on battery back-up.
I closed my running programs..Eudora for E-mail and the web browser.
Everything seemed to be ok and then I shut down the computer and replugged
the ups back in and booted up fine so it looks like everything works as it should. I didn't have much of a
load on the computer and didn't run it long on battery.

So I guess I'm good to go and do not need a "Smart-UPS"..yeah.

BTW...My APC 1500 ups is a SX model but I can't find that on the APC web site. Stg. Slaughter refers
it as a BX model ??????

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Yeah, well at that rate, again, I wouldnt be able to tell you if the unit would actually damage anything. However it sounds like you should really be going for a true sine wave output unit. Also make sure the PSU itself is dust clear and the fans are working properly.

If the PSU is working harder to keep up with a step aprox, and theres allot of dust and sediment on there it could be allowing voltage to cross paths on its boards. A friend of mine had this issue and it eventually fried his PSU because he just never cleaned it, and it got clogged up, passed voltage and super heated the ICs on the board (dust is a huge heat trap).

Just some things to keep in mind.

-Syn

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

couldnt help but notice the discussion going on about stepped wave issues with active PFC power supplies... I have a Antec true power trio 650 watt power supply with Active PFC and 3-12 volt rails and using a APC BackUPS XS 500 from what I understand the XS 500 has stepped wave output and was wondering if this would cause any damage to my PC or the components... when running on battery I notice a buzz emitted from my antec power supply, the system appears to run normally and doesnt trip out and shut down. I hope this buzzing sound isnt a warning that my PC will become toast if I leave it setup like this. I looked into the smartups units but thats wayyyyyyy out of my price range. is it absolutely critical to have a true sine wave UPS on a Active PFC power supply?... and also I have some network equipment running on the BX 1500 would that potentially damage my network equipment to? please respond ASAP

thanks
-Phil

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Im not going to be able to say if it will damage your PSU or not, but I know personally my last PSU was an antec truepower 650w and after time it emitted a buzzing noise and ended up blowing my mb.

How loud is the buzzing? Do you use any monitoring software to see your rail volts at runtime? Are there any power fluctuations or odd happenings?

-Syn

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Havent found any good software that will give me a proper reading of the voltages... but the buzz is louder then the fans. was ur antec PSU making that noise constantly or only when running off battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

at first intermittently, then after time all the time until it was to late πŸ˜•

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

well my PSU only does it when running off of the UPS, other then that I dont hear it any other time

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

The loud buzzing comes from the PSUs front end components. I don't agree with the wording "modified sinewave" because Back-UPSs' output is closer to modified square wave. Although uncommon there is simulated sinewave, which breaks down the climb into several steps.

http://img338.imageshack.us/img338/3759/waveformln6.gif
This is what the output of Back-UPS and majority of "modified sinewave" UPSs look like. In IT loads,this goes through an inductive filter (to keep RFI from power supply from getting into the power line) and turned into ~340v DC. The PSU then converts 340V DC into respective rails through a high frequency converter and an isolation transformer (so you won't have the slightest chance of seeing 340v at the output even in the event of a failure!)

The faster rise and fall jump rather than sloping up/down is causing the inductive filter to make an audible buzz.

Some CRTs and speakers pickup noise and you might see lines or hear the buzzing from the speaker, but that's nothing intolerable for the duration you need the computer to be on UPS. Speakers don't even need to be connected to UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Hi DELLsFan,
A Smart-UPS UPS would not accept the square wave power either. It would see it as a problem with incoming AC, and attmept to run on battery to protect your equipment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

Well, that's disheartening. I would pay for a UPS solution that could interpret non-standard incoming power (like square wave, lower frequency, varying voltage) and correct/condition it for sensitive equipment like computers. Surely SOMETHING exists as an alternative to replacing my (relatively) expensive inverters!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

DELLsFan wrote:
Hello!

We own several inverters that we integrated with our solar system at our facilities in Haiti. These inverters produce a square sine wave and not a regular smooth sine wave. Standard UPS systems do not accept square sine wave power. Unfortunately, these inverters were less expensive than the ones that produce the standard smooth waves. As one might expect, we receive fluctuating power from one of three sources at our main facility: City power, Generator power, or solar (usually in the evening). Would a quality SmartUPS from APC protect my sensitive computer equipment at our facilities?

Thanks in advance.
It might work if you get a double-conversion UPS like a Smart-UPS RT, but I don't know how well the front-end can compensate without relying on battery, but it will cost you more than buying a sinewave inverter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:30 AM

I'm having a difficult time understanding why APC products (which do a fantastic job of doing everything ELSE with incoming power) couldn't accomodate a non-standard sine wave. We can go to the moon and back and deploy an international space station in orbit for years, but can't figure out a way to condition incoming AC power?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

DELLsFan wrote:
I'm having a difficult time understanding why APC products (which do a fantastic job of doing everything ELSE with incoming power) couldn't accomodate a non-standard sine wave. We can go to the moon and back and deploy an international space station in orbit for years, but can't figure out a way to condition incoming AC power?
Standard UPS products are not designed for such. It's possible to design such a thing, but it would not be economically feasible. This is like asking why each and every parking space at Wal-Mart aren't designed to accomodate Hummer H1s.

APC as well as other common UPSs are designed to provide backup protection to IT loads, nominally operating off of the standard grid power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

Thanks for the response. My situation is obviously non-standard. Nothing ventured, nothing gained - so my time here has not been wasted. I am disappointed there isn't a high enough demand for the solution I would require from APC. However, I shouldn't be terribly surprised. After all, we ARE talking about American Power Conversion company - not Haitian Power Conversion.

As for Wal-Mart and the parking lot analogy, just wait a few more years. It's only a matter of time before the US becomes totally dependent on imports & starts buying luxury cars like a Hummer from China. Everything ELSE at Wal-Mart seems to originate from there. When that happens, I'll let you know if your analogy holds. πŸ˜‰

Cheers!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

I have come across this non-pure-wave stuff as well. I plan on making an adapter to convert square or modified into pure sine, or at least try to.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:25 PM . Last Modified: β€Ž2024-03-26 02:29 AM

You're much better off to convert from DC to a pure sinewave....wait....thats what you would have been doing if you invested the money up front for the right equipment

Buy cheap - Buy twice!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:26 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:26 PM . Last Modified: β€Ž2024-03-26 02:29 AM

Earlier you stated that when the APC unit is not running on battery it passes whatever it's source is to the plugged in devices. What does it output when there are spikes or dipps in the input voltage? I ask as we use our APC comming off of a portable generator as a way to clean the power for electronic devices. Also, durring a outage we have used the generator through the APC to power our sump pump and refrigerator/freezers. I have heard that the stepped sinewave is distructive to any motor. Is this the case?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:26 PM . Last Modified: β€Ž2024-03-26 02:29 AM

0 Likes
0
7414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:26 PM . Last Modified: β€Ž2024-03-26 02:29 AM

Do you see a small white sticker on the back or bottom of the UPS? This sticker will have the exact model and serial number. Our Back-UPS XS series will have a model number that begins with "BX"

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore