In PowerChute Personal Edition 2.0.0, it says "Note: Power problems of a very short duration are not recorded here". Just wondering what exactly is a "very short duration"? One second? Half a second? I know that it will record problems that last 4 seconds...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:03 AM . Last Modified: 2024-03-22 02:53 AM
Good day slapc,
The duration is 4 seconds, this is the frequency of polling the UPS.
Example:
We query the UPS now and see that all is well. And after 1 second the UPS goes to back-up for 2 seconds and gets back to normal operation in the next second. After 4 seconds when we query the UPS again the status will show as normal and the events which happened in these 4 seconds will not be captured.
JonPro
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:03 AM . Last Modified: 2024-03-22 02:53 AM
Good question..I had the same query when I saw this detail in the PCPE software. I believe that the PCPE software will not record the events which last lesser than 4 secs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:03 AM . Last Modified: 2024-03-22 02:53 AM
Good day slapc,
The duration is 4 seconds, this is the frequency of polling the UPS.
Example:
We query the UPS now and see that all is well. And after 1 second the UPS goes to back-up for 2 seconds and gets back to normal operation in the next second. After 4 seconds when we query the UPS again the status will show as normal and the events which happened in these 4 seconds will not be captured.
JonPro
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:03 AM . Last Modified: 2024-03-22 02:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:03 AM . Last Modified: 2024-03-22 02:53 AM
Thank you for the information.