Back-UPS RS 800Va does not start up after power is restored

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS RS 800Va does not start up after power is restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:29 AM

0 Likes
5
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:29 AM

Back-UPS RS 800Va does not start up after power is restored

Hi,
I have an Back-UPS RS 800VA (BR800BLK).

The problem is that the weekends, the UPS shutdowns and then never power up automatically,
even when 2 other UPS does not shutdown.

Could it be some electrical problem that affects and shutdown the UPS?
Why does the UPS does not power up automatically after clearly 2 days of receiving power?


I changed the senitivity settings from high to medium to see what happends. Also, the UPS load
is 30%.

Many thanks
Oliver

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

The only symptom of removing the comm. cable when PowerChute is installed should be a "Loss of Communication" error in PowerChute itself. If the UPS is exhibiting a red LED or abnormal indicator of any kind just because you unplug the communication cable that goes to the laptop/PC, that is strange. So when you say that the UPS does not shut down, it does not shut down according to the shutdown parameters you specify in PowerChute, i.e. for x amount of time on battery?

Please confirm that you are using PowerChute Personal Edition in conjunction with the RJ45-USB cable that came included with the UPS, with no USB/serial adapters or cable extenders in place. If your configuration is normal and fits those guidelines you should call technical support (1-800-800-4272) for a final set of quick troubleshooting steps and ask about your RMA options for return.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

Hi,
now I have some more info.

The UPS is new, buyed in december-2009.

Only 2 routers and a switch are pluged in the Battery UPS. I installed Powerchute on a notebook,
conected the UPS and configured the settings, then unplugged the data cable.
No computer is connected to the data port of the UPS.

The symptom is that the UPS emits a continuous beep, a red light in on the UPS and the power
is ok. The only solution is to turn off the UPS and turn it on. Removing the power cable of the UPS
and plugin it in the power outlet does not make any difference.

The UPS is connected to a Rack, in that Rack 2 other UPS are connected. None of the UPS have
a failure.

The UPS load is about 15 o 20%

Its a defective UPS?

Thanks
Oliver

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

Hi,
I could solve this issue by connecting the data cable to the UPS. It seems that once you setup PowerChute you can not remove
the cable or software.

Now I have the problem that the UPS does not shutdown. Since it does not shutdown, it not power on and the server does not power up neither.

Is there a way to setup PowerChute Personal to shutdown the UPS after the Server was shutdown?

Thanks
Oliver

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

Hi,
I have an Back-UPS RS 800VA (BR800BLK).

The problem is that the weekends, the UPS shutdowns and then never power up automatically,
even when 2 other UPS does not shutdown.

Could it be some electrical problem that affects and shutdown the UPS?
Why does the UPS does not power up automatically after clearly 2 days of receiving power?


I changed the senitivity settings from high to medium to see what happends. Also, the UPS load
is 30%.

Many thanks
Oliver

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

The only symptom of removing the comm. cable when PowerChute is installed should be a "Loss of Communication" error in PowerChute itself. If the UPS is exhibiting a red LED or abnormal indicator of any kind just because you unplug the communication cable that goes to the laptop/PC, that is strange. So when you say that the UPS does not shut down, it does not shut down according to the shutdown parameters you specify in PowerChute, i.e. for x amount of time on battery?

Please confirm that you are using PowerChute Personal Edition in conjunction with the RJ45-USB cable that came included with the UPS, with no USB/serial adapters or cable extenders in place. If your configuration is normal and fits those guidelines you should call technical support (1-800-800-4272) for a final set of quick troubleshooting steps and ask about your RMA options for return.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-22 02:28 AM

I'm using the PowerChute personal edition and the USB cable that came with the UPS.

I taked the UPS for a technical check, using the warranty. The UPS seems to be working fine, no problem
detected at the local APC distributor.

So, I may have a bad electrical issue. I will check that with an electrician.

The electrical grid is sending me something every morning that make the UPS o crazy. Will post in a few days.

Many thanks for your help
Oliver

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore