SRT battery replacement will not update
Showing results forΒ
Did you mean:Β
  • SRT battery replacement will not update
2150
127
MorneMeintjes
Ensign MorneMeintjes
Ensign
Posted: β€Ž2024-05-07 06:10 AM
3205
Hi all.
My client has replaced batteries, but the battery replacement date for the internal and external batteries will not update.
The units are SRT3000XLI manufactured 2015/2019.
Both has the same issue.
configuration->Battery->internal date-> change date (All RBC)
I there any specific procedure other than the above. Does the unit require a firmware upgrade
Please see media attached
  • Home & Office - UPS & Software
Kirk
Posted: β€Ž2024-05-13 04:41 AM
In response to MorneMeintjes
Configuration -> UPS -> Last Battery Replacement: Enter Month / Year and Apply.
Reboot the UPS, Initiate a manual Self Test than complete a Battery Calibration as outlined above.
Please let me know if you have more questions. If not and this information resolved the issues ensure you mark this as solved. πŸ‘
Kirk
Posted: β€Ž2024-05-07 07:17 AM . Last Modified: β€Ž2024-05-07 07:18 AM
2
3191
Starting with the main UPS disconnect the battery cartridge and wait for the unit to declare a fault. Wait another 30 seconds and reconnect the cartridge.
The system should prompt you to confirm this is a (New) battery cartridge select YES and enter the month and year than OK / Save.
Confirm the new month and date is present on the (Main) UPS! ☝️
If it is you can do the same for the extended battery packs. You must wait for the system to declare a fault (missing battery) than wait 30-60 seconds before reconnecting the battery terminals.
This is a lot easier via the NMC if present. πŸ‘
Once the battery dates have been updated reboot the UPS. Next, complete a Self Test of the system. Lastly initiate a battery calibration to insure the system knows the correct operational runtime.
MorneMeintjes
Ensign
Posted: β€Ž2024-05-12 11:50 PM
In response to Teken
3120
Appreciate your assistance, how do you update using the NMC, AP9630 installed at the moment.
Kirk
Β