Overload problem with an old UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Overload problem with an old UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:10 AM

0 Likes
3
11053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:10 AM

Overload problem with an old UPS

I have APC BACK-UPS RS 1500VA 230V which supports 865 watts tops. I have bought it 5 years ago. Let me explain my problem.

I have a APC voltage regulator behind of my ups. During sudden voltage drops, it gets triggered and voltage is tipped a little higher. It also causes my UPS to goes into battery mode for a second or two. Thats no problem.
After 5 years of service, during these on/off battery switches, my UPS started give me overload error light with complete shut down of entire system . My load is usually 450-550 watts by the way. First i thought batteries are failing after 5 years, after that i removed the batteries, i looked into their model, and i bought the same brand/model batteries (not official battery pack from APC but the same batteries the official battery pack uses :D) . I connected those new batteries. It solved the overload fail during 1-2 second interventions. But it didnt solve the problem when i completely switch off the power.
So i unplug the power cord of ups it should stay on for couple minutes at least. It does stay on when the load is below 350 watts but it suddenly fails i unplug the cord when the load is over 400 or 500 watts. So i thought it cant support up those upper watts but i tried this. I completely shutdown everything i unplugged ups cord from the grid. I started everything on battery. Systems are loaded and i pushed the UPS up to 700-750 watts without any fails, no overloads or anything.
What i learned from this experiment is, i think ups cant intervene fast enough or back up heavy loads quickly enough. Or there is something wrong with UPS or new batteries. I was thinking to buy or build APC BR24BP BACK-UPS battery pack extension of this UPS, could this solve my problem or the life of my UPS is just expired or any other thoughts?

ps. I have PowerChute installed i monitor all the activities on there

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

>
Or there is something wrong with UPS or new batteries. I was thinking to buy or build APC BR24BP BACK-UPS battery pack extension of this UPS, could this solve my problem or the life of my UPS is just expired or any other thoughts?
>

That's some good sleuthing.

I don't know how likely it is that the UPS is taking longer to transfer; would seem odd after only five years. You might try [changing the sensitivity setting to low|http://www.apcmedia.com/salestools/ASTE-6Z7V72_R0_EN.pdf] to reduce this, though it would also increase unnecessary UPS interventions.

Another possibility is the load on the UPS has changed. For example, as a computer's power supply ages, it becomes less capable of handling momentary power interruptions. Some react to loss of power by attempting to draw as much current as possible.

How did you adjust the load on the UPS when you were testing?

Also, you probably already know this: the manual indicates that the RS UPS has +/- 12% boost and trim. So using a voltage regulator seems a bit redundant.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

Jokes on you ๐Ÿ˜„

I have 3 monitors, one overclocked cpu core i7 930, one HD5970 and one 1 gtx8800 gpu that draw much of total power. My psu is xilence 1200watt model and i cant say that it's old. I never use that much of power, i know that 800 watt is not enough when i overclock everything on the system. I increase the load by stress testing the components using Prime95 or furmark
I just tried these things recently
If i load the system by stressing cpu and keeping the load around 500- 550watts, UPS can manage the power loss.
If i load the system by stressing gpu, even the load is around 450 watts, UPS cant manage the power loss.
Maybe gpu units are very susceptible to power interventions and like you said psu unit may try to draw as much as power like 1200 watts from UPS which causes overload

I know changing sensitivity setting to low would cancel those unnecessary interventions, i tried that but im not sure those interventions are unnecessery or not.
Regular voltage should be 220V here but it drops as low as 160V in here. UPS cant manage voltages under 188V, that's why i need a regulator

I do cpu computing as well as gpu computing for scientific purposes. It seems new batteries solved the problem for cpu computing part but not gpu computing. I will build external battery pack anyway, this will triple the current capacity, maybe this will solve the problem.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

I tried couple of things i want to take advice from you

1. I built (home-made) ups cables and connections. I connected 2 batteries to the front and 2 of them to the back. Powerchute still shows 2 battery of remaining time. (2 batteries mean 2 X 12V 9ah batteries)
2. So i thought maybe there is a connection problem. I took front batteries out and tested then i took back batteries out and tested front batteries. In both cases it shows only 2 battery of remaining time.
3. Then i connected 4 batteries together up front (2 serial 2 parallel to achieve 24V). It still showed 2 battery of time.

while 4 batteries connected (2serial 2 parallel). I read 450 watts of load and 13 mins of remaning battery life. So i decided to measure real remaning time. I disconnected the telecommunication port and cut off power. Then I measured 22 minutes. Which is quite acceptable because 2 of the batteries are brand new and the other 2 were 5 years old.

But still with these new combination, my ups still cant intervene (start to transfer juice) fast enough on heavy loads like 600 watts. So buying another pair of batteries shouldn't solve my problem.

1.Buying an online ups would definitely solve my problem (this one is line interactive). But is there anything else i could do before that?
2.How come powerchute display remaning time incorrectly? I connected those batteries to the back like a battery pack. It should at least triple the remaning time if it was real battery pack (APC BR24BP). Is there a chip or something to tell which is connected or not?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

>
Or there is something wrong with UPS or new batteries. I was thinking to buy or build APC BR24BP BACK-UPS battery pack extension of this UPS, could this solve my problem or the life of my UPS is just expired or any other thoughts?
>

That's some good sleuthing.

I don't know how likely it is that the UPS is taking longer to transfer; would seem odd after only five years. You might try [changing the sensitivity setting to low|http://www.apcmedia.com/salestools/ASTE-6Z7V72_R0_EN.pdf] to reduce this, though it would also increase unnecessary UPS interventions.

Another possibility is the load on the UPS has changed. For example, as a computer's power supply ages, it becomes less capable of handling momentary power interruptions. Some react to loss of power by attempting to draw as much current as possible.

How did you adjust the load on the UPS when you were testing?

Also, you probably already know this: the manual indicates that the RS UPS has +/- 12% boost and trim. So using a voltage regulator seems a bit redundant.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

Jokes on you ๐Ÿ˜„

I have 3 monitors, one overclocked cpu core i7 930, one HD5970 and one 1 gtx8800 gpu that draw much of total power. My psu is xilence 1200watt model and i cant say that it's old. I never use that much of power, i know that 800 watt is not enough when i overclock everything on the system. I increase the load by stress testing the components using Prime95 or furmark
I just tried these things recently
If i load the system by stressing cpu and keeping the load around 500- 550watts, UPS can manage the power loss.
If i load the system by stressing gpu, even the load is around 450 watts, UPS cant manage the power loss.
Maybe gpu units are very susceptible to power interventions and like you said psu unit may try to draw as much as power like 1200 watts from UPS which causes overload

I know changing sensitivity setting to low would cancel those unnecessary interventions, i tried that but im not sure those interventions are unnecessery or not.
Regular voltage should be 220V here but it drops as low as 160V in here. UPS cant manage voltages under 188V, that's why i need a regulator

I do cpu computing as well as gpu computing for scientific purposes. It seems new batteries solved the problem for cpu computing part but not gpu computing. I will build external battery pack anyway, this will triple the current capacity, maybe this will solve the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

0 Likes
0
11047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:10 PM . Last Modified: โ€Ž2024-03-21 03:09 AM

I tried couple of things i want to take advice from you

1. I built (home-made) ups cables and connections. I connected 2 batteries to the front and 2 of them to the back. Powerchute still shows 2 battery of remaining time. (2 batteries mean 2 X 12V 9ah batteries)
2. So i thought maybe there is a connection problem. I took front batteries out and tested then i took back batteries out and tested front batteries. In both cases it shows only 2 battery of remaining time.
3. Then i connected 4 batteries together up front (2 serial 2 parallel to achieve 24V). It still showed 2 battery of time.

while 4 batteries connected (2serial 2 parallel). I read 450 watts of load and 13 mins of remaning battery life. So i decided to measure real remaning time. I disconnected the telecommunication port and cut off power. Then I measured 22 minutes. Which is quite acceptable because 2 of the batteries are brand new and the other 2 were 5 years old.

But still with these new combination, my ups still cant intervene (start to transfer juice) fast enough on heavy loads like 600 watts. So buying another pair of batteries shouldn't solve my problem.

1.Buying an online ups would definitely solve my problem (this one is line interactive). But is there anything else i could do before that?
2.How come powerchute display remaning time incorrectly? I connected those batteries to the back like a battery pack. It should at least triple the remaning time if it was real battery pack (APC BR24BP). Is there a chip or something to tell which is connected or not?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of