Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerChute Serial shuts down system immediately, regardless of Shutdown Settings choices.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PowerChute Serial shuts down system immediately, regardless of Shutdown Settings choices.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Back-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
binky
binky
Explorer

Posted: ‎2025-10-07 02:36 PM

0 Likes
9
4217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-07 02:36 PM

PowerChute Serial shuts down system immediately, regardless of Shutdown Settings choices.

Hi.

I have a Back-UPS RS 1500MS2 (s/n 0B2442L07828), purchased new in June of this year (2025). I'm using
PowerChute Serial Shutdown Agent Version 1.3.0.301 under Windows 11 Pro version 24H2.

I have tried these three "Power Outage Configuration" settings

- "Immediately"

- "After the UPS has been on battery for xx seconds"

- "At runtime limit xx seconds"

All three produce the same behavior - when a power event occurs, PCSS immediately initiates a system shutdown.

For example, I currently have "At runtime limit" selected, with a runtime of 360 seconds. UPS Status shows 
UPS Load 24.0%
Runtime Remaining 34 Minutes

I expected that the system would be able to run for as much as 28 minutes on battery before shutting down, but when the laser printer in the next room starts up, the resulting power event causes the UPS to switch briefly to battery, and PCSS immediately initiates a system shutdown. From the log:

10/6/25 15:02:41 No Longer On Battery
10/6/25 15:02:40 On Battery

So, one second on battery was enough to trigger a system shutdown.

Am I doing something wrong?

I've attached a troubleshooting archive file.

Thanks,

-Nick

Attachments
PcssFiles-1759872502389.zip
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Teken
Teken
Champion

Posted: ‎2025-10-08 03:57 AM

0 Likes
0
4212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-08 03:57 AM

Perform the following tasks and report back the results:

 

Disconnect the USB cable from the computer running APC PCSS application. What happens when you disconnect AC Mains from the UPS?!?

 

If it continues to run and power the connected loads time how long it does so and report back the results.

 

You may also install the legacy PCPE and report back the results. Please insure PCSS is properly uninstalled and the computer fully rebooted once removed.

 

You may use this APC Resource Link to download a copy of PCPE here:

 

https://www.se.com/us/en/download/document/APC_PCPE_310/

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

binky
binky
Explorer

Posted: ‎2025-10-08 02:37 PM

0 Likes
3
4190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-08 02:37 PM

Hi Teken.
Thanks for the reply. I performed the experiment you described:

  1. Disconnect the USB cable between the Back-UPS and the computer.
  2. Unplug the Back-UPS from mains power.

As one might expect, the Back-UPS front panel changed to show running on battery, with 34 minutes of runtime. The computer continued running normally, and did not shut down.

I did not wait for the battery to be exhausted. I'm not sure what that would have accomplished, other than to test the accuracy of the displayed runtime. 

So it appears that PCSS really is behaving as I hypothesized - initiating a shutdown before the configured conditions occur.

Is the preferred solution really simply to consign PCSS to the bin and use different software?

Is the communication protocol the Back-UPS uses published anywhere?

Thanks again,

-Nick

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-10-09 01:14 AM

In response to binky
0 Likes
2
4188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-09 01:14 AM

The first step of removing the USB cable and replicating a lights out / grid down event was to isolate and confirm the UPS was not at fault and fully operational. In this case the test affirms the UPS and RBC is fine.

 

The suggestion to use the legacy PCPE was again to help isolate the problem. Whether it be PCSS, Windows, USB Drivers, Power Management etc.

 

If PCPE works fine without issues than the next step is to gather logs and submit the same to APC Technical Support to help identify root cause and hopefully offer a break fix / end solve.

 

My suggestion is simply a troubleshooting (Go / No Go) method to narrow root cause. Along with offering the end user a break fix to use in the interim instead of having nothing to use.

 

As an aside you may also consider using APCUPSD / NUT software if either do not work as expected.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

binky
binky
Explorer

Posted: ‎2025-10-09 02:06 PM

In response to Teken
0 Likes
1
4172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-09 02:06 PM

Hi @Teken.

My apologies - I misunderstood the direction of your inquiry. I've since uninstalled PCSS and installed PCPE from the link you provided. I configured PCPE to "Keep my computer on as long as possible," with shutdown scheduled at five minutes of battery power remaining.

With the USB cable connected from the Back-UPS to the computer, I unplugged the Back-UPS from mains power. Its front panel displayed that it had switched to battery power with about 28 minutes remaining.

The computer did not shut down. The PCPE console reflected the same information, with the "Time Until Shutdown" shown as 23 minutes.

PCPE provides all of the functionality I need, but as it is no longer being maintained, it represents an unknown, but likely increasing, risk. APCUPSD also appears no longer to be maintained. NUT may be a reasonable alternative. 

How does one go about contacting APC/Schneider technical support? This forum is as close as I was able to get. My original post includes a troubleshooting archive file.

Thanks again for your help.

 

-Nick

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-10-10 06:08 AM

In response to binky
0 Likes
0
4167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-10 06:08 AM

Since it appears APC / Schneider has once again decided to update their website the usual and expected links no longer work! 🤦‍♂️

 

As such please endure using this link and if available select the country required and select Chat, Phone, Email.

 

https://www.se.com/us/en/work/support/

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

fredkm
fredkm Troubleshooter
Troubleshooter

Posted: ‎2025-10-13 02:32 AM

0 Likes
3
4091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-13 02:32 AM

From the logs it doesn't look like PCSS triggers a system shutdown. What I do see is PCSS getting notified by the OS that the system is going into hibernate/sleep:

2025-10-06 15:02:40,281 [PcbeHSM-EventDispatcher] INFO  - [application.PicardApplication.()] stateTransitionNotify signal=XXX_TO_POWERFAIL
2025-10-06 15:02:40,335 [SMTPMailWorker] WARN  - [SMTPMailer.SMTPMailWorker.()] Subject :Dinsdale : On Battery
2025-10-06 15:02:41,368 [PcbeHSM-EventDispatcher] INFO  - [application.PicardApplication.()] stateTransitionNotify signal=POWERFAIL_TO_XXX
2025-10-06 15:02:41,368 [PcbeHSM-EventDispatcher] INFO  - [application.PicardApplication.()] stateTransitionNotify signal=POWERFAIL_TO_ONLINE
2025-10-06 15:02:43,050 [Thread-716] WARN  - [application.PicardApplication.()] Request received from OS to suspend.

Not sure what could cause this. PCSS installation should disable native power management for the UPS,  and OS sleep/hibernate should not be triggered by the UPS switching to battery power. Do you have another battery in your system (apart from the connected UPS)? If so, can you ensure in Windows Power Settings you have configured your OS not going to sleep/hibernate when on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

binky
binky
Explorer

Posted: ‎2025-10-13 08:49 AM

In response to fredkm
0 Likes
2
4067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-13 08:49 AM

HI @fredkm.

Thanks for the input. The computer has no other battery - it's a desktop system. It is configured never to go into hibernate mode. Besides, the only event that occurs is the momentary power sag caused by the laser printer starting up. The computer should never see that, since it's being powered by the UPS.

The now-obsolete PowerChute Personal Edition handles the power event correctly, simply reporting the switch to battery power and back to mains power without shutting down the system.

 

I suspect the relevant log entries are in this section:

2025-06-05 17:58:34,468 [M11ComponentManagerThread] WARN  - [DataModels.NewShutdownHandler.()] Shutdown FSM created
2025-06-05 17:58:34,468 [ShutdownExecutor Thread-1] INFO  - [HelperClasses.ShutdownFSM.()] Starting Shutdown FSM
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-2] INFO  - [DataModels.M11OSShutdown.()] unable to retrieve the OS Shutdown Delay information from PS, using default.
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-3] ERROR - [DataModels.NewShutdownHandler.()] PCBEOutletMonitorTask - Could not determine pcbe outlet
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-3] ERROR - [DataModels.NewShutdownHandler.()] PCBEOutletTurnOffDelayMonitorTask - Could not determine pcbe outlet
2025-06-05 17:58:34,469 [M11ComponentManagerThread] INFO  - [MicroLinkPowerSource.MicroLinkPowerSource.()] added ShutdownHandler data model to DataModelRegistry
2025-06-05 17:58:34,469 [M11ComponentManagerThread] INFO  - [MicroLinkPowerSource.MicroLinkPowerSource.()] added TriggerConsumer data model to DataModelRegistry
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-2] INFO  - [DataModels.M11OSShutdown.()] getCommandFiles() - unable to retrieve list of command files
2025-06-05 17:58:34,469 [M11ComponentManagerThread] INFO  - [MicroLinkPowerSource.MicroLinkPowerSource.()] added UserInformation data model to DataModelRegistry
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-2] INFO  - [DataModels.NewShutdownHandler.()] Adjusting OS SD Delay from 60 secs to 0 secs

Specifically these two lines:

2025-06-05 17:58:34,469 [ShutdownExecutor Thread-2] INFO  - [DataModels.M11OSShutdown.()] unable to retrieve the OS Shutdown Delay information from PS, using default.
2025-06-05 17:58:34,469 [ShutdownExecutor Thread-2] INFO  - [DataModels.NewShutdownHandler.()] Adjusting OS SD Delay from 60 secs to 0 secs

Why ShutdownExecutor is unable to retrieve the shutdown delay from PowerChute is probably the key, although why it later chooses to change the value from what is presumably the default of 60 seconds to zero is another question.

 

Schneider technical support is looking into the issue. I'm still waiting for their report.

 

Thanks again,

 

-Nick

Reply

Link copied. Please paste this link to share this article on your social media post.

binky
binky
Explorer

Posted: ‎2025-10-15 02:44 PM

In response to binky
1 Like
1
4048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 02:44 PM

Hi @Teken, @fredkm.

Well, this one ends with a mystery. At Schneider's request, I reinstalled PCSS to retest, and was unable to duplicate the problem. I supposed I could have tried uninstalling and reinstalling PCSS before going any further, but it didn't occur to me - nor is it a very appealing approach to troubleshooting.

At any rate, problem solved, if not understood. At least for now.

Thanks,

-Nick

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-10-16 03:11 AM

In response to binky
0 Likes
0
4042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-16 03:11 AM

Appreciate the follow up and final outcome. Keep an eye on it and report back any further issues. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore