New back-UPS RS 800 all four led blink.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New back-UPS RS 800 all four led blink.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
6
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

New back-UPS RS 800 all four led blink.

I just bought new back-UPS RS 800.When I plug power with no load, after 10 seconds all four led start blink.But when I turn it on, it self test successfull and online normally.they stop blink and green online indicator lit. But when I turn it off again ,after 10 seconds all four led start blink again.Anyone have any suggestions?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:21 AM

So these adapters have 3 prongs on one side to accept the power cord from the UPS and 2 prong on the other side to plug into your room's outlet?

There needs to be a 3 prong outlet in order for the UPS to work properly - this 3rd prong is the "ground" wire that, in short, allows the UPS to redirect electricity (surges, etc) as needed. Without this, the UPS cannot safely protect your equipment to its fullest potential.

If the electrical system in your condo doesn't have a ground, you'd need to see if an electrician can install one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

If all the lights are flashing at the same time, then it means that there is an internal fault with the UPS circuit. If this is the case, contact your regional APC Customer Care Center to get the replacement unit under factory warranty.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

Actually I saw these same symptoms on an RS 800 when I had it plugged into a multi-outlet adapter that didn't properly connect to the outlet's ground. I'm not sure if you're seeing a similar problem, but does it do the same thing when you plug it into a properly grounded outlet?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

Today I've got the new one from APC thailand (Thanks to Mr.William).But problem still remain T_T.
May be this problem come from outlet adapter?

I just try with 3 different adapters, two of them has a problem.
Then I try to use power cord without ground pin ( there is only 2 pin) and there's no problem.

Anyone have any suggestions?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

What's the model number on this UPS? I don't know the international ones very well. But it does seem related to your adapters, like I said it doesn't seem to like them. You're supposed to plug it directly into the wall anyway.

What kind of adapters show the problem, and which one doesn't?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:22 AM

Thank you for reply.

The medels is BR800I and all of the outlet adapter are same kind , but different brand.One of them is Belkin ,another two is local brand in thailand.
I'm not sure if adapter or my room's (I live in condominium ) electric system is the problem. If the electric system is cause, then what is it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
1566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:40 AM . Last Modified: ‎2024-03-22 02:21 AM

So these adapters have 3 prongs on one side to accept the power cord from the UPS and 2 prong on the other side to plug into your room's outlet?

There needs to be a 3 prong outlet in order for the UPS to work properly - this 3rd prong is the "ground" wire that, in short, allows the UPS to redirect electricity (surges, etc) as needed. Without this, the UPS cannot safely protect your equipment to its fullest potential.

If the electrical system in your condo doesn't have a ground, you'd need to see if an electrician can install one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore