Smart-UPS 2200 keeps restarting

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS 2200 keeps restarting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-03-30 12:05 PM

0 Likes
11
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-30 12:05 PM

Smart-UPS 2200 keeps restarting

Smart-UPS 2200 keeps restarting

 

I have a Smart-UPS 2200 which has served me well for several years.  Lately the unit will restart itself and then run with no issues.  It's like a blink, where it turns off for a second then restarts and runs fine.  However, I leave my computer on 24/7 so this becomes an issue since the computer doesn't restart.  Nothing else is wrong, battery test shows the batteries are good, self test shows no issue.

 

How do I correct this?

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-02 09:21 AM

0 Likes
10
1893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 09:21 AM

If you remove AC Mains from the wall what happens? How long does the unit provide backup power? What does the error logs show as the last transfer state?

 

NOTE: If you remove AC mains from the unit and the system shuts down immediately the batteries are toast. If however the system continues to run for the expected runtime you have removed the batteries as the primary fault. 

Keeping in mind if the expected runtime is 30 minutes but you only see 5 minutes the battery is toast! 

The battery’s are rated for 3-5 years of service life. Which is based on usage, temperature, and environmental conditions. My expectation is if you remove power the unit will turn off immediately or within a few seconds. 

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-02 08:20 PM

In response to Teken
0 Likes
0
1871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 08:20 PM

I just checked and with the unit unplugged for several hours, run time is still 5 hours and 50 minutes at 94% charged. So it's not the batteries (I wish it was, that's an easy fix). But every day, at different times, the unit cycles and all the AC outlets go down. This happens if I'm working on the computer or away. Load does not seem to matter. Thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-02 08:28 PM

In response to Teken
0 Likes
8
1871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 08:28 PM

Not sure if my reply posted so here it is again.

 

Thanks for the reply. With the unit unplugged for several hours, it shows a run time of 5 hours and 50 minutes. So it's not the batteries (I wish it was, that's an easy fix). Menu shows: Last UPS Self Test, passed; Battery Replace, Jul-2024; UPS Firmware 1, 08.8. Thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-03 09:53 AM

In response to CIDAdvisors
0 Likes
7
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-03 09:53 AM

A couple of things you can do to help narrow down the issue. As to a UPS hardware issue, connected load, electrical wiring fault.

 

Brain Dead: This procedure will reset the main system to a default state. Power down and remove all connected loads. Remove AC Mains from the wall. Disconnect all batteries from the system. Press and hold the power button until you hear a click / beep. 

You may not hear anything when this procedure is done. 

Reconnect everything (except) the battery packs & loads. 

Report back what happens as the best case the problem is cleared by the brain dead procedure. If the system randomly restarts the unit has an internal fault.

 

Keeping in mind if your area has very poor grid power the system will obviously shut down when there’s a power blip! ☝️

 

The reason you’re doing this test (initially) without the battery cartridge is to isolate if the charging system / inverter circuit is a problem.

 

If you don’t observe the problem for 7 days. You can move forward by connecting the battery cartridge. If you see another reset after the cartridge is inserted (rinse & repeat) the removal of the battery cartridge to narrow down if it was a fluke vs it’s the battery charging / inverter circuit.

 

If everything is fine you can move forward by connecting the load and monitor what happens. 

 

If you have a NMC installed a lot more information could be gathered. If you don’t have a NMC installed please insure you have APC Power Chute software installed and connected to a computer system.

 

Doing so would help capture error codes, active faults, and line conditions. We are interested in knowing if there are power quality issues vs hardware issues or both.

 

Given you did a great job in replicating a lights out event with removing AC Mains. On the surface it appears the inverter circuit is working fine as it allowed the battery to supply AC power when needed.

 

NOTE: It’s important to check all line sets attached to the unit. This includes the main power cable to the UPS. Along with any cords inserted into the output outlets.

 

When everything is powered up and running wiggle each cord set. Nothing should happen when this is done. Please do post up what the NMC / Power Chute indicates the incoming line voltage is vs output voltage from the UPS. 

If there are any error messages like relay weld, ground fault, over temperature, etc in the hard logs please do call them out with dates & times.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-06 02:54 PM

In response to Teken
0 Likes
6
1813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-06 02:54 PM

Ok, I pulled everything off the back of the unit. I'm not entirely clear what "Remove AC Mains from the wall" means but I left the UPS plugged in and removed the batteries. Then I pushed the power button and it immediately beeped, then when I released the button the screen displayed if I wanted to turn off the unit, I chose No.

 

I'll monitor to see if there is an interruption with the power. My area has a strong grid so that should not be an issue. I'll report back in 7 days (on or about April 13).

 

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-08 08:17 AM

In response to CIDAdvisors
0 Likes
5
1811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-08 08:17 AM

AC Mains = Unplug the (UPS) power cord from the AC wall outlet. 

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-10 08:09 PM

In response to Teken
0 Likes
4
1782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-10 08:09 PM

Ok, I pulled everything off the back of the unit, removed the batteries, unplugged the unit from the wall, then pushed the power button and it immediately beeped.  Ran it now for three days and it keeps shutting down briefly.  This does not sound good.  Any advice?  Hoping I don't need to buy a new unit but I've had it 9 years (although I only had a 6 year warranty).

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-11 05:41 AM

In response to CIDAdvisors
0 Likes
3
1773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-11 05:41 AM

If you followed my suggestion about running the unit without the battery cartridge. If there was a power grid issue I would expect the unit to turn off and possibly restart again.

 

Because there isn’t a battery inside. 🙂

 

If on the other hand the battery cartridge was inserted and plugged in and the system also shut down.

 

Theres a problem . . . 

 

Please connect the system to a computer running the APC Power Chute software. Doing so will offer you and I more factual data as to active faults, error codes, and the line conditions in your area.

 

You should be able to view past errors from the LCD - Logs. But we want to be able to track all of the above easier.

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-11 09:05 PM

In response to Teken
0 Likes
1
1761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-11 09:05 PM

It will take a minute to do this.  I need to see how to connect these units, and see if I even have a 9-pin connector on my computer (I presume this is what I'll need).  I do have the disk.  I'll work on this, this weekend.  Once connected, do I need to wait for a fault to see the error, or will a problem be immediately evident? Keeping in mind that when the UPS faults, the computer shuts down and does not restart (until I press the start button).

Reply

Link copied. Please paste this link to share this article on your social media post.

CIDAdvisors
Crewman CIDAdvisors
Crewman

Posted: ‎2024-04-11 09:06 PM

In response to Teken
0 Likes
0
1761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-11 09:06 PM

Oh, and thank you for all this help!  I greatly appreciate it!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-12 04:02 AM

In response to CIDAdvisors
0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-12 04:02 AM

You’ll be connecting to the unit with the USB cable to UPS / Computer. For now the computer will be plugged (powered) directly to the wall outlet.

 

We don’t want the computer to turn off during this monitoring process. It goes without saying if the computer happens to turn off at some point and it’s NOT connected to the UPS.

 

You have other issues to resolve such as bad power / failing PSU inside of the computer system / both. 🤦‍♂️🤣

 

You may also download the Power Chute Business Edition from APC if you can’t find your copy. 👍

 

Lastly, in case I did not ask / mention this if you have the (EPO) Emergency Power Off in use and connected. Please insure this isn’t also the root cause!

 

The EPO is on the back and uses a small green / blue / black phoenix connector. That connector is wired to a N.O (Normally Open) / N.C (Normally Closed) switch and placed on the wall. 

Should there be an emergency and the power needs to be immediately turned off. Pressing that button will immediately shut down the unit! ☝️

 

If this EPO is not in place - no worries. If it is test it to see if works and all wiring is sound then disconnect it to rule out it’s not the EPO. 

Let me know what you see and observe in the next few days. Once the software is installed and monitoring the UPS.

 

Assuming you don’t experience a black out during this period (super bad luck) I would say! 🤣

 

The software will affirm the incoming line voltage / output voltage. Along with any active faults / error codes, etc.

 

As a reminder you need to test the system initially for 72 hours with no battery cartridge attached. If the unit operates fine without the battery let it continue this way until it turns off / faults. At this point you can share the logs and other metrics such as incoming voltage, frequency, etc.

 

Once the system has faulted out without the battery. Connect the battery and monitor again ignoring the obvious errors of the battery missing / installed.

 

Let the unit operate until it turns off / faults. The software will capture everything leading to the shut down.

 

Relay the error logs / metrics here for all of us to review.

 

NOTE: This is also a good time to validate the outputs have not randomly been programmed (scheduled) to turn off. Given the shut down is random this is pretty unlikely. Regardless you should default the UPS to a factory state a few times just to see if the unit behaves differently. 

Cheers! 👍🤟🍺🍺🍺

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore