Hello.
I had a ten/10 minutes power outage this morning, but my six years old APC Back-UPS XS BX1500 didn't last long enough to power down my Windows machine, but my Debian/Linux did autoshutdown by itself due to very low power on time. The battery power only lasted under five minutes. Do I need to replace its battery from http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=RBC33 or is my old UPS insufficient for my setup?
FYI from my other computer with an old Debian/Linux:
$ cat /var/log/apcupsd.events
...
2011-05-13 07:33:04 -0700 Power failure.
2011-05-13 07:33:10 -0700 Running on UPS batteries.
2011-05-13 07:33:23 -0700 Reached remaining time percentage limit on batteries.
2011-05-13 07:33:23 -0700 Initiating system shutdown!
2011-05-13 07:33:23 -0700 User logins prohibited
2011-05-13 07:34:56 -0700 apcupsd exiting, signal 15
2011-05-13 07:34:56 -0700 apcupsd shutdown succeeded
2011-05-13 07:40:28 -0700 apcupsd 3.14.8 (16 January 2010) debian startup succeeded
$ /sbin/apcaccess for my powered systems together without its monitor powered on (not sleep):
APC : 001,037,0914
DATE : 2011-05-13 12:41:48 -0700
HOSTNAME : FooBar
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : FooBar
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2011-05-13 07:40:26 -0700
STATUS : ONLINE
LINEV : 114.0 Volts
LOADPCT : 40.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 19.9 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132444
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2011-05-13 12:42:39 -0700
My detailed computer and monitor setup can be found in here: http://zimage.com/~ant/antfarm/about/computers.txt ... Note that UPS is only connected to two PCs with two optical mice, and one monitor.
Thank you in advance. ๐
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:58 AM . Last Modified: โ2024-03-21 10:45 PM
Dupe.
Message was edited by: ant
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:56 AM . Last Modified: โ2024-03-21 10:46 PM
how long has it lasted with this load in the past? if it is 6 years old, i'd assume it needs a battery replacement but apcupsd is only reporting a 40% load. if the ups was fully loaded with all of the items you mentioned when you retrieved that status, i'd look towards a replacement battery. the existing battery, if original, probably cannot provide the full runtime anymore.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:56 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:56 AM . Last Modified: โ2024-03-21 10:46 PM
Hi ant,
By any chance, do you have the total amount of Watts/VA of the attached load on the battery side only? If we have that information we can easily calculate or know the estimated runtime that the UPS can provide.
Also, the battery life could affect the runtime of the unit.
Documentation below can give you additional as well.
[Kbase 10691|http://nam-en.apc.com/app/answers/detail/a_id/10691/kw/insufficient%20runtime]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:56 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:56 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
i am not sure what judy is getting at but my recommendation is that it is time to replace the battery because the current battery isnt functioning 100% anymore since its 5+ years old.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
APC products are terrible and if you have one, you should immediately return it. THere's no support and they simply don't work as described. For example, a battery backup by APC doesn't actually do anything other than act as a light weight surge protector. These people should be bankrupted out of business.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
well, i think what judy was suggesting after re-reading this is that if you could provide the load percentage so she could check the runtime chart for you and we could see the expected runtime. according to apcupsd, it was reporting 40% at the time that data was provided so we could compare that against the runtime chart.
the UPS provides a runtime estimate when its online. when it is on battery, the estimate becomes more accurate. thus, yes there can be a bit of an accuracy factor on the runtime and it could require a runtime calibration if you don't have many power outages to ultimately calibrate it.
if you don't want to buy a battery, you could look towards the trade UPS program and trade in the UPS and get a discount towards a new UPS and new battery with a 3 year warranty. that will most likely be a lot more cost effective since a battery might be a little $$ and only come with a 1 year warranty on the unit itself.
here are some options -> http://www.apc.com/recycle/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
ah ok. so we can do 44% of the 865 watts.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
i am not sure how to do it on apcupsd but a calibration just discharges the battery to 10-20% and then charges back up so then the UPS knows how much runtime it really has and re-calculates it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:46 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
yup. that would be what i would call a manual calibration. it should be accurate as long as you had no software settings that intervened and prevented the UPS from draining its battery, which i dont believe you did.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
yup, most likely.
check this out -> http://www.apcupsd.com/manual/manual.html#soft-runtime-calibration
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
well, if you had everything plugged in earlier when you gave me that read out from apcupsd, it said:*LOADPCT* : 40.0 Percent Load Capacity*? BX1500 can handle 865 watts. so even though your power supplies max out at ~600 watts each, they don't draw that constantly. i would use 346 watts as your normal load and then it probably uses a little more when you turn everything on and there is inrush current.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
Yep, it looks like I will need to get a new UPS or a new battery:
On Sunday night, there were two quick (a few minutes) power outages due to the crazy heat wave. My old APC Back-UPS XS BX1500, from 9/25/2005, did not even last a second and shut down with my two PCs connected. I noticed my UPS' status now shows "ONLINE LOWBATT" with just one PC and 19" 5:4 LCD monitor connected:
$ /sbin/apcaccess
APC : 001,037,0913
DATE : 2012-08-17 05:34:05 -0700
HOSTNAME : MyBox
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : MyBox
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2012-08-13 20:19:09 -0700
STATUS : ONLINE LOWBATT
LINEV : 115.0 Volts
LOADPCT : 30.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 1.8 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : Low line voltage
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000048 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132...
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2012-08-17 05:34:55 -0700
However, it is about $100 (without taxes, shipping fees, etc.) for a new battery and no discount for a new APC UPS. ๐ UPS works fine as long as it doesn't use its battery. Hmm, should I get a new battery or a new UPS? Have consumer UPSes improved since 2005?
It also can handle power hiccups like these according to
/var/log/apcupsd.events log file:
...
2012-07-03 07:09:21 -0700 apcupsd 3.14.8 (16 January 2010) debian startup
succeeded
2012-07-23 07:37:11 -0700 Power failure.
2012-07-23 07:37:14 -0700 Power is back. UPS running on mains.
2012-07-29 21:26:00 -0700 Power failure.
2012-07-29 21:26:03 -0700 Power is back. UPS running on mains.
2012-08-07 23:37:41 -0700 Power failure.
2012-08-07 23:37:44 -0700 Power is back. UPS running on mains.
2012-08-08 07:37:34 -0700 Power failure.
2012-08-08 07:37:36 -0700 Power is back. UPS running on mains.
...
Thank you in advance. ๐
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:57 AM . Last Modified: โ2024-03-21 10:45 PM
I also disconnected everything from the battery outlets to see the differences:
$ /sbin/apcaccess status
APC : 001,037,0905
DATE : 2012-08-17 10:34:10 -0700
HOSTNAME : MyBox
VERSION : 3.14.8 (16 January 2010) debian
UPSNAME : MyBox
CABLE : USB Cable
MODEL : Back-UPS RS 1500
UPSMODE : Stand Alone
STARTTIME: 2012-08-13 20:19:09 -0700
STATUS : ONLINE
LINEV : 116.0 Volts
LOADPCT : 0.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 170.3 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 097.0 Volts
HITRANS : 138.0 Volts
ALARMDEL : Always
BATTV : 26.9 Volts
LASTXFER : Low line voltage
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
MANDATE : 2005-03-16
SERIALNO : QB0512132...
BATTDATE : 2005-03-16
NOMINV : 120 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 865 Watts
FIRMWARE : 8.g8 .D USB FW:g8
APCMODEL : Back-UPS RS 1500
END APC : 2012-08-17 10:34:54 -0700
170.3 Minutes???
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:58 AM . Last Modified: โ2024-03-21 10:45 PM
This is weird! Earlier, I was using my main Windows XP Pro. SP3 computer and my UPS said "On Battery" with its orange light and beeped loudly at me. There was NO power outage!!! My Windows PC stayed up fine on its battery outlet, but Linux box (non-battery outlet) shut down from its apcupsd and USB cable connected to UPS:
2012-08-13 20:19:10 -0700 apcupsd 3.14.8 (16 January 2010) debian
startup succeeded
2012-08-23 07:37:56 -0700 Power failure.
2012-08-23 07:37:57 -0700 Battery power exhausted.
2012-08-23 07:37:57 -0700 Initiating system shutdown!
2012-08-23 07:37:57 -0700 User logins prohibited
2012-08-23 07:37:58 -0700 apcupsd exiting, signal 15
2012-08-23 07:37:58 -0700 apcupsd shutdown succeeded
I had to turn UPS off to make it stop beeping and telling me battery. So weird. Maybe my UPS is broken too? Maybe I should replace the whole thing and not just its dual batteries?
Message was edited by: ant
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-29 05:58 AM . Last Modified: โ2024-03-21 10:45 PM
Dupe.
Message was edited by: ant
Link copied. Please paste this link to share this article on your social media post.