New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
SRT10KXLT LCD Screen Issues
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-2404:09 AM
I’m not sure what you’re stating or asking?!? If your question is about changing the colour of the LCD you have limited options in the menu to do so.
If the question is (Why) the LCD is displaying yellow / red colour. That’s because there are active faults / errors present and they need to be acknowledged or corrected.
Those problems can be end of life battery needing to be replaced. The unit is running on battery due to power outage / high or low voltage input. If there are temperature / humidity sensors it could indicate out of range limits. If there was a EPO activation upon power up the system will declare that event. There dozens of reasons as to why the LCD would be yellow / red.
Yellow normally indicates a warning. Red indicates a high severity condition that requires immediate attention.
Please restate your question or affirm which of the two statements I made (up above) reflects your problem.