Is my old APC Back-UPS XS BX1500's battery low or insufficient?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is my old APC Back-UPS XS BX1500's battery low or insufficient?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
22
2261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

Is my old APC Back-UPS XS BX1500's battery low or insufficient?

Hello.

I had a ten/10 minutes power outage this morning, but my six years old APC Back-UPS XS BX1500 didn't last long enough to power down my Windows machine, but my Debian/Linux did autoshutdown by itself due to very low power on time. The battery power only lasted under five minutes. Do I need to replace its battery from http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=RBC33 or is my old UPS insufficient for my setup?

FYI from my other computer with an old Debian/Linux:
$ cat /var/log/apcupsd.events
...
2011-05-13 07:33:04 -0700 Power failure.
2011-05-13 07:33:10 -0700 Running on UPS batteries.
2011-05-13 07:33:23 -0700 Reached remaining time percentage limit on batteries.
2011-05-13 07:33:23 -0700 Initiating system shutdown!
2011-05-13 07:33:23 -0700 User logins prohibited
2011-05-13 07:34:56 -0700 apcupsd exiting, signal 15
2011-05-13 07:34:56 -0700 apcupsd shutdown succeeded
2011-05-13 07:40:28 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded

$ /sbin/apcaccess for my powered systems together without its monitor powered on (not sleep):
APC : 001,037,0914
DATE : 2011-05-13 12:41:48 -0700
HOSTNAME : FooBar
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : FooBar
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2011-05-13 07:40:26 -0700
STATUS : ONLINE
LINEV : 114.0 Volts
LOADPCT : 40.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 19.9 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132444
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2011-05-13 12:42:39 -0700

My detailed computer and monitor setup can be found in here: http://zimage.com/~ant/antfarm/about/computers.txt ... Note that UPS is only connected to two PCs with two optical mice, and one monitor.

Thank you in advance. πŸ™‚

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

Dupe.

Message was edited by: ant

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 22
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

how long has it lasted with this load in the past? if it is 6 years old, i'd assume it needs a battery replacement but apcupsd is only reporting a 40% load. if the ups was fully loaded with all of the items you mentioned when you retrieved that status, i'd look towards a replacement battery. the existing battery, if original, probably cannot provide the full runtime anymore.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

Hi ant,

By any chance, do you have the total amount of Watts/VA of the attached load on the battery side only? If we have that information we can easily calculate or know the estimated runtime that the UPS can provide.

Also, the battery life could affect the runtime of the unit.

Documentation below can give you additional as well.

[Kbase 10691|http://nam-en.apc.com/app/answers/detail/a_id/10691/kw/insufficient%20runtime]

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i picKed a winna wrote:
how long has it lasted with this load in the past? if it is 6 years old, i'd assume it needs a battery replacement but apcupsd is only reporting a 40% load. if the ups was fully loaded with all of the items you mentioned when you retrieved that status, i'd look towards a replacement battery. the existing battery, if original, probably cannot provide the full runtime anymore.
Previous power outages were shorter than this one, so I don't know. Also, I upgraded PCs last December 2010 as well. I think the upgraded PCs use more power.

I am using the same battery that came with the UPS. You can see its 2005 date in apcuspd's results too.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:56 AM . Last Modified: β€Ž2024-03-21 10:46 PM

juangele wrote:
Hi ant,

By any chance, do you have the total amount of Watts/VA of the attached load on the battery side only? If we have that information we can easily calculate or know the estimated runtime that the UPS can provide.

Also, the battery life could affect the runtime of the unit.

Documentation below can give you additional as well.

[Kbase 10691|http://nam-en.apc.com/app/answers/detail/a_id/10691/kw/insufficient%20runtime]
Total amount of watts/VA of attached load on battery side? How do I get that? Are you saying pretend that there is a power outage and run the command I did earlier?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i am not sure what judy is getting at but my recommendation is that it is time to replace the battery because the current battery isnt functioning 100% anymore since its 5+ years old.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i picKed a winna wrote:
i am not sure what judy is getting at but my recommendation is that it is time to replace the battery because the current battery isnt functioning 100% anymore since its 5+ years old.
Thanks. So I shouldn't trust the readings then since they seem to be inaccurate.

