RS1500 detecting no voltage when power still on

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • RS1500 detecting no voltage when power still on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
5
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

RS1500 detecting no voltage when power still on

Ever since the power company upgraded my electrical and gas meters to Smart Meters, my RS1500 will detect a no-voltage condition while everything else in the house remains powered. At first, I thought it was just dirty power since it had the classic brief click/beep pattern to it. I reset the sensitivity of the unit with no luck. I then noticed that this occurs at very regular times of day, so I was able to grab the voltage info during these events twice this weekend. Both times, it said the current voltage was 0 volts but nothing else in the house so much as flickered. Checking the voltage at other times when the UPS is fine returns 119 to 121 volts, which is pretty much expected.

I suspect it is related to the Smart Meters calling home. If you are not familiar with them, basically Smart Meters have the capability to transmit usage data back to the power company at regular intervals. The Smart Meters installed at my home are using radio waves for sending their data. I do not know the frequency that they use other than it is the same frequency used by Casablanca remote controlled ceiling fans. I had the power company out on Thursday and they said the voltage on the line was fine, although they did not come out during one of the problem times like I asked. At this point, I suspect that either the Smart Meters are either a) causing dirty power even though they don't transmit data over the power lines or b) causing RF interference that is causing the RS1500 to mistakenly detect a "power out" event.

Has anyone experienced this? Or is there an electrical engineer out there who might be able to theorize why the Smart Meter would make the RS1500 thinks there is 0 volts when there is indeed power? I'm still trying to get the power company to step up and take responsibility for this problem, but it would help to have a better idea of what is happening in the first place. Right now, the only problem with the Smart Meters that they will acknowledge is that it operates on the same frequency as the Casablanca ceiling fans.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

I have it set up to query the UPS on each on-battery event and log the results now. The logs show mostly 0 volts during the events, although occasionally it shows normal voltage (119-121V) but still "onbatt" status. I suspect the later occurs when the event is so brief that by the time the query is processed, it is over and the voltage is back to normal. The UPS does not have time to get through the whole click, 4 beep sequence of a normal power outage during most of these events because they are so brief.

Edited to add this paragraph: I also have it set up to log the voltage every 5 minutes. Those logs show a consistent voltage of 118-122V for the last 4 days (when I started that log). So far, no event has coincided with this every 5 minute logging.

Voidstar, is there any specific sort of testing to do to see if it is the meter? My dad works in the hardware side of computers (I'm purely a software/security person), so I can run over to his place over the weekend and borrow some of his tools to test the outlet. I just have no clue what to look for.

Message was edited by: Shwaine

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

that is quite interesting. i am eager to also see what you find out. i wasnt aware of these "smart meters."

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:18 AM

I've done some more digging today and it seems the power company person from Thursday was somewhat mistaken about the Smart Meters. The gas meter does indeed use radio frequencies (450-470MHz) to transmit its data. However, the electric meter uses the TWACS protocol for data over power lines to transmit its data. I would chalk this all up to dirty power caused by the electric meter except that still doesn't explain why, when queried, the UPS says it is detecting 0 volts on the line during these events. I would expect to see high or low voltage spikes during a data over the power line transmission, but not 0 volts. Is there some modulation the TWACS unit might be doing that would fool the UPS into thinking the power had gone out?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

I can't say anything definitive without testing the UPS with a TWACS energy meter.

In general, in order to determine the AC voltage, the UPS has to determine the frequency and phase of the input line. To do that, the UPS looks at the zero crossings where the voltage goes positive to negative or negative to positive.

Coincidentally, from what I can find online, it looks like TWACS modulates the line near the zero crossing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

Can you log the voltage over time using PowerChute? It is possible the power line carrier is interfering with the UPS' detection. If it seems very cyclical, then the meter is likely the blame.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

0 Likes
0
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:34 PM . Last Modified: ‎2024-03-26 12:17 AM

I have it set up to query the UPS on each on-battery event and log the results now. The logs show mostly 0 volts during the events, although occasionally it shows normal voltage (119-121V) but still "onbatt" status. I suspect the later occurs when the event is so brief that by the time the query is processed, it is over and the voltage is back to normal. The UPS does not have time to get through the whole click, 4 beep sequence of a normal power outage during most of these events because they are so brief.

Edited to add this paragraph: I also have it set up to log the voltage every 5 minutes. Those logs show a consistent voltage of 118-122V for the last 4 days (when I started that log). So far, no event has coincided with this every 5 minute logging.

Voidstar, is there any specific sort of testing to do to see if it is the meter? My dad works in the hardware side of computers (I'm purely a software/security person), so I can run over to his place over the weekend and borrow some of his tools to test the outlet. I just have no clue what to look for.

Message was edited by: Shwaine

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore