UPS shuts down long before battery is empty

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS shuts down long before battery is empty
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
4
12036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

UPS shuts down long before battery is empty

Hello

I have the following problem with my Backup UPS BX700U-GR: the UPS shuts itself down when running on battery long before the battery is nearing depletion.


So Power Chute is telling me that I have something like 70 minutes on battery.

I unplug the UPS from mains, then time to shutdown becomes 9 minutes and it does indeed shut down after that.

In Power Chute I have it configured for maximum time on battery, i.e. it should shut down the computer when there are only 5 minutes of battery left.

It's like this option is not working, it is like the Power chute is configured to shut down not when the battery still has 5 minutes, but after 9 minutes on battery.

This is obviously very annoying, because I want the UPS to stay on for as long as it can.

After it shuts down, if I press the ON button, it will come back to life, but  turns off  almost immediately. So maybe the battery is faulty and Power Chute does not report correctly the time I have on battery when the UPS is powered? I do not know.


Your help is kindly appreciated.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
0
12023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

Hi,

The issue is the Back-UPS is not reporting the proper available runtime while running on AC. When the UPS switches to battery it calculates the load to the battery charge and updates the available runtime to 9 minutes. Depending on the load the issue may be the battery needs replacement. How old is the UPS and the battery? If the battery is more than 4 years old and the unit has run on battery many time or the environment is hot or cold the battery will degrade sooner.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

0 Likes
0
12023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

HI, thanks for the reply.

The UPS is 2 months old, so basically brand new, it  is kept indoors so temperature is about 23 degrees Celsius permanently. Battery date is Nov 2016.

Self tests says it's ok. The UPS basically is supposed to keep 2 routers running, load is approx. 5%, so very low.

So you think the battery is defective out of the box?

I don't know: even before shutting down, the battery level reported is high - I have tested at 90% to 60%, the battery % never drops when AC is switched off and if I power the UPS back on, it does run for longer than the initial 9 minutes.

So it means it is reporting incorrectly even without AC?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

0 Likes
0
12024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:37 AM

Hi,

The issue is the Back-UPS is not reporting the proper available runtime while running on AC. When the UPS switches to battery it calculates the load to the battery charge and updates the available runtime to 9 minutes. Depending on the load the issue may be the battery needs replacement. How old is the UPS and the battery? If the battery is more than 4 years old and the unit has run on battery many time or the environment is hot or cold the battery will degrade sooner.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

0 Likes
0
12024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

HI, thanks for the reply.

The UPS is 2 months old, so basically brand new, it  is kept indoors so temperature is about 23 degrees Celsius permanently. Battery date is Nov 2016.

Self tests says it's ok. The UPS basically is supposed to keep 2 routers running, load is approx. 5%, so very low.

So you think the battery is defective out of the box?

I don't know: even before shutting down, the battery level reported is high - I have tested at 90% to 60%, the battery % never drops when AC is switched off and if I power the UPS back on, it does run for longer than the initial 9 minutes.

So it means it is reporting incorrectly even without AC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

0 Likes
0
12022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

You may be observing the No Load shutdown feature enabled on the BX700U-GR.

Please reference the following information, which can be found in your Users Manual.

Secret Squirrel

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

0 Likes
0
12021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:58 AM . Last Modified: ‎2024-03-27 12:36 AM

thank you, that was indeed the issue.

I disabled it and now it seems to work.

much appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore