My trusty 30 year old APC Back-Ups 280B acts like it's working... until testing/no power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • My trusty 30 year old APC Back-Ups 280B acts like it's working... until testing/no power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
126
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
JOHN_FL
Ensign JOHN_FL
Ensign

Posted: ‎2024-10-08 10:38 AM

0 Likes
1
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 10:38 AM

My trusty 30 year old APC Back-Ups 280B acts like it's working... until testing/no power

I have an old Back-UPS 280B.  It's worked quite well for a long time.  However, (not necessarily lately, I can't say exactly when) I finally realized, it's not keeping my router/cable modem powered in the event of a power outage.  (I suppose I'm fortunate to have few enough outages that I never really noticed.)

 

The power light on the switch no longer lights up, but it does function.  It beeps when I turn it on.   ANd, if I go into test mode or unplug it, it does it's cadence of a beep every second or three to tell me power is out.  But, whatever is plugged in won't have power while in test mode or unplugged.  And the unit is keeping the battery charged.

 

The battery seems good.  On the multimeter it's a solid 12.72 volts, no fluctuating.  To be fair, it's an old-ish battery, but as far as I can tell it's in good shape.  I'm in another catch 22 of "if I have doubts about the unit, do I want to buy, and possibly end up stuck with a new battery I won't need if the unit is bad?"   The battery did power a lamp through an inexpensive 12 volt inverter for ten plus seconds, showing 11.34 volts while running the inverter.  Assuming I only have an inexpensive multimeter and nothing much beyond that, is there a better way to definitively test the battery?

 

I have another amusing mystery;  There was a 5W15OJ (rectangular/white)  resistor rattling around loose in there.  To the bet of my capabilities, I would say that it belonged in the R99 slot on the board, but I can't say with certainty.  I can say that carefully positioning and holding it in place while testing didn't make the UPS work.

So is it the battery, or is there some other likely failure point?

 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-09 07:06 AM . Last Modified: ‎2024-10-09 07:29 AM

0 Likes
0
632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-09 07:06 AM . Last Modified: ‎2024-10-09 07:29 AM

John,

 

Short Answer: Replace Unit

 

Long Answer: The battery is not healthy and needs to be replaced. This is superseded by the fact the UPS needs to be replaced given the broken resistor.

 

There are dozens of UPS options available that cover the entire spectrum in terms of price. 

 

Take this opportunity to splurge on your self and buy a pure sine wave inverter made in 2024! 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore