Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Replacement Batteries for BX 1300LCD Battery Backup

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Replacement Batteries for BX 1300LCD Battery Backup
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Iggy64_apc
Iggy64_apc
Cadet

Posted: ‎2021-06-28 09:43 PM

0 Likes
3
214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:43 PM

Replacement Batteries for BX 1300LCD Battery Backup

This was originally posted on APC forums on 7/22/2008


Forgive me if I have posted into the wrong topic. I am a total newbie to this forum and to UPS. I tried to get a feel for what goes where, but I'm still not sure.

Wanting some protection for my home computers, I shopped UPS solutions and settled on the APC BX 1300 LCD because I have heard only good things about APC and this model seemed to offer good value for the price. It offers the various features I was told to look for, including user-replaceable batteries. On the packaging (back of the box) it says "User-Replaceable & Hot Swappable Batteries. Can be replaced with minimal effort without powering down your equipment......"

Curious about the cost of replacements, I looked up this model on the APC replacement parts site, and found no listing. I emailed the service group, and the reply says that the BX (or is it XS?) LCD models do no have replaceable batteries. I'm not really sure what that means. Does it mean that when the batteries go bad, I have to chuck the unit and get a whole new UPS unit? Seems like quite a waste. (Also seems like bogus advertising on the box.) If this is true, is there some other model that makes more sense for someone like me - - who doesn't like to throw away an appliance because its batteries went dead?

I haven't broken the box open yet, so I can return the unit and switch to a different model. But I find the whole XS, RS, BX, .. whatever scheme a bit confusing (yup, I said I was I newbie), and it just gets worse from there for me.

Thanks for any clarification and advice.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:43 PM

0 Likes
0
213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:43 PM

This was originally posted on APC forums on 7/23/2008


I don't set the prices so I don't know what the price is going to be when it's released.

BUT other than that, your assumptions are correct. I wouldn't expect to see a sku'd battery for the first three years.

See Answer In Context

Reply
Share
Replies 3
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:43 PM

0 Likes
0
213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:43 PM

This was originally posted on APC forums on 7/22/2008


The battery should be stated in the manual as something like an APCRBC105.

They haven't been released yet to manufacturing because the UPS is still within its first 3 years of use, and any problems that result in a failed battery, should be reviewed as the unit overall. Those units come back to APC, undergo inspection, and look at the cause of the failed battery.

Hope this helps.

Reply
Share
Iggy64_apc
Iggy64_apc
Cadet

Posted: ‎2021-06-28 09:43 PM

0 Likes
0
213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:43 PM

This was originally posted on APC forums on 7/23/2008


Thanks for your reply. I think I understand, but I'd like to clarify - - - -

The unit is covered under warranty for 3 years. A battery failure within 3 years is considered premature, and the unit should be examine by APC to determine the cause. APC will make repairs and - if necessary - replace the battery. Therefore, there is no need for me to buy user-replacement batteries during the first 3 years.

Apparently, the BX 1300 LCD model is less than 3 years old, so nobody that owns one needs to buy replacement batteries yet, for the reason given above. That's why APC isn't selling them. However, when the model has been on the market for 3 years, APC will make replacement batteries available to users.

Is that essentially correct?

Any rule of thumb for what replacement batteries cost? Are they, say, half the original cost of the UPS unit? Just curious.

Thanks very much for helping me out. Obviously, I can use all the help I can get right now.

Reply
Share
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:43 PM

0 Likes
0
214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:43 PM

This was originally posted on APC forums on 7/23/2008


I don't set the prices so I don't know what the price is going to be when it's released.

BUT other than that, your assumptions are correct. I wouldn't expect to see a sku'd battery for the first three years.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc