Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smoke & Flames from BR-1200

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smoke & Flames from BR-1200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
3
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

Smoke & Flames from BR-1200

This is the second APC UPS I've had that went up in smoke and flames. The first was an RS-1000, which APC replaced with my current BR-1200. The power was off, but the unit was still plugged in. I heard a slight ringing tone, and then flame and sparks shot out of the unit. Another short ringing tone, and more flame and sparks, actually launching a burning ember out of the unit. By that time I had gotten under the desk and unplugged it. The room still smells of burning plastic and ozone. I suppose I should be happy that the unit protected my system by sacrificing itself, but it worries me that it could have started a fire if I hadn't been present. I often leave the system on when I'm gone, and even when I shutdown, I usually leave the UPS connected to the wall receptacle. Has anyone else had this happen? Is it a flaw in the unit, or something that's supposed to occur?

We were having a storm, with brownouts (which is why the unit was off), but it seems to me that a surge that would cause such a meltdown would have affected other electronic items in my house, but nothing else was damaged.

Thanks for any information

-aj

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
0
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

This is the second APC UPS I've had that went up in smoke and flames. The first was an RS-1000, which APC replaced with my current BR-1200. The power was off, but the unit was still plugged in. I heard a slight ringing tone, and then flame and sparks shot out of the unit. Another short ringing tone, and more flame and sparks, actually launching a burning ember out of the unit. By that time I had gotten under the desk and unplugged it. The room still smells of burning plastic and ozone. I suppose I should be happy that the unit protected my system by sacrificing itself, but it worries me that it could have started a fire if I hadn't been present. I often leave the system on when I'm gone, and even when I shutdown, I usually leave the UPS connected to the wall receptacle. Has anyone else had this happen? Is it a flaw in the unit, or something that's supposed to occur?

We were having a storm, with brownouts (which is why the unit was off), but it seems to me that a surge that would cause such a meltdown would have affected other electronic items in my house, but nothing else was damaged.

Thanks for any information

-aj

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
0
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

I did contact Tech Support, and they are sending a replacement unit. I'm just nervous about using the new unit if it's going to go up in flames again. I posted here hoping to find out if this is a common occurrence or not.

Thanks,
aj

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
0
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

AJ,

As I had previously stated, after speaking with Product Leaders, it is extremely uncommon for one, nevermind two units to act like this. Chances are, it's something to do with the electrical that's passed to the UPS that's causing this. Two instances like this in one residence spread out over different sized UPS's are almost unheard of.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
0
855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

This is the second APC UPS I've had that went up in smoke and flames. The first was an RS-1000, which APC replaced with my current BR-1200. The power was off, but the unit was still plugged in. I heard a slight ringing tone, and then flame and sparks shot out of the unit. Another short ringing tone, and more flame and sparks, actually launching a burning ember out of the unit. By that time I had gotten under the desk and unplugged it. The room still smells of burning plastic and ozone. I suppose I should be happy that the unit protected my system by sacrificing itself, but it worries me that it could have started a fire if I hadn't been present. I often leave the system on when I'm gone, and even when I shutdown, I usually leave the UPS connected to the wall receptacle. Has anyone else had this happen? Is it a flaw in the unit, or something that's supposed to occur?

We were having a storm, with brownouts (which is why the unit was off), but it seems to me that a surge that would cause such a meltdown would have affected other electronic items in my house, but nothing else was damaged.

Thanks for any information

-aj

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore