okay.. the model is be500y-IN... when i switch on the UPS it goes into a self test mode ... as usual like it does... i used to switch on the PC soon after the UPS is put on (and before the self test starts)
the self test will take place while the PC is booting up..until 2 days back.., when my PC is booting up and the moment the UPS goes into self test mode, my CPU is put off!as if, like it was being tripped off.. thats the issue. also..., when i try to test the UPS by switching off the mains when my PC is on, the system goes for a restart or OFF position... is this a confirmed symptom of battery failure?
when i spoke to the call center, the guy said there could be a problem with the pc's smps ...the ups is 2 yrs old approx..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Karthik,
I have attached the user manual for your UPS, see if you could find the description of the problem under Status Indicators.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
The battery was replaced and the problem is solved now...
thanks for the assistance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
It's good to hear that the issue has been fixed now. I was suspecting that it was the battery but I was not familiar with your unit since I am supporting units for US and Canada region.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Welcome to the APC forum Karthik!
Can you further explain what is going on with your UPS? Your post above says that your UPS runs a self-test the moment you turn it ON which is how it was designed. The UPS will then run another self-test after 14 days.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
oops..! im terribly sorry about that post.. i had typed the issue earlier and believed it was entered into the forum...dont know wat has happened.. nevertheless, here is the remaining of the post...
"the self test would take place while the PC is booting up..until 2 days back... When my PC is booting up and the moment the UPS goes into self test mode, my CPU is put off! as if, like it was being tripped off.. thats the issue..
also..., when i try to test the UPS by switching off the mains when my PC is on, the system goes for a restart or OFF position..mostly OFF"
Message was edited by: karthik316_1999
Message was edited by: karthik316_1999
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Karthik,
Thanks for giving this information. Now I understand it better, the computer shuts off whenever the UPS runs a self-test. Here are some steps that would help us diagnose the problem.
- Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
- Perform a self test on the UPS with no load attached to it. You run a self test by turning off and turning on the UPS or on some models while the UPS is online you could press and hold the On/Test and release it once the Online LED starts flashing
- Kindly observe the LED and Audio indicators of your UPS
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
-> The load attached gets switched off and the red light glows on the UPS with the beeper sounding continuously
Perform a self test on the UPS with no load attached to it
-> This runs just perfect
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
Result: The load attached gets switched off and the red light glows on the UPS with the beeper sounding continuously
Perform a self test on the UPS with no load attached to it
Result: This runs just perfect
Message was edited by: karthik316_1999
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
After running a self-test was there any LED light that lit up? Doing a pull plug test you've said that there was a read light that came on, was that the Overload LED?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:19 AM . Last Modified: 2024-03-22 03:26 AM
During the self test, the amber glows as usual and once it is done the green light turns back (when running self test successfully without the load connected)
The red light glows on but i dont have any separate LED's for the functions.. its just the colour of the same bulb... so yes, that should be the overload LED
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.