I wonder if I am better off to buy a new, stronger UPS, instead of buying a battery replacement. Have UPS' improved a lot and become cheaper over five years?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

APC products are terrible and if you have one, you should immediately return it. THere's no support and they simply don't work as described. For example, a battery backup by APC doesn't actually do anything other than act as a light weight surge protector. These people should be bankrupted out of business.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

well, i think what judy was suggesting after re-reading this is that if you could provide the load percentage so she could check the runtime chart for you and we could see the expected runtime. according to apcupsd, it was reporting 40% at the time that data was provided so we could compare that against the runtime chart.

the UPS provides a runtime estimate when its online. when it is on battery, the estimate becomes more accurate. thus, yes there can be a bit of an accuracy factor on the runtime and it could require a runtime calibration if you don't have many power outages to ultimately calibrate it.

if you don't want to buy a battery, you could look towards the trade UPS program and trade in the UPS and get a discount towards a new UPS and new battery with a 3 year warranty. that will most likely be a lot more cost effective since a battery might be a little $$ and only come with a 1 year warranty on the unit itself.

here are some options -> http://www.apc.com/recycle/

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

ah ok. so we can do 44% of the 865 watts.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i picKed a winna wrote:
well, i think what judy was suggesting after re-reading this is that if you could provide the load percentage so she could check the runtime chart for you and we could see the expected runtime. according to apcupsd, it was reporting 40% at the time that data was provided so we could compare that against the runtime chart.

the UPS provides a runtime estimate when its online. when it is on battery, the estimate becomes more accurate. thus, yes there can be a bit of an accuracy factor on the runtime and it could require a runtime calibration if you don't have many power outages to ultimately calibrate it.
Calibration. How do I do that? I never had to do that before and didn't know it was required. Power outages are very rare. Most incidents are power hiccups (not actual outages) when turning on my old 20" CRT TV from 1996 in my room or turning on something from another room across the hall. Here are all the recorded incidents according to apcaccess' events since 9/21/2010:

$ cat /var/log/apcupsd.events
2010-09-21 06:37:09 -0700 apcupsd exiting, signal 15
2010-09-21 06:37:09 -0700 apcupsd shutdown succeeded
2010-09-21 06:38:25 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-09-26 13:28:55 -0700 Power failure.
2010-09-26 13:28:57 -0700 Power is back. UPS running on mains.
2010-09-28 18:22:15 -0700 Power failure.
2010-09-28 18:22:17 -0700 Power is back. UPS running on mains.
2010-10-01 07:58:19 -0700 Power failure.
2010-10-01 07:58:21 -0700 Power is back. UPS running on mains.
2010-10-01 11:00:18 -0700 Power failure.
2010-10-01 11:00:20 -0700 Power is back. UPS running on mains.
2010-10-01 21:46:01 -0700 apcupsd exiting, signal 15
2010-10-01 21:46:02 -0700 apcupsd shutdown succeeded
2010-10-01 21:27:06 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 21:44:14 -0700 apcupsd exiting, signal 15
2010-10-01 21:44:14 -0700 apcupsd shutdown succeeded
2010-10-01 21:45:09 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 21:47:53 -0700 apcupsd exiting, signal 15
2010-10-01 21:47:53 -0700 apcupsd shutdown succeeded
2010-10-01 21:48:47 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 21:54:01 -0700 apcupsd exiting, signal 15
2010-10-01 21:54:01 -0700 apcupsd shutdown succeeded
2010-10-01 21:56:43 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 23:28:19 -0700 apcupsd exiting, signal 15
2010-10-01 23:28:19 -0700 apcupsd shutdown succeeded
2010-10-01 23:29:14 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 23:32:52 -0700 apcupsd exiting, signal 15
2010-10-01 23:32:52 -0700 apcupsd shutdown succeeded
2010-10-01 23:33:46 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 23:40:33 -0700 apcupsd exiting, signal 15
2010-10-01 23:40:33 -0700 apcupsd shutdown succeeded
2010-10-01 23:41:22 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 23:44:24 -0700 apcupsd exiting, signal 15
2010-10-01 23:44:24 -0700 apcupsd shutdown succeeded
2010-10-01 23:45:46 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-01 23:46:43 -0700 apcupsd exiting, signal 15
2010-10-01 23:46:43 -0700 apcupsd shutdown succeeded
2010-10-01 23:51:52 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-06 20:50:33 -0700 Power failure.
2010-10-06 20:50:36 -0700 Power is back. UPS running on mains.
2010-10-17 20:50:52 -0700 Power failure.
2010-10-17 20:50:55 -0700 Power is back. UPS running on mains.
2010-10-18 07:28:38 -0700 apcupsd exiting, signal 15
2010-10-18 07:28:38 -0700 apcupsd shutdown succeeded
2010-10-18 07:29:34 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-25 07:24:52 -0700 apcupsd exiting, signal 15
2010-10-25 07:24:52 -0700 apcupsd shutdown succeeded
2010-10-25 07:25:47 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-10-26 22:54:19 -0700 Power failure.
2010-10-26 22:54:21 -0700 Power is back. UPS running on mains.
2010-10-31 21:27:40 -0700 Power failure.
2010-10-31 21:27:43 -0700 Power is back. UPS running on mains.
2010-11-03 07:51:20 -0700 apcupsd exiting, signal 15
2010-11-03 07:51:20 -0700 apcupsd shutdown succeeded
2010-11-03 07:52:16 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-11-19 22:22:43 -0800 Power failure.
2010-11-19 22:22:45 -0800 Power is back. UPS running on mains.
2010-11-20 08:47:12 -0800 Power failure.
2010-11-20 08:47:15 -0800 Power is back. UPS running on mains.
2010-11-26 22:13:22 -0800 Power failure.
2010-11-26 22:13:25 -0800 Power is back. UPS running on mains.
2010-11-28 09:33:58 -0800 apcupsd exiting, signal 15
2010-11-28 09:33:58 -0800 apcupsd shutdown succeeded
2010-11-28 09:34:56 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-11-28 19:18:43 -0800 apcupsd exiting, signal 15
2010-11-28 19:18:43 -0800 apcupsd shutdown succeeded
2010-11-28 19:19:37 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-12 12:40:15 -0800 Power failure.
2010-12-12 12:40:18 -0800 Power is back. UPS running on mains.
2010-12-13 08:39:59 -0800 apcupsd exiting, signal 15
2010-12-13 08:39:59 -0800 apcupsd shutdown succeeded
2010-12-13 08:40:54 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-20 16:07:31 -0800 apcupsd exiting, signal 15
2010-12-20 16:07:31 -0800 apcupsd shutdown succeeded
2010-12-20 18:47:42 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-20 20:14:05 -0800 apcupsd exiting, signal 15
2010-12-20 20:14:05 -0800 apcupsd shutdown succeeded
2010-12-20 20:14:52 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-24 06:48:00 -0800 apcupsd exiting, signal 15
2010-12-24 06:48:00 -0800 apcupsd shutdown succeeded
2010-12-24 07:03:46 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-24 17:25:10 -0800 apcupsd exiting, signal 15
2010-12-24 17:25:10 -0800 apcupsd shutdown succeeded
2010-12-24 17:25:57 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-24 19:54:01 -0800 apcupsd exiting, signal 15
2010-12-24 19:54:01 -0800 apcupsd shutdown succeeded
2010-12-24 19:54:50 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-25 18:31:26 -0800 apcupsd exiting, signal 15
2010-12-25 18:31:26 -0800 apcupsd shutdown succeeded
2010-12-25 18:32:14 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-26 13:18:07 -0800 apcupsd exiting, signal 15
2010-12-26 13:18:07 -0800 apcupsd shutdown succeeded
2010-12-26 13:18:54 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2010-12-28 21:15:31 -0800 Power failure.
2010-12-28 21:15:32 -0800 Power is back. UPS running on mains.
2011-01-01 18:20:22 -0800 apcupsd exiting, signal 15
2011-01-01 18:39:42 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-08 19:20:12 -0800 Power failure.
2011-01-08 19:20:14 -0800 Power is back. UPS running on mains.
2011-01-15 10:51:06 -0800 apcupsd exiting, signal 15
2011-01-15 10:51:06 -0800 apcupsd shutdown succeeded
2011-01-15 10:51:57 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-24 04:32:59 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-24 06:03:02 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-24 07:24:46 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-24 07:26:37 -0800 apcupsd exiting, signal 15
2011-01-24 07:26:37 -0800 apcupsd shutdown succeeded
2011-01-24 07:29:39 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-01-26 01:31:39 -0800 Power failure.
2011-01-26 01:31:43 -0800 Power is back. UPS running on mains.
2011-01-26 01:31:55 -0800 Power failure.
2011-01-26 01:31:58 -0800 Power is back. UPS running on mains.
2011-01-26 01:32:36 -0800 Power failure.
2011-01-26 01:32:39 -0800 Power is back. UPS running on mains.
2011-01-26 03:40:20 -0800 Power failure.
2011-01-26 03:40:23 -0800 Power is back. UPS running on mains.
2011-02-18 20:17:18 -0800 Power failure.
2011-02-18 20:17:21 -0800 Power is back. UPS running on mains.
2011-02-21 12:20:55 -0800 apcupsd exiting, signal 15
2011-02-21 12:20:55 -0800 apcupsd shutdown succeeded
2011-02-21 12:21:45 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-02-21 14:17:23 -0800 apcupsd exiting, signal 15
2011-02-21 14:17:23 -0800 apcupsd shutdown succeeded
2011-02-21 14:21:49 -0800 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-02-22 21:57:42 -0800 Power failure.
2011-02-22 21:57:44 -0800 Power is back. UPS running on mains.
2011-03-07 22:37:26 -0800 Power failure.
2011-03-07 22:37:29 -0800 Power is back. UPS running on mains.
2011-03-16 22:25:06 -0700 Power failure.
2011-03-16 22:25:09 -0700 Power is back. UPS running on mains.
2011-03-20 08:55:51 -0700 apcupsd exiting, signal 15
2011-03-20 08:55:51 -0700 apcupsd shutdown succeeded
2011-03-20 08:56:48 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-04-02 22:02:27 -0700 Power failure.
2011-04-02 22:02:29 -0700 Power is back. UPS running on mains.
2011-04-11 18:56:24 -0700 apcupsd exiting, signal 15
2011-04-11 18:56:24 -0700 apcupsd shutdown succeeded
2011-04-11 18:57:24 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-04-20 00:16:45 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-04-20 00:30:32 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-05-02 10:20:57 -0700 Power failure.
2011-05-02 10:20:59 -0700 Power is back. UPS running on mains.
2011-05-06 17:23:00 -0700 apcupsd exiting, signal 15
2011-05-06 17:23:00 -0700 apcupsd shutdown succeeded
2011-05-06 17:24:52 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
2011-05-08 21:08:42 -0700 Power failure.
2011-05-08 21:08:44 -0700 Power is back. UPS running on mains.
2011-05-13 07:33:04 -0700 Power failure.
2011-05-13 07:33:10 -0700 Running on UPS batteries.
2011-05-13 07:33:23 -0700 Reached remaining time percentage limit on batteries.
2011-05-13 07:33:23 -0700 Initiating system shutdown!
2011-05-13 07:33:23 -0700 User logins prohibited
2011-05-13 07:34:56 -0700 apcupsd exiting, signal 15
2011-05-13 07:34:56 -0700 apcupsd shutdown succeeded
2011-05-13 07:40:28 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded

Also, back in late summer of 2008, I did had to manually power off UPS for over a month due to a house remodel so I didn't use it for a while.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i am not sure how to do it on apcupsd but a calibration just discharges the battery to 10-20% and then charges back up so then the UPS knows how much runtime it really has and re-calculates it.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:46 PM

i picKed a winna wrote:
i am not sure how to do it on apcupsd but a calibration just discharges the battery to 10-20% and then charges back up so then the UPS knows how much runtime it really has and re-calculates it.
How about when my UPS run out of power like a few days ago? I know on some laptops/notebooks, draining all the battery power and then recharge will give more accurate status. Will that work for this old UPS battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

yup. that would be what i would call a manual calibration. it should be accurate as long as you had no software settings that intervened and prevented the UPS from draining its battery, which i dont believe you did.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

i picKed a winna wrote:
yup. that would be what i would call a manual calibration. it should be accurate as long as you had no software settings that intervened and prevented the UPS from draining its battery, which i dont believe you did.
Hmm, I don't know Linux's UPS software does that. I used mostly the default settings from 2005 or so. Also, it is done through its USB connection.

I forgot to mention that after my old UPS and its connected computer stuff were shut down a few days ago, I tried to turn on my UPS for kicks when the power was still out. UPS' front light came on red and then off again after a second. I assume its battery power was completely gone?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

yup, most likely.

check this out -> http://www.apcupsd.com/manual/manual.html#soft-runtime-calibration

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

i picKed a winna wrote:
yup, most likely.

check this out -> http://www.apcupsd.com/manual/manual.html#soft-runtime-calibration
Thanks. I will have to decide to get a completely new UPS or a battery. I don't know if my old one is strong enough to handle two powerful PCs with an old 19" LCD monitor. I don't know how much power they actually use in total. I know I have two PSUs (600 + 650 watts).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

well, if you had everything plugged in earlier when you gave me that read out from apcupsd, it said:*LOADPCT* : 40.0 Percent Load Capacity*? BX1500 can handle 865 watts. so even though your power supplies max out at ~600 watts each, they don't draw that constantly. i would use 346 watts as your normal load and then it probably uses a little more when you turn everything on and there is inrush current.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

i picKed a winna wrote:
well, if you had everything plugged in earlier when you gave me that read out from apcupsd, it said:*LOADPCT* : 40.0 Percent Load Capacity*? BX1500 can handle 865 watts. so even though your power supplies max out at ~600 watts each, they don't draw that constantly. i would use 346 watts as your normal load and then it probably uses a little more when you turn everything on and there is inrush current.
Ah OK. Earlier I had my monitor, PCs idling, and other things off for apcaccess results. Here's what I have if I was using it like right now (4% more load):

$ /sbin/apcaccess
APC : 001,037,0914
DATE : 2011-05-17 13:24:47 -0700
HOSTNAME : FooBar
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : FooBar
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2011-05-13 07:40:26 -0700
STATUS : ONLINE
LINEV : 115.0 Volts
LOADPCT : 44.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 17.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132444
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2011-05-17 13:25:20 -0700

Also, I was watching a videos from my HDTV recordings (my Windows box acts as a media center/home theater) when the power outage hit.

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

Yep, it looks like I will need to get a new UPS or a new battery:

On Sunday night, there were two quick (a few minutes) power outages due to the crazy heat wave. My old APC Back-UPS XS BX1500, from 9/25/2005, did not even last a second and shut down with my two PCs connected. I noticed my UPS' status now shows "ONLINE LOWBATT" with just one PC and 19" 5:4 LCD monitor connected:

$ /sbin/apcaccess
APC : 001,037,0913
DATE : 2012-08-17 05:34:05 -0700
HOSTNAME : MyBox
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : MyBox
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2012-08-13 20:19:09 -0700
STATUS : ONLINE LOWBATT
LINEV : 115.0 Volts
LOADPCT : 30.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 1.8 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : Low line voltage
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000048 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132...
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2012-08-17 05:34:55 -0700

However, it is about $100 (without taxes, shipping fees, etc.) for a new battery and no discount for a new APC UPS. 😞 UPS works fine as long as it doesn't use its battery. Hmm, should I get a new battery or a new UPS? Have consumer UPSes improved since 2005?

It also can handle power hiccups like these according to
/var/log/apcupsd.events log file:
...
2012-07-03 07:09:21 -0700 apcupsd 3.14.8 (16 January 2010) debian startup
succeeded
2012-07-23 07:37:11 -0700 Power failure.
2012-07-23 07:37:14 -0700 Power is back. UPS running on mains.
2012-07-29 21:26:00 -0700 Power failure.
2012-07-29 21:26:03 -0700 Power is back. UPS running on mains.
2012-08-07 23:37:41 -0700 Power failure.
2012-08-07 23:37:44 -0700 Power is back. UPS running on mains.
2012-08-08 07:37:34 -0700 Power failure.
2012-08-08 07:37:36 -0700 Power is back. UPS running on mains.
...

Thank you in advance. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:57 AM . Last Modified: β€Ž2024-03-21 10:45 PM

I also disconnected everything from the battery outlets to see the differences:

$ /sbin/apcaccess status
APC : 001,037,0905
DATE : 2012-08-17 10:34:10 -0700
HOSTNAME : MyBox
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : MyBox
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2012-08-13 20:19:09 -0700
STATUS : ONLINE
LINEV : 116.0 Volts
LOADPCT : 0.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 170.3 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : Low line voltage
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132...
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2012-08-17 10:34:54 -0700

170.3 Minutes???

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

This is weird! Earlier, I was using my main Windows XP Pro. SP3 computer and my UPS said "On Battery" with its orange light and beeped loudly at me. There was NO power outage!!! My Windows PC stayed up fine on its battery outlet, but Linux box (non-battery outlet) shut down from its apcupsd and USB cable connected to UPS:

2012-08-13 20:19:10 -0700 apcupsd 3.14.8 (16 January 2010) debian
startup succeeded
2012-08-23 07:37:56 -0700 Power failure.
2012-08-23 07:37:57 -0700 Battery power exhausted.
2012-08-23 07:37:57 -0700 Initiating system shutdown!
2012-08-23 07:37:57 -0700 User logins prohibited
2012-08-23 07:37:58 -0700 apcupsd exiting, signal 15
2012-08-23 07:37:58 -0700 apcupsd shutdown succeeded

I had to turn UPS off to make it stop beeping and telling me battery. So weird. Maybe my UPS is broken too? Maybe I should replace the whole thing and not just its dual batteries?

Message was edited by: ant

Reply

Link copied. Please paste this link to share this article on your social media post.

ant_apc
Lieutenant ant_apc
Lieutenant

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:58 AM . Last Modified: β€Ž2024-03-21 10:45 PM

Dupe.

Message was edited by: ant

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of