New Battery in XS 1000

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New Battery in XS 1000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

0 Likes
1
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

New Battery in XS 1000

Just bought a new RBC 123 battery for my XS1000.  I hot swapped it in.  And immediately on my Mac Pro, the icon in the menu bar said it was at 100%.  Which seemed strange.  I left it plugged in for 24 hours just to make sure it was charged.

I unplugged the XS1000 to test the battery. The display on the front shows the load at 3 of 5 bars.  Upon unplugging unit it immediately went to 1 minute left. In the menu bar info I could see the percentage go down steadily by the second.  Within 60 seconds it was down to 9%.  Then it stayed there for several seconds.  I didn't want my computer to shut off if the battery went out, so i shut down.  With very little load the display on the front of the XS1000 shot up to 10 minutes left.

I plugged in a standing fan.  Probably draws about 50-75 watts.  It ran for about an hour and display went down to 9 minutes left.  Then I plugged in a hair dryer. Put it on low, and UPS immediate dropped to 1 minute, than 0 and turned off.  Unplugged fan and hair dryer.

I plugged the XS1000 back in.  Plugged my computer back in and turned it on.  Upon start up, battery reading on computer said it was at 27% and charging.  Within 2 hours it was fully charged to 100%.

My question is: do I need to calibrate the battery some how?  On 3/5 load shouldn't it last more than 1 minute?  I feel like when i originally got the unit 3 years ago, it lasted at least 5 minutes.  Maybe even 10 minutes with a similar load.

Thanks for any advice/help in advanced.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

Your having plugged "dummy" loads (fan, lamp and hair dryer) into the unit and forcing it to run from the battery until it was exhausted is probably all of the calibration that is required. (The hair dryer was probably too much load, and might have damaged the unit. A lamp with a hundred watt bulb, maybe two, will do as well as anything. The load has to be past a threshold of about 30% for the microcontroller to acquire valid calibration data. The battery also needs about eight hours to charge fully before this test.)

I had one unit that refused to "recalibrate" itself through this method. I solved that problem by temporarily using a computer running PowerChute Personal Edition for Windows, and indicating to the software that I'd replaced the UPS battery. This appears to clear any stored data the UPS has about the condition of its batteries, allowing it to relearn that information. There hasn't been a Macintosh version of PowerChute Personal Edition available for a while now, though third party solutions such as apcupsd could be used, if you're comfortable with the command line.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:26 AM . Last Modified: ‎2024-03-27 01:45 AM

Your having plugged "dummy" loads (fan, lamp and hair dryer) into the unit and forcing it to run from the battery until it was exhausted is probably all of the calibration that is required. (The hair dryer was probably too much load, and might have damaged the unit. A lamp with a hundred watt bulb, maybe two, will do as well as anything. The load has to be past a threshold of about 30% for the microcontroller to acquire valid calibration data. The battery also needs about eight hours to charge fully before this test.)

I had one unit that refused to "recalibrate" itself through this method. I solved that problem by temporarily using a computer running PowerChute Personal Edition for Windows, and indicating to the software that I'd replaced the UPS battery. This appears to clear any stored data the UPS has about the condition of its batteries, allowing it to relearn that information. There hasn't been a Macintosh version of PowerChute Personal Edition available for a while now, though third party solutions such as apcupsd could be used, if you're comfortable with the command line.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore