Red flashing power light and a constant beep tone after installing a new battery.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Red flashing power light and a constant beep tone after installing a new battery.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
11
14710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

Red flashing power light and a constant beep tone after installing a new battery.

I recently bought a replacement battery for my APC 550 Back Up, but when I went to put the new battery in I get a red flashing light and a constant beeping tone. I unplugged everything from the unit and tried it with nothing else plugged in and it still does it. I put the old battery back in and now the old battery is doing it too. What cold be the problem?

This is the battery I bought to replace the old one.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

Never replaced it before, the old battery is the original battery that came with it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

This sounds like the result of a failed self-test. Perhaps the new battery is unusually depleted or old stock?

I'd try leaving the unit plugged in but turned off (so it won't produce the constant beep tone) with the new battery in place for 24 hours. After that, if you have a DC voltmeter and feel comfortable doing so, disconnect the battery and take a voltage reading. It should be at least 12.8-13 volts by that point and may be slightly higher. If it isn't, I would suspect a possible bad replacement battery. Otherwise, just power the unit on and see if it behaves normally.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

Ok I will try that, but what explains that it now still does it when I put the old battery back in it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

Perhaps the old battery has a fault like a shorted cell, which would cause it to be drained of energy very quickly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

Oh ok, so it must have drained very quickly when I unhooked it and now that's why its beeping also.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

I left it plugged in for over 24 hours and when I turn it on its till beeping.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:25 AM

Hello Bill, 

The flashing red light and constant tone is indicative of a "replace battery" condition. Normally to clear it, you would need to do self test, which is automatically done whenever the unit is turning off. 

Where did you purchase the battery from? What is the model and serial number? Often, batteries can "dry up" if they sit for more that 6 months without being charged, and would need to be replaced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

This site's insert link option doesn't work, but I bought the battery on Amazon. The item number is PK1270F1.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

The replacement battery for the BE550G is the APCRBC110. We have seen this in units using third part batteries, because the battery does not meet the specifications that the unit is expecting. 

I would recommend using the APCRBC110, turning on the unit with no load over night, then adding load in the morning and running a self test. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

But  would that explain the old battery that came with it is now doing the same thing when I put it back in? It also makes the same noise and flashing light with no battery in it at all when I try to turn it on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

Hi Bill,

I agree with Shannon on the next steps moving forward. To answer your questions about the older battery, is this the original battery and if so, what's the serial number of your UPS? If you have replaced it before, was it a 3rd party battery or an authentic RBC?

Thanks,

Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

0 Likes
0
14709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:53 AM . Last Modified: ‎2024-03-27 01:24 AM

Never replaced it before, the old battery is the original battery that came with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore