Back-UPS alarm, no light, newish battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS alarm, no light, newish battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
dpfels
Crewman dpfels
Crewman

Posted: ‎2025-10-13 05:31 AM

0 Likes
5
751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-13 05:31 AM

Back-UPS alarm, no light, newish battery

Hi,

I have a Back-UPS 600.  I replaced the battery  less than 6 months ago.

This morning, I woke up to the unit emitting a solid beep with the power light off.  When I reset the alarm (holding down the button to shut off the unit, then repowering), it returned to the same alarm state.  I checked the outlet (it works).  I moved the UPC to another powered outlet.  Even after leaving it to charge for 30 minutes, it returns to an alarm state when powered on.

I suspect this is a power overload problem, but there is nothing currently plugged into the UPC.  Is there any way to reset the unit?

Thanks,

Dan

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2025-10-16 02:58 AM

In response to dpfels
1 Like
0
666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-16 02:58 AM

Appreciate the follow up and added information and would agree the unit is broken and needs to be replaced.

 

I suggest you wait until Black Friday for a sale to ease the pain of buying a new system.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Teken
Kirk Teken
Kirk

Posted: ‎2025-10-14 03:26 AM

0 Likes
4
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 03:26 AM

If the system isn’t connected to a computer running APC Power Chute Software do so now and wait for the system to declare the active fault / error.

 

Screen capture the tabs that show the following information: Input / Output Voltage, Power, Battery Voltage.

 

Than export the following logs from (PCSS / PCPE) event, data, ups, diagnostics and upload the same here for review.

 

Brain Dead: Once the above has been done complete the brain dead procedure and report back the results:

 

https://www.apc.com/ca/en/faqs/FA158947/

 

Questions Ask . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

dpfels
Crewman dpfels
Crewman

Posted: ‎2025-10-14 06:25 AM

In response to Teken
0 Likes
3
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 06:25 AM

Hi,

I have already tried the “Braindead” procedure, with no improvement. 
I am using a Mac so running Power Chute is not as easy (will bring home my work computer to do this,

but it may take a few days.). 
In any case, a full reset (Braindead) didn’t solve my problem. 
Dan

Reply

Link copied. Please paste this link to share this article on your social media post.

Jimzap531
Crewman Jimzap531 Crewman
Crewman

Posted: ‎2025-10-15 12:33 AM

In response to dpfels
0 Likes
2
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 12:33 AM

Hi, Dpfels,

 

By serial number, if the UPS is old or discontinued, it is better to recommend a new UPS, example: AS07XX (2007)

 

Here are some recommendations or tests to perform, in the following FAQ file.

Video: Why might my APC Back-UPS Product be beeping?

https://www.se.com/us/en/faqs/FA158827/

 

Best regards,

 

Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

dpfels
Crewman dpfels
Crewman

Posted: ‎2025-10-15 05:18 AM

In response to Jimzap531
0 Likes
1
703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 05:18 AM

Hi,

The even log is attached.  As you can see, it indicates an overload status, which is solved by turning the unit off.

Regarding the unit status, it shows the battery, (APC branded, purchased in April 2025) as 100% charged.  Details copied below.

Finally, the unit itself was purchased in 2020.  It is a BE600M1, so hardly out of date (still offered for sale on Amazon as of today.)

 

One final thing: I also tried running the Brain Dead protocol (battery out, unplugged, no load, holding down the power button for >5 seconds), but leaving it unplugged with no load and no battery for about 10 hours to ensure that any memory/storage was completely erased.  This also made no difference.

 

I am coming to the conclusion (wait for it) that my unit is fried.  I assume that there are some components inside that can fail (surge suppressors, for instance)?  Is there any other way to reset the unit or confirm that it is truly dead?  At 5 years of age, I don't think I qualify for warrantee service (although I am annoyed that I just purchased a new battery.)  If it is beyond repair, I will move on to purchasing a new UPS.

Thanks,

Dan

- System Status

On Line
0.0
%
493
Minutes

- Power Status

123.0
VAC

- Battery Status

100.0
%
13.5
VDC

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-10-16 02:58 AM

In response to dpfels
1 Like
0
667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-16 02:58 AM

Appreciate the follow up and added information and would agree the unit is broken and needs to be replaced.

 

I suggest you wait until Black Friday for a sale to ease the pain of buying a new system.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore