A few questions:
After a new ups is installed should a run time calibration be ran to get the most accurate reading?
A run time calibration should be ran after new batteries are installed...correct?
Should a run time calibration be ran yearly?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:08 PM . Last Modified: 2024-03-21 03:13 AM
1.) Yes, once all your load is attached this is a good idea.
2.) Yes, you can do it at this time as well
3.) Yes and maybe if you change your load around a lot. I would not do it more than 1-2 times a year or after you change the batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:08 PM . Last Modified: 2024-03-21 03:13 AM
1.) Yes, once all your load is attached this is a good idea.
2.) Yes, you can do it at this time as well
3.) Yes and maybe if you change your load around a lot. I would not do it more than 1-2 times a year or after you change the batteries.