Site wiring fault light - what if it turns on and off?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Site wiring fault light - what if it turns on and off?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
3
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

Site wiring fault light - what if it turns on and off?

Hello, I have an APC ES (can further specify model if needed) on an old building with a monitor, desktop, and 2 small lamps hooked into it. This setup has been installed in the same outlet for about 6 months, and during the summer months when first installed, the site wiring fault light never came on. With colder weather, however, I have noticed on three occasions the following:

- The wire fault light was off, and the computer was running.
- Upon shut-down, I waited over 10 minutes to turn the computer back on, and have noticed that the fault light has come on.
- The second time this happened, the light has gone off by itself after 5-10 minutes of the computer being on.
- I have noticed that the light changes intensity, from a dim red to a bright red, as equipment has been turned on and off.

A few questions follow. If possible, answering all would be great:

- I dismiss a potential reverse polarity because, if so, the light would be on all the time. On another building, I actually experienced an outlet with reverse polarity, and the APC unit (an earlier model) had the site fault light on continuously.
- I suspect that cold weather might be at play. Each time this has happened, the room temperature was in the middle-upper 50s, if not slightly lower. For instance, last Saturday, the light was on during most of the day, and towards the evening, I decided to turn on the heating system. The next day, the light was gone.
- Could the above be a reason for the wiring fault light to come on? If so, what would be the possible reason why?
- My equipment has been exposed to these conditions for, probably, 48-60 hours. Considering the APC unit has been supplying power to my computer, so it has never been directly exposed to the outlet, should I be concerned about damage (generally speaking, of course, and with no certainties)?

I appreciate any details anyone can offer about the above. Today the light has been off consistently, but I hope my APC unit will take the brunt of any outlet problems before my equipment does - is this a fair statement?

Thanks,E

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • fault
  • light
  • red
  • site
  • wiring
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

An overloaded neutral can cause this.

I've experienced one case where the site wiring fault LED have been turning on very dimmly on a APC surge protector and I could only tell it was lit when the room was dark. I later found out that when the electrical shower (very common in my country) was on it caused a slight overload on the main neutral wire that goes to the circuit breaker panel and the voltage difference between neutral and ground could reach 2 volts even though they're bonded together at the electrical panel at the entrance of the house. Then I found out that if there is very small voltage differences between neutral and ground the site wiring fault LED will turn on, very dimmly though.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

An overloaded neutral can cause this.

I've experienced one case where the site wiring fault LED have been turning on very dimmly on a APC surge protector and I could only tell it was lit when the room was dark. I later found out that when the electrical shower (very common in my country) was on it caused a slight overload on the main neutral wire that goes to the circuit breaker panel and the voltage difference between neutral and ground could reach 2 volts even though they're bonded together at the electrical panel at the entrance of the house. Then I found out that if there is very small voltage differences between neutral and ground the site wiring fault LED will turn on, very dimmly though.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

The light is most commonly caused by a bad ground. I would suspect that the colder weather might be affecting the ground connection in the outlet

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-22 02:29 AM

Hello, I have an APC ES (can further specify model if needed) on an old building with a monitor, desktop, and 2 small lamps hooked into it. This setup has been installed in the same outlet for about 6 months, and during the summer months when first installed, the site wiring fault light never came on. With colder weather, however, I have noticed on three occasions the following:

- The wire fault light was off, and the computer was running.
- Upon shut-down, I waited over 10 minutes to turn the computer back on, and have noticed that the fault light has come on.
- The second time this happened, the light has gone off by itself after 5-10 minutes of the computer being on.
- I have noticed that the light changes intensity, from a dim red to a bright red, as equipment has been turned on and off.

A few questions follow. If possible, answering all would be great:

- I dismiss a potential reverse polarity because, if so, the light would be on all the time. On another building, I actually experienced an outlet with reverse polarity, and the APC unit (an earlier model) had the site fault light on continuously.
- I suspect that cold weather might be at play. Each time this has happened, the room temperature was in the middle-upper 50s, if not slightly lower. For instance, last Saturday, the light was on during most of the day, and towards the evening, I decided to turn on the heating system. The next day, the light was gone.
- Could the above be a reason for the wiring fault light to come on? If so, what would be the possible reason why?
- My equipment has been exposed to these conditions for, probably, 48-60 hours. Considering the APC unit has been supplying power to my computer, so it has never been directly exposed to the outlet, should I be concerned about damage (generally speaking, of course, and with no certainties)?

I appreciate any details anyone can offer about the above. Today the light has been off consistently, but I hope my APC unit will take the brunt of any outlet problems before my equipment does - is this a fair statement?

Thanks,E

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of