Running a printer on a UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Running a printer on a UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
3
6243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

Running a printer on a UPS

I have a customer who wants to run a desktop PC, monitor and "small printer" on a UPS for 30 minutes.


I confirmed that the printer is a necessity, and needs to be able to run during an outage (rules-out running it through a surge-only outlet).  Is there a Back-UPS and/or Smart-UPS capable of this?  In the past, I've always recommended the printer NOT be used, and it's usually not an issue.

Thanks!

Tyler

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
0
6243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

Is it a laser printer? We'd need to know the power consumption of the devices too. My thought is if you HAD to use a laser printer, you need to size the UPS accordingly to handle in-rush from the printer warm up.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
0
6243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

Hi Tyler,

No problem. Here is some info one of our UPS support folks after I asked for some feedback to make sure I didn't miss anything:

The issue is only with laser printers. Ink Jets are no problem as long as the load is sized for their draw while printing (which is usually 15-30 watts like the you said.) With laser printers, the issue is the fuser assembly. It is essentially a heating element that fuses the powdered toner to the paper. The sine wave isn't actually a problem but it's initial inrush which can be huge. You can usually get away with a Smart-UPS 1500 VA for smaller desktop lasers, although anything more commercial sized might be better off with a 2200. I would probably direct the user to an SMX unit just because it has a higher watt rating than the SMC/SMT. Most customers just save the print job in their queue and reprint when power returns.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
0
6244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

Is it a laser printer? We'd need to know the power consumption of the devices too. My thought is if you HAD to use a laser printer, you need to size the UPS accordingly to handle in-rush from the printer warm up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
0
6243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

I knew you'd be able to help, Angela! πŸ™‚

I'm waiting to hear back from the customer on the model of the printer. If it's not a laser printer, are there any other necessary requirements I should look out for? Is stepped approximation safe or is a pure sine wave required?  According to some Google perusing, it looks like a lot of basic ink jet printers only pull 15-30 watts while printing.  Obviously, laser printers have huge in-rush currents to worry about, but that doesn't seem to be the case with ink jets. I've heard that printers in general should not be used with UPS units. Any truth to that, or are laser printers just giving printers in general a bad reputation?? πŸ™‚

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

0 Likes
0
6244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:25 PM . Last Modified: β€Ž2024-03-20 12:37 AM

Hi Tyler,

No problem. Here is some info one of our UPS support folks after I asked for some feedback to make sure I didn't miss anything:

The issue is only with laser printers. Ink Jets are no problem as long as the load is sized for their draw while printing (which is usually 15-30 watts like the you said.) With laser printers, the issue is the fuser assembly. It is essentially a heating element that fuses the powdered toner to the paper. The sine wave isn't actually a problem but it's initial inrush which can be huge. You can usually get away with a Smart-UPS 1500 VA for smaller desktop lasers, although anything more commercial sized might be better off with a 2200. I would probably direct the user to an SMX unit just because it has a higher watt rating than the SMC/SMT. Most customers just save the print job in their queue and reprint when power returns.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore