Poor backup performance on APC Home UPS with a 100Ah Battery ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Poor backup performance on APC Home UPS with a 100Ah Battery ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:10 AM

0 Likes
11
3001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:10 AM

Poor backup performance on APC Home UPS with a 100Ah Battery ?

I have a 600VA(model no. HI600SQ) ups with a 100Ah battery. I merely get about 90 Minutes of backup when running on batteries at just half the load. I had both the battery and UPS replaced under warranty and its the same.There is a scheduled power cut for exactly 2 hours everyday, so that gives 22 hours without any interruptions for the battery to charge which I believe should suffice .

The people at APC tell me that I should get atleast 4 to 5 hours of backup running at about half the load(300VA/~180 Watts) and 2 hours at full load(600VA/~360 watts). APC has load indicators to indicate the load when running on the batteries

I m totally clueless on what to do next ? The electrical appliances connected are just a couple of tubelights and fans. Regarding the replacement under warranty, the techs who examined the UPS said it was fine and so did the battery shop guy, but I got it replaced anyway just to make sure.

How would I able to diagnose if something is wrong in the wiring configuration ? Thats the only thing left for me to diagnose, but where and how do I start ?

Any thoughts would be appreciated

Anjay.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
3000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

The website has a product catalogue of all the models available in India. This is all the info I could get

BATTERY SPECS_

Model name : AMCO A100T (dry charged series)
Voltage : 12V.
Capacity(Ah)20hr : 100
Nominal Wt. Filled : 27 Kgs.
Electrolyte Volume : 7.2 Liters
Charging Current : 10 Amps
Dimension(L*B*H) : 410*176*233 mm.

Environment temperature is 30 to 34 C.

And by power factor I believe you are referring to the watts consumed by the electrical appliances.

At full load, all the appliances connected to the UPS consume 380 Watts or 600 VA. In this case I barely get about 45 minutes of battery backup.

At half load, approximately 160-180 watts is what I normally use. Here the battery backup lasts only upto 90-100 minutes average.

As I mentioned earlier when I started the thread, I have a scheduled power cut for 2 hours everyday. There are no interruptions after this power cut, hence giving it a full 22 hours to charge everyday.

Hope to hear from you soon


Thanks,

Anjay. K.



P.S: This is their website [http://www.amco.co.in/downloads.php?id=d#]

Message was edited by: anjaykm

Message was edited by: anjaykm

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:10 AM

0 Likes
0
3000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:10 AM

The only real wiring you need to be concerned about in terms of battery connection are the 12v +/- DC ports on the back of the unit. You may be using the APC trolley that supports the batteries and provides a little jumper to attach to the HI600SQ unit or the connector that came with the unit, or you may be using a third party connector. Either way, as long as the port's connection is secure and the +/- leads are properly connected and you are using a 12v battery, there isn't much else to consider battery-wise.

Can you provide the battery manufacturer, and all the specs? I'd like to double check this runtime estimation you have been provided.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
3000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

I m using the battery connectors that was given by APC. The connection seems to be solid since its been only 4 months since I bought the UPS. And there is no corrosion at the terminals so far.


The battery is a AMCO 100 Ah, what other specs would you like to know about the battery ? Not sure what else there is, dont see much given in the Product manual. I m not sure if you have heard of that manufacturer, since I m in India.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

Just to confirm, that's a 12v battery? Any other manufacturer's specs you could provide, no matter how trivial they seem would help. I vaguely recognize the AMCO name but I am not familiar with their product offerings. We'll try to run another calculation once we have any other details you can give. I can also try to google the battery if needed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
3000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

Yes it is a 12V battery.

THis is what I could find in the manual.

"Ensure voltage regulator range is between 14.2 and 14.4 for 12 volts battert. Output beyond 14.4 leads to overcharging and frequent topping up"

I hope this is helpful ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

anjaykm wrote:
Yes it is a 12V battery.

THis is what I could find in the manual.

"Ensure voltage regulator range is between 14.2 and 14.4 for 12 volts battert. Output beyond 14.4 leads to overcharging and frequent topping up"

I hope this is helpful ?
I'll look into this and see if we get the same calculation. Typically APC has runtime charts for our own units using our own batteries...I'm not sure where this 4 or 5 hour estimation came from. I'll also look into seeing if there's something else configuration-wise that might be missing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

Still researching the issue...had to try and pull what we could off the web to fill in some info on the AMCO battery. Will return later once we've figured the calculation out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

Oh ok, I thought you forgot about it..


Thanks in Advance

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

Alright we're still going to need more information since nothing AMCO has is helping with our calculation.

We need the exact battery model, since there is no info on the web about a generic "AMCO 100ah battery", power factor of the load you are using, and environment temperature.

Any data we can get on the "per battery cell" specs on the battery and total battery performance would be helpful. I don't know how the calculation was done when you spoke to a rep earlier without all the detailed information, since we typically do not provide battery runtimes for non-APC batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

I do not see anything wrong with the back up mentioned in the thread. At half the load i.e, 300VA/180W the user is getting 90 minutes back up approximately. This draws about 30A from battery assuming 90% efficiency of square wave inverter. Please remember two points now:
1. Assuming 100% battery discharge efficiency also, you won't get more than 3hrs back up at half the load.
2. In reality batteries never give 100% efficiency at such high current discharge rates. The efficiency will be around 60 to 65% and hence you will actually get 65AH only. It means you should get 2 Hrs back up at half the load. There are certain other factors which can eat away the Capacity to make it 90 minutes only.

Please let me know on this and let APC people also comment on this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

is it just a single 12 volt battory? my system reqires 2 battory packs at 12v each, the oem battorys faild after a year havent found replacement since so i took to some custom mod work and if you know what you are doing, 2 12v marine battorys work great bulky and dont looking good but they work awsom, 500 crank amps each 1000 total, i get about 6 and half hours run time full load. ^_^ charge system is holding up well and delivers a constant v rateing. consider this option depending on your unit is not under warenty and stuff

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

0 Likes
0
3001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:10 AM . Last Modified: ‎2024-03-22 04:09 AM

The website has a product catalogue of all the models available in India. This is all the info I could get

BATTERY SPECS_

Model name : AMCO A100T (dry charged series)
Voltage : 12V.
Capacity(Ah)20hr : 100
Nominal Wt. Filled : 27 Kgs.
Electrolyte Volume : 7.2 Liters
Charging Current : 10 Amps
Dimension(L*B*H) : 410*176*233 mm.

Environment temperature is 30 to 34 C.

And by power factor I believe you are referring to the watts consumed by the electrical appliances.

At full load, all the appliances connected to the UPS consume 380 Watts or 600 VA. In this case I barely get about 45 minutes of battery backup.

At half load, approximately 160-180 watts is what I normally use. Here the battery backup lasts only upto 90-100 minutes average.

As I mentioned earlier when I started the thread, I have a scheduled power cut for 2 hours everyday. There are no interruptions after this power cut, hence giving it a full 22 hours to charge everyday.

Hope to hear from you soon


Thanks,

Anjay. K.



P.S: This is their website [http://www.amco.co.in/downloads.php?id=d#]

Message was edited by: anjaykm

Message was edited by: anjaykm

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.