Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Need Help

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Need Help
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
11
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Need Help

Hello,

I am completely new to the world of UPS. I have always heard good things about APC, so here I am. LOL!

I was wondering if I post specs of a new computer build that I will be doing soon, if someone could help me pick an appriopriate UPS that would be large enough to handle what I have and perhaps have some room for growth in the future? (I tried to use the tool on the website, but I don't think it is detailed enough to help me given some on the hardware I use).

Please let me know if this is ok to post or if its against the rules.

Thanks,

Angie

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hello,

I have decided to go with the P11VT3 Surge Protector. I am still confused about the calculations for my equipment, but those articles you posted were very helpful.

As a final question, given my system, is this surge protector more than enough for what I need?

Thanks for all of your time and help!

Angie

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hello,

I am completely new to the world of UPS. I have always heard good things about APC, so here I am. LOL!

I was wondering if I post specs of a new computer build that I will be doing soon, if someone could help me pick an appriopriate UPS that would be large enough to handle what I have and perhaps have some room for growth in the future? (I tried to use the tool on the website, but I don't think it is detailed enough to help me given some on the hardware I use).

Please let me know if this is ok to post or if its against the rules.

Thanks,

Angie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

hi angie,

you can post that and we will certainly do our best to make a recommendation or point you in the right direction.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hello again,

My computer system specs are as follows:

Motherboard: Intel DP55SB P55 Micro-ATX
CPU: Intel Core i7-870
RAM: Corsair CMX8GX3M4A1333C9 8GB DDR3 1333
Hard Drive: Corsair Force 60 GB SSD
Power Supply: Corsair AX750
Video Card: EVGA GTS 450 FTW
Sound Card: Creative Sound Blaster X-Fi Titanium FPS
Optical Drive: Pioneer BDR-205 12x Blu-Ray Burner
Speakers: Logitech Z-5500
Printer: Brother HL-2240
Monitor: Samsung T260HD
Case: Antec Two Hundred v2

Thanks again! Looking forward to your suggestions! Let me know if I missed anything in my specs or any other info you need.

Angie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:30 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

ok..looking into this.

your power supply has power factor correction, explained [in this article|http://nam-en.apc.com/app/answers/detail/a_id/8883/], so we need to multiply the 750W power supply rating by 1.25 and we get ~937 watts. this means, your power supply could pull this maximum wattage value so we need to size the unit appropriately.

my first recommendation would be to see if you can find a BR1500LCD or BX1500LCD unit. Alternatively, if you cannot find that anywhere, I suggest a BX1500G or BR1500G.

problem is, this does not account for all the other stuff - tv, speakers, etc so we need to get the specs on all of that stuff and add it to the wattage draw. you may be ok with this size unit if everything is not turned on at once but the computer does have the potential to pull a lot of power. can you find the user's manual for these other things besides the computer to see what the power requirements are in watts?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hi,

Honestly, the speakers and the printer don't actually need to be hooked up to the UPS part of the UPS, i am just concerned about the power supply, internal components inside the case, and the monitor. The speakers and printer draw rediculous amounts of wattage when in use.. So I don't think i really need them if there was a electrical outage or something like that. I just want them protected from brown outs, power surges, or any other conditions like that, so they are safe and not destroyed.

But, I will do some research to provide you with the wattage of the internal components and the monitor.

thanks,

angie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

you're welcome. i think what you picked out is great as long as what you have plugged into your wall now is not tripping any breakers ๐Ÿ™‚

let me know if you need anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hi,

Below is what I could find:

Motherboard: Intel DP55SB P55 Micro-ATX (Wattage: Unable to find)
CPU: Intel Core i7-870 (Wattage: 95 Watts)
RAM: Corsair CMX8GX3M4A1333C9 8GB DDR3 1333 (Wattage: Unable to find)
Hard Drive: Corsair Force 60 GB SSD (Wattage: 2 Watts)
Power Supply: Corsair AX750 (Wattage: already covered above)
Video Card: EVGA GTS 450 FTW (Wattage: Unable to find, minimum 400 watt supply required - 22 A on +12 volt line)
Sound Card: Creative Sound Blaster X-Fi Titanium FPS (Wattage: Unable to find)
Optical Drive: Pioneer BDR-205 12x Blu-Ray Burner (Wattage: Unable to find)
Speakers: Logitech Z-5500 (Wattage: 505 Watts RMS, 1010 Watts Peak)
Printer: Brother HL-2240 (Wattage: 9 Watts Sleep Mode, 65 Watts Ready, 495 Watts Printing)
Monitor: Samsung T260HD (Unable to find)
Case: Antec Two Hundred v2 (Wattage: N/A)

I am sorry I am not much help on the wattages, but on most of the components, the manufactuer doens't list them in the specs or manual.

Please advise further!

Angie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

ok, well the computer we'll max at 750. it probably wont be pulling 750 watts all the time, we just need to worry about when you turn it on and there is an inrush of power. we generally dont recommend printers plugged into the battery back up since it can indeed overload the unit. i know you mentioned you will be putting it on the surge side though. thus, with the computer and monitor/tv on the surge side only, i think you'll be ok. i think i found the monitor uses 70W max and consumes very little in sleep.

i think with this new information, with all of this stuff, you are probably cutting it really close and may need to look towards something such as an SMT2200 Smart UPS, since that is the next VA level up.

i forgot to ask you how much runtime you are looking for by the way?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hello,

Thanks for the recommendation. I had not even looked at prices on any of the units yet, but I looked up the SMT2200 and had no clue it would be expensive or could range so much in price ($450 - $1000)

Maybe UPS isn't what I need, I'm just basically want to protect my components from damage from the situations mentioned above. The computer really doesn't need to be on when the power goes out, it isn't mission critical. I was looking into maybe just getting a Surge Protector or Automatic Voltage Regulator.

I am not sure what the difference is. Also on these 2 items, I have no clue how to get Joules or VA or any other power specs calculated given my setup from above.

Please help,

Angie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

take a look at this to understand what [volt amps and watts are|http://nam-en.apc.com/app/answers/detail/a_id/1503/]

a battery back up provides runtime on battery when the power goes out. automatic voltage regulation is a transformer that boosts or trims voltage when it is too high or too low. nominal voltage is 120v for the united states. various power issues can cause it to drop down to 100 or go up to 120. in these examples, the transformer would boost or trim the voltage to get closer to the 120v and not damage the equipment. certain equipment may even turn off rather than getting damaged.

joules is a standard measurement of how much surge protection a surge protector has. APC uses joules and also eP joules (equivalent protection joules) since we use a few different types of technology. joules only measures a certain type of technology. [this may help explain some too|http://nam-en.apc.com/app/answers/detail/a_id/65/]

i would suggest looking at a surge protector [from here|http://www.apc.com/products/family/index.cfm?id=176] which will provide the maximum surge protection that we offer. they also have a lifetime warranty and [equipment protection policy|http://www.apc.com/support/service/equipment_protection_policy.cfm]

for a voltage regulator, the smallest one we have would be a LE1200 which can handle 1200 volt amps worth of load. assuming you are using 120v input voltage in your home - 1200/120 = 10A max you can draw through that unit and provide automatic voltage regulation for.

a UPSs purpose is mainly to provide battery back up but you'll find that a lot include the surge protection and automatic voltage regulation within them even though its not their main function. thus, if you dont need/want that functionality, you can just buy the pieces you need.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

0 Likes
0
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:31 AM . Last Modified: โ€Ž2024-03-22 12:38 AM

Hello,

I have decided to go with the P11VT3 Surge Protector. I am still confused about the calculations for my equipment, but those articles you posted were very helpful.

As a final question, given my system, is this surge protector more than enough for what I need?

Thanks for all of your time and help!

Angie

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore