Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Problem with backup power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Problem with backup power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
10
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Problem with backup power

okay.. the model is be500y-IN... when i switch on the UPS it goes into a self test mode ... as usual like it does... i used to switch on the PC soon after the UPS is put on (and before the self test starts)
the self test will take place while the PC is booting up..until 2 days back.., when my PC is booting up and the moment the UPS goes into self test mode, my CPU is put off!as if, like it was being tripped off.. thats the issue. also..., when i try to test the UPS by switching off the mains when my PC is on, the system goes for a restart or OFF position... is this a confirmed symptom of battery failure?
when i spoke to the call center, the guy said there could be a problem with the pc's smps ...the ups is 2 yrs old approx..

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Karthik,

I have attached the user manual for your UPS, see if you could find the description of the problem under Status Indicators.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

The battery was replaced and the problem is solved now...
thanks for the assistance!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

It's good to hear that the issue has been fixed now. I was suspecting that it was the battery but I was not familiar with your unit since I am supporting units for US and Canada region.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Welcome to the APC forum Karthik!

Can you further explain what is going on with your UPS? Your post above says that your UPS runs a self-test the moment you turn it ON which is how it was designed. The UPS will then run another self-test after 14 days.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

oops..! im terribly sorry about that post.. i had typed the issue earlier and believed it was entered into the forum...dont know wat has happened.. nevertheless, here is the remaining of the post...

"the self test would take place while the PC is booting up..until 2 days back... When my PC is booting up and the moment the UPS goes into self test mode, my CPU is put off! as if, like it was being tripped off.. thats the issue..
also..., when i try to test the UPS by switching off the mains when my PC is on, the system goes for a restart or OFF position..mostly OFF"

Message was edited by: karthik316_1999

Message was edited by: karthik316_1999

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Karthik,

Thanks for giving this information. Now I understand it better, the computer shuts off whenever the UPS runs a self-test. Here are some steps that would help us diagnose the problem.

- Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
- Perform a self test on the UPS with no load attached to it. You run a self test by turning off and turning on the UPS or on some models while the UPS is online you could press and hold the On/Test and release it once the Online LED starts flashing
- Kindly observe the LED and Audio indicators of your UPS

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
-> The load attached gets switched off and the red light glows on the UPS with the beeper sounding continuously

Perform a self test on the UPS with no load attached to it
-> This runs just perfect

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Perform a pull plug test while your UPS is Online, let us know if the it would turn off or if the load attached to it turns off.
Result: The load attached gets switched off and the red light glows on the UPS with the beeper sounding continuously

Perform a self test on the UPS with no load attached to it
Result: This runs just perfect

Message was edited by: karthik316_1999

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

After running a self-test was there any LED light that lit up? Doing a pull plug test you've said that there was a read light that came on, was that the Overload LED?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

During the self test, the amber glows as usual and once it is done the green light turns back (when running self test successfully without the load connected)
The red light glows on but i dont have any separate LED's for the functions.. its just the colour of the same bulb... so yes, that should be the overload LED

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

0 Likes
0
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-22 03:26 AM

Karthik,

I have attached the user manual for your UPS, see if you could find the description of the problem under Status Indicators.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore