Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PC reboots when I print to a network printer

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PC reboots when I print to a network printer
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
152
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
9
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

PC reboots when I print to a network printer

I have a Win7 (64) workstation connected to a home network via cable... I installed a brand new BE550G a week ago. Every time I print to a laser printer (for the 1st time) it will reboot my PC. The printer is not connected to my PC and is connected to a router which is protected by its own UPS. All servers (3) and 2 printers have their own UPS's.

Once I finish rebooting I can then print ok without it rebooting. On the new 550 I have my PC with a 23" monitor and 2 small speakers. No other accessories.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Hi Derek,

 

You may restart the print spooler service and delete the print jobs to check if it helps to fix the issue. 

 

a) Press the Windows key and R on the keyboard together.

b) Type “Services.msc” inside the box and press Enter.

c) Click on Print Spooler service and right-click on it.

d) Click the "Stop" button to stop the Print Spooler Service if it is running.

e) Check whether the Startup type is set to Automatic. If not, then set it to Automatic.

f) Go to the following location and delete all the pending documents from the “Printer”. “C:\WINDOWS\system32\spool\PRINTERS”

g) Delete all the queued print jobs (select and delete all the files) in the folder so the folder is devoid of pending print jobs. The folder should be empty when you are done.

h) Restart your system and check the Print Spooler Service again to be sure the Print Spooler Service restarts automatically on reboot (since the Startup type is set to Automatic).

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Hi Derek,

I am just curious with what is going on. Does the PC reboots even if you've used a different PC to print on the same printer? There are some instances wherein even if the printer is not attached to the UPS, whenever it initiates itself or heats up the heating element it eats/consumes a large amount of electricity. During this state, the UPS detects a sag/low voltage and that would cause it to run on battery.

On your end it would really be helpful to know if the UPS would run on battery or would it stay online when you print. It would be helpful to know if it is just the PC that is affected.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Hi Derek,

May I ask where the printer is connected? Is it on the same wall outlet and/or same circuit where the UPS is plugged in?

Also, whenever the printer is working and the computer rebooted, do you know the state of the UPS?If it emitted a beep (like it's on battery)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

The printer is not on the same wall outlet - different outlet, same circuit.

I don't hear any beeps when I print... all I hear is a click and then it reboots. I did notice the other day that it went to the UPS briefly when I tried to print. Do you think I've got my voltage limits set to high (on the low end)?

I'm puzzled as to why the new UPS doesn't mask the issue... I've had no problems printing in the past when I didn't have the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Sorry for the delay - I was out of town the entire week.

I tried printing to the printer from a Windows server on the network and it worked just fine - it did not reboot.

I wonder if it is a power supply issue on my workstation? I'm going to buy an upgraded power supply and will see what happens...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Hi Derek,

Have you tried re-installing the Printer Driver on your PC? I think we had similar issues though mine was not a network printer but a printer attached to a computer and shared on the network. My printer was connected on a Windows 7 PC and I installed it on my laptop that is running Windows XP. When I used my laptop to print, it rebooted.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Yes, I've just tried to uninstall the printer driver and reinstall a fresh new one downloaded from the vendor. Same result.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

I have run out of idea. Other things that I can think of are : (1) Removing the PC from the UPS; (2) Calling the manufacturer of the printer; (3) Reinstalling the Operating System; and (4) Calling the manufacturer of the PC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

The above-mentioned issue is that the system crashes and reboots when printing might have occurred due to corrupt printer drivers or the printer settings are incorrect on the system.in order to confirm it, I would suggest you to first Run inbuilt printer troubleshooter and check if it works and if this is not helpful then use the System File Checker tool to repair missing or corrupted system files. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

0 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:58 AM . Last Modified: ‎2024-03-21 10:45 PM

Hi Derek,

 

You may restart the print spooler service and delete the print jobs to check if it helps to fix the issue. 

 

a) Press the Windows key and R on the keyboard together.

b) Type “Services.msc” inside the box and press Enter.

c) Click on Print Spooler service and right-click on it.

d) Click the "Stop" button to stop the Print Spooler Service if it is running.

e) Check whether the Startup type is set to Automatic. If not, then set it to Automatic.

f) Go to the following location and delete all the pending documents from the “Printer”. “C:\WINDOWS\system32\spool\PRINTERS”

g) Delete all the queued print jobs (select and delete all the files) in the folder so the folder is devoid of pending print jobs. The folder should be empty when you are done.

h) Restart your system and check the Print Spooler Service again to be sure the Print Spooler Service restarts automatically on reboot (since the Startup type is set to Automatic).

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore