Question About 2 Notebook Surge Protectors

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Question About 2 Notebook Surge Protectors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
8
1864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Question About 2 Notebook Surge Protectors

Hello,

I am looking to buy surge protector for traveling and 2 products caught my eye. Here are their models:

- PNOTEPROC6

- PNOTEPRO3 (this one is mentioned to be discontinued)

While the latter is discontinued it is twice cheaper now. I wonder how former (which I assume is newer) is better than one that is discontinued? By the way, both have a 3-prong power input and output which is the type of power supply I have on my DELL E6420 notebook.

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • laptop
  • notebook
  • protector
  • surge
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Hi Felix,

A better way to look at it would be with the voltage of a surge rather than the joules. The regulation for surge protection devices is that they can handle a 6,000 volt surge and still protect your devices. You then have different different levels of Let-Through voltage, which is the amount of voltage that your devices will actually see after the surge passes through the surge protector. This device has a max let-through of 330v, which most computer equipment can handle with no issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Hi Felix,

The main difference between the two products is that the newer unit has better surge protection.  If you look at the tech specs for each, you can find the 'Surge Energy Rating'.  The new unit has 600 Joules of protection, where the older unit only had 180 Joules.  The higher the Joule rating, the better the protection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Thanks Ben. How many joules does average lighting strike pack?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Hi Felix,

A better way to look at it would be with the voltage of a surge rather than the joules. The regulation for surge protection devices is that they can handle a 6,000 volt surge and still protect your devices. You then have different different levels of Let-Through voltage, which is the amount of voltage that your devices will actually see after the surge passes through the surge protector. This device has a max let-through of 330v, which most computer equipment can handle with no issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Which device of 2 that I mentioned has 330v maximum let-through? The one that handles up to 600 joules or 180 joules?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Hello Felix,

Both devices have that 330V let through voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

On 2/13/2017 7:59 PM, Shanon said:

Hello Felix,

Both devices have that 330V let through voltage.

Hi Shanon. I read this help article  about let-through and joules. So it seems that surge protector with less joules is better for small electronics?

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

A little off-topic, but did anyone else just get an e-mail notification of this forum thread that never subscribed to? In fact, how do I unsubscribe? I don't see any way to do that.

Thank you in advance. 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:31 AM . Last Modified: ‎2024-03-27 12:55 AM

Yes this is off topic. In the future questions or concerns about the forum should be posted under the heading of General Questions & Suggestions. 

You can edit your preferences and deselect "send me e-mail notifications". 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore