Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Power protection advice needed

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Power protection advice needed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
148
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

0 Likes
6
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

Power protection advice needed

I think I should describe my setup before asking my question:

I just had two new circuits put into my office, making at least three, possibly four (my husband thinks the existing plugins were already on two separate circuits.

Into a Back-UPS NS 1250 I have plugged
a Mac Pro
four internal hard drives (20gb total)
One pci slot is filled with a usb card adding four ports
Am using two LCD monitors each 26 inches but only one is plugged into the NS 1250.
Also plugged in are my router & modem, and small speakers

Into a separate APC surge arrest unit I have plugged a phone (digital), my ethernet cord, a small laser printer, and an external usb hub. This was plugged into the same wall circuit and is now plugged into a separate circuit since I had a problem last night with my setup.

My photo printer, scanner and second 26" monitor are plugged into a Backup LS 700 on a separate circuit. When I use an external drive for backup I plug it into the LS 700.

We had a storm last night. This morning the NS 1250, which is the newest protector, possibly still under warranty, was blaring a warning. "Replace Battery."

Of course it's the weekend and no one at APC is available. Other than the green "on Line" light, there are no lights that I can see to tell me if the rest of the protection is still working. I'm even more concerned about brownouts, power surges etc, than I am about battery backup.

So my main question is whether my equipment is protected even though the battery is dead. Should I be pulling plugs until I can replace the battery or the whole unit?

I'm a total novice and can't afford to replace my equipment. Have been reading threads and someone said "have only the computer and monitor plugged into one unit and that in a separate circuit." Why then are there more receptacles? I have a large U shaped desk (working with photoshop mostly) and cords keep getting shorter. If my cpu and monitor need a separate power protector and separate electrical circuit I will have to figure out a whole new arrangement for my equipment.

Please, can anyone help with the protection question or give other advice?

Peggy

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

It's so good to know questions can be answered on weekend. I'm powering off now. There is actually another storm heading this way. June has been unusually active! Thanks again!
Peggy

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

Hi. Thank you for your quick response! The replace battery LED is solid. I'm not sure from what I've read if the software will work on an intel Mac Pro. I just switched from Windows a few months ago. I think I downloaded a Mac version from the APC website awhile ago but if it doesn't work there's no sense in installing it.

It's safe, then to leave my computer on while it (hopefully) recharges? Will it do the "self-test" without the software. I remember that there was an option to test using the software.

Thank you about the reassurance about the other equipment.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
TheNotoriousKMP_apc
Contributor

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

Hi Peggy,

Was the replace battery LED on the front of the UPS flashing or blinking? If it's flashing, verify the battery connection. If it's solid, and you experience a sustained power outage and the UPS ran on battery, chances are, the UPS is just indicating that it's in a low battery state and needs some time to recharge and then a self-test should clear that. Do you have any APC PowerChute software integrated into this setup? That should provide some useful information in helping to arrive at a cause/problem/resolution.

Also, as far as your setup, I wouldn't worry about the equipment plugged into the UPS. The extra ports there are available for peripherals, which is what you seem to be using it for.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
TheNotoriousKMP_apc
Contributor

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

Peggy,

Since you just switched to a Mac recently chances are there's no supported software for you, yet.

As for the charging, yes the design of the UPS will allow a trickle charge to the battery while outputting most of the input power to the load attached.

In order to run a self-test without software, simply depress the power button for 4-5 seconds and you'll see the Green ONLINE LED flash, you can release the power button and the self-test should initiate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:22 AM

Thank you again. Can you tell me if the other protection, such as from surges, is still working even though the battery is not?

As soon as I find out about that, I'm going to power down my computer because if understand you, that will allow the battery to recharge faster and I will know if I need a new battery or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
TheNotoriousKMP_apc
Contributor

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:33 PM . Last Modified: ‎2024-03-26 12:18 AM

Peggy,

Yes regardless of a fully functional battery you still have full surge protection and range of Automatic Voltage Regulation.

And yes unplugging equipment from the UPS will allow it to charge faster.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

It's so good to know questions can be answered on weekend. I'm powering off now. There is actually another storm heading this way. June has been unusually active! Thanks again!
Peggy

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore