New apc xs 1300 only puts out 100 volts when disconnected from power supply of 119volts.
Battery is fully charged and shows at least 60 minute duration.
Serial # 4B1329P23746.
Fans slow down when on battery backup. This can't be good for the electronics.
Have tried unit reset as mentioned in another post. Unit unplugged, battery removed, power button held >20 seconds, battery replaced, unit plugged back in to power. No change in output, still 100 volts as tested with multimeter.
Is the voltage output adjustable? Any suggestions?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 2024-03-20 04:16 AM
Please review this article and verify the model and type of voltmeter you're using -> Low output voltage reading on a UPS that uses a step approximated sine wave | FAQs | Schneider Elect...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 2024-03-20 04:16 AM
Please review this article and verify the model and type of voltmeter you're using -> Low output voltage reading on a UPS that uses a step approximated sine wave | FAQs | Schneider Elect...