PowerChute 3.0.2 data accuracy?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PowerChute 3.0.2 data accuracy?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
2
886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

PowerChute 3.0.2 data accuracy?

Hi;

I have a BR800BLK that is 8 years old this month. I recently replaced the battery set with an SPS brand. Now I am starting to notice that the BR800 is switching briefly (<5sec) from AC to battery power, even though line voltage has not been interrupted.

i ran the self-test from the PowerChute software and the BR800 passed the test.
Battery status is being reported as 100% charged, and the load is only about 150W, with about 40min backup time.

While viewing the current status tab in Powerchute, I noticed that the line voltage was fluctuating from 125V most of the time, to between 115V and 120V for brief periods.
I was monitoring the line voltage on a DMM during the time I saw the fluctuations in Powerchute, and there was no fluctuation at all on the DMM. It was reading a steady 123.7V.
On the powerchute performance tab, no power problems have been reported, despite the BR800 switching briefly to battery while I had the software open. But both the Br800 and powerchute  do indicate that it has switched to battery when it does.

These events appear to happen in clusters. I heard it switch to battery at least once this morning before I had my computer turned on, then it happened again while I was using the computer but did not have APC services running. I then started the services and opened Powerchute to see if I could learn anything, but so far I have not.

About the apparently erroneous voltage fluctuations; could this be the source of the brief switch-overs? But I have the sensitivity set to medium, which sets the high limit to 139V and the low to 102V, neither of which I have observed in Powerchute during an event.

I do recall that, before I changed the battery, the BR800 was switching to battery often, and also for brief periods like it is doing today. Eventually, the unit would not supply any power, either from AC mains or battery, so I changed the battery. That fixed the problem.

So what do you think? Is it time for a new UPS? I had considered replacing it before I decided to replace the battery, but I am now beginning to second guess my decision not to replace the BR800.

I would appreciate your suggestions/ideas.

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • power
  • PowerChute
  • problem
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
0
886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

Hi Bill;

I have set the sensitivity to low. This has apparently solved my problems with the BR800. But I wanted to do some more extensive testing using a variac (or the type thas is only a variable transformer, and therefore does not introduce waveform distortion or noise into the BR800). I found that the switch-over from AC to battery always occurs at a much lower voltage than the low setting in PowerChute. For example; when PowerChute is set to low sensitivity, and voltage setting of 100/139, the switch from AC to battery occurs at 78.5V, and switches back to AC at 83.5V. When I ran my tests, I set the variac using a DMM connected to the input of the BR800, and once adjusted, I let it sit at that voltage for several minutes to find whether the BR800 would switch after time.

Interestingly, if I set the low voltage in PowerChute to 104V, the switchover from AC to battery occurred at 78.2V, and switch back to AC at B.

When sensitivity was changed to medium, with low voltage set to 104V, switchover from AC to battery occurred at 88.0V, and switch back to AC at 94.1V.

When sensitivity is set to high, I was unable to collect data, as the BR800 switched erratically at almost all voltages between 100V and 130V.

Then, there is this really strange behaviour which the BR800 exhibits under very specific conditions:
If sensitivity is set to high, and the input voltage is brought to about 128V, the BR800 will switch back and forth several times, but then it will latch up in the battery mode, and remain there until the input voltage is lowered to around 127V. It did not appear to make any difference what the voltage settings in PCP were.

None of these problems occur when sensitivity is set to low, which is where I am going to leave it.

Thinking that this issue could be caused by line noise, I installed two clamp-on ferrites onto the BR800 line cord at various points. There was no change in occurrence of the problem. I do not know what the value of these ferrites was, although I do have the means to test them if you want me to. I thought I might want to try other ferrites, selected for the most common line noise that might be present. Unfortunately, I have no means of analyzing the AC line for noise, except to try different chokes.

The last thing I tried was to disconnect all of the battery backed-up loads from the BR800. But the BR800 continued to exhibit the problem.
Note that all of the problems occur when the sensitivity setting is at medium or high, with the most frequent of course at high.

Unless you have something further I should try for the problem, I am going to leave the sensitivity set to low. I will keep you informed if there are any changes.

FW

See Answer In Context

  • Tags:
  • br800
  • sensitivity
  • switching
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
0
885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

Hi,

PowerChute will only report the data that is received from the UPS. Try setting the sensitivity to low and monitor it. If that does not help and the voltage is not fluctuating but the UPS is reporting it then it may be time to replace it. 

As for PowerChute not recording the switch to battery, this may happen if the switch is less than 4 - 5 seconds. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
0
887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-27 12:37 AM

Hi Bill;

I have set the sensitivity to low. This has apparently solved my problems with the BR800. But I wanted to do some more extensive testing using a variac (or the type thas is only a variable transformer, and therefore does not introduce waveform distortion or noise into the BR800). I found that the switch-over from AC to battery always occurs at a much lower voltage than the low setting in PowerChute. For example; when PowerChute is set to low sensitivity, and voltage setting of 100/139, the switch from AC to battery occurs at 78.5V, and switches back to AC at 83.5V. When I ran my tests, I set the variac using a DMM connected to the input of the BR800, and once adjusted, I let it sit at that voltage for several minutes to find whether the BR800 would switch after time.

Interestingly, if I set the low voltage in PowerChute to 104V, the switchover from AC to battery occurred at 78.2V, and switch back to AC at B.

When sensitivity was changed to medium, with low voltage set to 104V, switchover from AC to battery occurred at 88.0V, and switch back to AC at 94.1V.

When sensitivity is set to high, I was unable to collect data, as the BR800 switched erratically at almost all voltages between 100V and 130V.

Then, there is this really strange behaviour which the BR800 exhibits under very specific conditions:
If sensitivity is set to high, and the input voltage is brought to about 128V, the BR800 will switch back and forth several times, but then it will latch up in the battery mode, and remain there until the input voltage is lowered to around 127V. It did not appear to make any difference what the voltage settings in PCP were.

None of these problems occur when sensitivity is set to low, which is where I am going to leave it.

Thinking that this issue could be caused by line noise, I installed two clamp-on ferrites onto the BR800 line cord at various points. There was no change in occurrence of the problem. I do not know what the value of these ferrites was, although I do have the means to test them if you want me to. I thought I might want to try other ferrites, selected for the most common line noise that might be present. Unfortunately, I have no means of analyzing the AC line for noise, except to try different chokes.

The last thing I tried was to disconnect all of the battery backed-up loads from the BR800. But the BR800 continued to exhibit the problem.
Note that all of the problems occur when the sensitivity setting is at medium or high, with the most frequent of course at high.

Unless you have something further I should try for the problem, I am going to leave the sensitivity set to low. I will keep you informed if there are any changes.

FW

  • Tags:
  • br800
  • sensitivity
  • switching
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of