Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Recommended power strip with BR1500G/BR1500GI

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Recommended power strip with BR1500G/BR1500GI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
7
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

Recommended power strip with BR1500G/BR1500GI

I know that power strips with Surge Protection capability are not to be used with UPS outlet ports. Would a normal power strip/extension cord suffice for my purpose?

Also, I have a power strip lying around here with "lightning protection" feature, is that the same with surge protection?

Thanks for your help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

If you are referring to the statement "Surge protectors filter the power for surges and offer EMI/RFI filtering but do not efficiently distribute the power, meaning that some equipment may be deprived of the necessary amperage..." then I'm bemused too. It implies surge protectors should never be used for computer equipment even on their own despite the fact that's what they being mainly sold and used for. So I tend to believe believe that original statement is a load of nonsense, and at best an exaggeration of major proportions. I would welcome anyone to explain otherwise. The only possible issue I can think of is the impact of having a square wave or modified sine wave input to the surge protector device.

Message was edited by: astor

Message was edited by: astor

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

BUMP!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

I actually read that link already before even creating this thread. Thanks for the info anyway. Though can you explain why do power strips NOT distribute current equally to the loads? I'm an electronics engineer by license and I don't quite seem to understand that statement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

We always recommend plugging directly from the UPS to the wall though ultimately, as long as you use a quality extension cord, it will probably be fine. We just can't technically support it and if there was a failure due to the extension cord, we would likely not cover it. As far as "lightning protection", I've never heard the term but I would say that would be the same as surge protection.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

What I meant is plugging a power strip to the outlet ports of the UPS, what is recommended? FYI, my UPS' input port is directly connected to the wall outlet.

Hmmm, I wonder what's that lightning protection.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

Well of course lightning is a very common cause of surges but yeah, I'm also curious why it's called lightning protection. I would recommend checking out the knowledge base document below for info on plugging surges or extension cords into the output which shows our official response to it but as I mentioned before, we don't recommend it but it doesn't necessarily mean it won't work.

http://nam-en.apc.com/app/answers/detail/a_id/1372/kw/surge

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

BUMP!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:56 AM . Last Modified: ‎2024-03-21 04:33 AM

If you are referring to the statement "Surge protectors filter the power for surges and offer EMI/RFI filtering but do not efficiently distribute the power, meaning that some equipment may be deprived of the necessary amperage..." then I'm bemused too. It implies surge protectors should never be used for computer equipment even on their own despite the fact that's what they being mainly sold and used for. So I tend to believe believe that original statement is a load of nonsense, and at best an exaggeration of major proportions. I would welcome anyone to explain otherwise. The only possible issue I can think of is the impact of having a square wave or modified sine wave input to the surge protector device.

Message was edited by: astor

Message was edited by: astor

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore